The PEN conductor is the incoming combined Protective Earth and Neutral that all homes with a TN-C-S electrical supply have (and that's the majority of UK homes).What's needed for any charge point installation on a TN-C-S supply (used to be called PME) is PEN fault protection. There's an insidious fault that occurs on the LV distribution network (outside the premises) where the PEN conductor can be damaged or go open circuit without any obvious symptoms. Because the PEN conductor for underground cables is often an outer sheath it's not unusual for that to be damaged without damage to the three line conductors.When this happens the return current flows via the other two phases and the local three phase supply voltages become unstable. One consequence of this is that the floating bit of the PEN conductor (the bit on the consumer side of the cable damage) can rise to a dangerously high voltage. This then causes the protective earth conductor in those homes to rise to the same high voltage.Not a problem indoors, as homes are an equipotential zone, with all conductive stuff bonded together. This is a problem for anything outdoors though, like an EV. The car body sill be connected to the incoming PEN conductor, and the ground around the car will be at or near true earth potential. A PEN fault then gives rise to an electric shock risk for anyone standing outside who touches the car.The fix if for either the charge point to include PEN fault protection (many do) or for PEN fault protection to be provided via a separate box in the supply, or by changing the house earthing system from TN-C-S to TT. The latter was my solution - I didn't bother to use the incoming PEN to provide a protective earth, and instead have this provided via an earth electrode.2
-
Grumpy_chap said:Here's something I never thought of.
Got an Electrician round today to quote the installation for the EV charger. He mentioned that before he can connect the EV charger load, both the incoming fuse and the meter will require uprating by the electricity supplier and the DNO. I doubt they'll be particularly quick, though the costs might not be too bad as set by the OFGEM (probably). I hope that can all be done without requiring the main incomer cable being changed.I think....0 -
Thanks for the explanation @JSHarris. Tesla chargers don't have built in PEN fault protection, so something needs to be done.I'm a Forum Ambassador on the housing, mortgages, student & coronavirus Boards, money saving boards. I volunteer to help get your forum questions answered and keep the forum running smoothly. Forum Ambassadors are not moderators and don't read every post. If you spot an illegal or inappropriate post then please report it to forumteam@moneysavingexpert.com (it's not part of my role to deal with this). Any views are mine and not the official line of MoneySavingExpert.com.2
-
michaels said:They are safe. For example I could install one here without adding anything and it would be perfectly safe. The issue is that they aren't specifically designed for the UK market, and the UK has an oddball electrical system where the distribution network can develop a potentially lethal fault.Lots of reasons as to why we have this system, but it mostly comes back to the same reason we have ring finals (the daftest and most unsafe arrangement possible IMHO). After WWII we were in deep debt. We needed to reduce imports and almost all the copper in wiring was imported. Both the adoption of ring finals and the adoption of PME (now called TN-C-S) reduced copper use. The use of PME reduced the copper needed for the LV network single phase cables by about a third, so was well worth doing at that time.4
-
I was just having a scan through the latest offerings from Tesla and came across this 0 miles M3P, supposedly at an £11k discount.
https://tesla-info.com/car/GB-LRW3286_c7c1388391cca9b1c731c8de62761bd4
Northern Lincolnshire. 7.8 kWp system, (4.2 kw west facing panels , 3.6 kw east facing), Solis inverters, Solar IBoost water heater, Mitsubishi SRK35ZS-S and SRK20ZS-S Wall Mounted Inverter Heat Pumps, ex Nissan Leaf owner)0 -
JKenH said:I was just having a scan through the latest offerings from Tesla and came across this 0 miles M3P, supposedly at an £11k discount.
https://tesla-info.com/car/GB-LRW3286_c7c1388391cca9b1c731c8de62761bd4
Not everything they have is listed on the website.0 -
1961Nick said:
I'll be amazed if you don't get delivery before the June quarter end.
A bit less happy when they called back to rearrange to 4 pm next Friday, 30th. That is "by the skin of the teeth" June...2 -
Grumpy_chap said:1961Nick said:
I'll be amazed if you don't get delivery before the June quarter end.
A bit less happy when they called back to rearrange to 4 pm next Friday, 30th. That is "by the skin of the teeth" June...
You're gonna love the TM3, but I suspect you'd be thrilled with any BEV, such a lovely driving experience, even for ex-petrolheads like me.Mart. Cardiff. 8.72 kWp PV systems (2.12 SSW 4.6 ESE & 2.0 WNW). 20kWh battery storage. Two A2A units for cleaner heating. Two BEV's for cleaner driving.
For general PV advice please see the PV FAQ thread on the Green & Ethical Board.3 -
JKenH said:I was just having a scan through the latest offerings from Tesla and came across this 0 miles M3P, supposedly at an £11k discount.
https://tesla-info.com/car/GB-LRW3286_c7c1388391cca9b1c731c8de62761bd44kWp (black/black) - Sofar Inverter - SSE(141°) - 30° pitch - North LincsInstalled June 2013 - PVGIS = 3400Sofar ME3000SP Inverter & 5 x Pylontech US2000B Plus & 3 x US2000C Batteries - 19.2kWh0
Confirm your email address to Create Threads and Reply

Categories
- All Categories
- 349.6K Banking & Borrowing
- 252.6K Reduce Debt & Boost Income
- 452.9K Spending & Discounts
- 242.6K Work, Benefits & Business
- 619.3K Mortgages, Homes & Bills
- 176.3K Life & Family
- 255.5K Travel & Transport
- 1.5M Hobbies & Leisure
- 16.1K Discuss & Feedback
- 15.1K Coronavirus Support Boards