  • Equaliser123
    Equaliser123 Posts: 3,404 Forumite
    Cardew wrote: »
    That will surely depend on the inverter.

    .

    Good point. Does that mean that my 3.29kwp panels will never actually produce more than 3kw due to my inverter being a 3kw type?

    The installers said that it would not be an issue if it ever went over its rating for a period of time.
  • zeupater
    zeupater Posts: 5,389 Forumite
    Part of the Furniture 1,000 Posts Name Dropper Combo Breaker
    So do you think those predicted figures might be correct after all?
    Hi

    For the first three months of your dataset the actuals are within 1.3% of the PVGIS prediction, and that's without knowing what inverter, panels, actual cable runs etc are ..... that's pretty good estimate in my opinion.

    As for February, well it was a particularly dull month and the Met-Office anomalies map set describes how bad it's been over the country as a whole, so I wouldn't worry too much about your particular bad performance ..... next year could be as good as 2008 to make up for it (check ot the Feb 2008 sunshine anomaly !!).

    It's all swings & roundabouts when considering single actual datasets v long term averages, but averaging a few years of your own production should provide a more stable correlation by smoothing out any major monthly anomalies such as we have experienced in February.

    HTH
    Z
    "We are what we repeatedly do, excellence then is not an act, but a habit. " ...... Aristotle
    B)
  • zeupater
    zeupater Posts: 5,389 Forumite
    Part of the Furniture 1,000 Posts Name Dropper Combo Breaker
    edited 5 March 2011 at 9:03PM
    Good point. Does that mean that my 3.29kwp panels will never actually produce more than 3kw due to my inverter being a 3kw type?

    The installers said that it would not be an issue if it ever went over its rating for a period of time.
    Hi

    In the rare case where your panels produce 3.29kW DC, plus whatever their output tolerance is, your inverter (assuming 3000W AC max) will limit the output to 3.00kW AC by 'clipping' any excess.

    Assuming that your panels are positive rated on nominal output tolerance, are brand new and therefore have not suffered any performance degradation, this will likely cost you a loss of around 22kWh per year with your setup (less than 1%) .....

    HTH
    Z
    "We are what we repeatedly do, excellence then is not an act, but a habit. " ...... Aristotle
    B)
  • Cardew
    Cardew Posts: 29,059 Forumite
    Part of the Furniture 10,000 Posts Name Dropper Rampant Recycler
    Good point. Does that mean that my 3.29kwp panels will never actually produce more than 3kw due to my inverter being a 3kw type?

    The installers said that it would not be an issue if it ever went over its rating for a period of time.

    It is important to appreciate just what kWp means in this context.

    Panels are given a standard rating for producing their power output in standard laboratory conditions with controlled 'sunlight' density(watts per M2) and ambient temperature.

    So your set of 3.29kWp panels would produce 3.29kW under those laboratory conditions. Those conditions exist roughly 35 degrees above and below the equater.

    Move your panels to, say Greenland and they will not exceed, say 2kW on the brightest day. Move them to the Equator and you might get, say 5kW. (2kW and 5kW are just to illustrate the principle)

    Depending where you live in UK will be a factor in the size of the inverter. There are also losses and the performance of panels deteriorates over the years.

    So the choice of the size of the inverter is down to the judgement of the installer. Presumably they felt that a 3kW inverter would be the best compromise for your site and system.

    However it is possible that the choice of a smaller inverter, was influenced by it being cheaper.

    More technical detail on kWp here:

    http://www.solar-facts-and-advice.com/kWp.html
  • jackieblack
    jackieblack Posts: 10,493 Forumite
    Part of the Furniture 10,000 Posts Name Dropper Photogenic
    zeupater wrote: »
    Hi

    For the first three months of your dataset the actuals are within 1.3% of the PVGIS prediction, and that's without knowing what inverter, panels, actual cable runs etc are ..... that's pretty good estimate in my opinion.

    As for February, well it was a particularly dull month and the Met-Office anomalies map set describes how bad it's been over the country as a whole, so I wouldn't worry too much about your particular bad performance ..... next year could be as good as 2008 to make up for it (check ot the Feb 2008 sunshine anomaly !!).

    It's all swings & roundabouts when considering single actual datasets v long term averages, but averaging a few years of your own production should provide a more stable correlation by smoothing out any major monthly anomalies such as we have experienced in February.

    HTH
    Z

    Thanks zeupater, I wasn't sure that I'd put the info in correctly, but having looked at those met office maps maybe I did it ok after all! :):o
    2.22kWp Solar PV system installed Oct 2010, Fronius IG20 Inverter, south facing (-5 deg), 30 degree pitch, no shading
    Everything will be alright in the end so, if it’s not yet alright, it means it’s not yet the end
    MFW #4 OPs: 2018 £866.89, 2019 £1322.33, 2020 £1337.07
    2021 £1250.00, 2022 £1500.00, 2023 £1500, 2024 £1350
    2025 target = £1200, YTD £690
    Quidquid Latine dictum sit altum videtur
  • Equaliser123
    Equaliser123 Posts: 3,404 Forumite
    Cardew wrote: »
    It is important to appreciate just what kWp means in this context.

    Panels are given a standard rating for producing their power output in standard laboratory conditions with controlled 'sunlight' density(watts per M2) and ambient temperature.

    So your set of 3.29kWp panels would produce 3.29kW under those laboratory conditions. Those conditions exist roughly 35 degrees above and below the equater.

    Move your panels to, say Greenland and they will not exceed, say 2kW on the brightest day. Move them to the Equator and you might get, say 5kW. (2kW and 5kW are just to illustrate the principle)

    Depending where you live in UK will be a factor in the size of the inverter. There are also losses and the performance of panels deteriorates over the years.

    So the choice of the size of the inverter is down to the judgement of the installer. Presumably they felt that a 3kW inverter would be the best compromise for your site and system.

    However it is possible that the choice of a smaller inverter, was influenced by it being cheaper.

    More technical detail on kWp here:

    http://www.solar-facts-and-advice.com/kWp.html

    Thanks. I was told - several times - that the smaller inverters work better.

    Appreciate the point that the rating is under lab conditions. A touch misleading though.
  • Equaliser123
    Equaliser123 Posts: 3,404 Forumite
    Thanks. I was told - several times - that the smaller inverters work better.

    Appreciate the point that the rating is under lab conditions. A touch misleading though.

    Hit the inverters limit today for 30 mins or so on and off. 3kw recorded on my SunnyBeam.

    Now if I had a larger inverter, I wonder if I would have hit the 3.29kwp....
  • free_juice?
    free_juice? Posts: 92 Forumite
    Where are you? There wasn't even two minutes of sunshine in the SE. My 3kW inverter logged 1139.05 at 1pm, next highest 761W and apart from that sub 500.
    Hi, we’ve had to remove your signature. If you’re not sure why please read the forum rules or email the forum team if you’re still unsure - MSE ForumTeam
  • Equaliser123
    Equaliser123 Posts: 3,404 Forumite
    Where are you? There wasn't even two minutes of sunshine in the SE. My 3kW inverter logged 1139.05 at 1pm, next highest 761W and apart from that sub 500.

    Ha! South Wales. I must confess, I was surprised.

    Had a poor morning (only about 2kw/h produced up to midday) but as our panels our WSW facing, we tend to generate more later. 1400 - 3kw for 30 mins. Managed 9.5kw/h for the day.

    To be fair, whilst a nice day, there have been other nice days where the generation is only 2.2-2.4kw. Today didn't seem especially bright although clearly the panels were happy!
  • Cardew
    Cardew Posts: 29,059 Forumite
    Part of the Furniture 10,000 Posts Name Dropper Rampant Recycler
    Crisp clear and sunny, without a cloud in the sky, here in the Midlands.

    Standing by for 'highest of the year' reports after 6pm!!!!
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 350.9K Banking & Borrowing
  • 253.1K Reduce Debt & Boost Income
  • 453.5K Spending & Discounts
  • 243.9K Work, Benefits & Business
  • 598.7K Mortgages, Homes & Bills
  • 176.9K Life & Family
  • 257.2K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16.1K Discuss & Feedback
  • 37.6K Read-Only Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.