  • martin2020
    martin2020 Posts: 51 Forumite
    Fourth Anniversary 10 Posts Name Dropper
    chamelion said:
    Do any of you folks' LUX buzz? Mine has a quite distinct buzzing sound when idle... 
    mine buzzed when i set the reactive power to 50 percent as stated in this thread, i reduced it down to 10 and the buzzing stops - any lower than 7 and my inverter switches from battery to grid every few minutes when my house is runnning at base load.

    id love a propper explanations of what some of these settings do
    I asked them about this and got this reply, still not really sure what those settings do.

    Q) Also a little more info on the Active Power Percent% and Reactive Power Percent% would help

    A) This setting may influence on the solar performance only when you set output reactive power very large and set output reactive power . In your setting, you set PF=1 (Unit power factor), so it is OK, it will not influnce solar, the reactive power percent is useless


    Very strange that it could effect solar,  i wonder what they mean by this.
    ive played around with these settings for weeks and the only stable setup for me is over reactive power at about 14%. yet the same settings dont  work as good for my brothers lux  which has to be on under reactive power, so i dunno maybe im overthinking it and asking for too much of it.
    Anything else and i see vast switching when the solar inverter comes on and takes over in a morning.
  • htsoft
    htsoft Posts: 27 Forumite
    Third Anniversary 10 Posts
    martin2020 said:
    Very strange that it could effect solar,  i wonder what they mean by this.
    ive played around with these settings for weeks and the only stable setup for me is over reactive power at about 14%. yet the same settings dont  work as good for my brothers lux  which has to be on under reactive power, so i dunno maybe im overthinking it and asking for too much of it.
    Anything else and i see vast switching when the solar inverter comes on and takes over in a morning.

    Similar here: tried a few different setups there, lots of contactor switching at sunrise/sunset when the inverter goes into standby/charge/discharge. Right now it's on 3% over reactive, slight buzzing sometimes plus fewer switches than on "0" setup. Haven't tried under reactive yet though....
    3kW solar PV, Lux 3600 with 4 Pylontech batteries
    Tesla Model 3 SR+
  • I have asked them for further clarification along with a couple of other queries.
  • EVandPV
    EVandPV Posts: 2,112 Forumite
    Fifth Anniversary 1,000 Posts Name Dropper
    EVandPV said:
    I think the Batteryview app can tell us Lux users how many cycles we've had from the Pylons, a feature currently missing from the web portal data.
    The figure highlighted in this screenshot would appear to be in the right ball park for my system and if I'm not mistaken, shows the total number of charge/discharge cycles.



    We've had the batteries for 95 days so that would be about 1.3 cycles per day, which seems about right.
    Strangely, there is a heading for cycle data but the figures bare no relation to our system, there's no way it could have done 2043 cycles in 95 days !
    Hi EVandPV where do you get the batteryview app from please?
    https://www.dropbox.com/s/d2lopix9jqghofq/Batteryview.rar?dl=0

    https://www.dropbox.com/s/vacsk4v3icnjhg8/BatteryView 20181220-低压.zip?dl=0


    Scott in Fife, 2.9kwp pv SSW facing, 2.7kw Fronius inverter installed Jan 2012 - 14.3kwh Seplos Mason battery storage with Lux ac controller - Renault Zoe 40kwh, Corsa-e 50kwh, Zappi EV charger and Octopus Go
  • TheMaster_2
    TheMaster_2 Posts: 22 Forumite
    Part of the Furniture 10 Posts Name Dropper Combo Breaker
    htsoft said:
    martin2020 said:
    Very strange that it could effect solar,  i wonder what they mean by this.
    ive played around with these settings for weeks and the only stable setup for me is over reactive power at about 14%. yet the same settings dont  work as good for my brothers lux  which has to be on under reactive power, so i dunno maybe im overthinking it and asking for too much of it.
    Anything else and i see vast switching when the solar inverter comes on and takes over in a morning.

    Similar here: tried a few different setups there, lots of contactor switching at sunrise/sunset when the inverter goes into standby/charge/discharge. Right now it's on 3% over reactive, slight buzzing sometimes plus fewer switches than on "0" setup. Haven't tried under reactive yet though....
    I asked some more questions, here these are the responses, hope it help!

    Q) I am trying to stop the invertor from importing energy when there is power in the batteries, do these settings effect import/export at all? In your last email it mentions the below, how does this affect solar performance?

    "This setting may influence on the solar performance only when you set output reactive power very large and set output reactive power"

     

     A) For import power, can you please shoot some picture when you see import and then we will analysis for you, there are serveral reasons for import: 

    (1) Solar power + battery discharge power ability < the power your load take

    (2) when sunshine decrease suddenly or the load increase suddenly, then inverter need time to adjust

     For reactive power setting, sorry that I forget that your inverter is AC coupled inverter, so the settings of AC coupled inverter will not have influence on on grid inverter power generation

     


     Q) Are you working with Octopus Energy in the UK on any kind of integration/API for their Agile tariff for battery charging?

    A) yes, we are working with Octopus and we have test several  units to charge at lowest cost automatically, it worked.  if you want to add in our test list, you can contact our UK partner Jake (I copied in the email)and he will help you.

    Q) Lastly is the parallel LUX invertor solution working now to run 2 invertors in parallels so I can get 7kWH output as I am looking to purchase a 2nd one, and is it better to run my 6 batteries shared or split into 2 x 3 ?

     A) For batteries, both solutions are OK, battery together or seperated.


  • chamelion
    chamelion Posts: 483 Forumite
    Part of the Furniture 100 Posts Name Dropper
    htsoft said:
    martin2020 said:
    Very strange that it could effect solar,  i wonder what they mean by this.
    ive played around with these settings for weeks and the only stable setup for me is over reactive power at about 14%. yet the same settings dont  work as good for my brothers lux  which has to be on under reactive power, so i dunno maybe im overthinking it and asking for too much of it.
    Anything else and i see vast switching when the solar inverter comes on and takes over in a morning.

    Similar here: tried a few different setups there, lots of contactor switching at sunrise/sunset when the inverter goes into standby/charge/discharge. Right now it's on 3% over reactive, slight buzzing sometimes plus fewer switches than on "0" setup. Haven't tried under reactive yet though....
    I asked some more questions, here these are the responses, hope it help!

    Q) I am trying to stop the invertor from importing energy when there is power in the batteries, do these settings effect import/export at all? In your last email it mentions the below, how does this affect solar performance?

    "This setting may influence on the solar performance only when you set output reactive power very large and set output reactive power"

     

     A) For import power, can you please shoot some picture when you see import and then we will analysis for you, there are serveral reasons for import: 

    (1) Solar power + battery discharge power ability < the power your load take

    (2) when sunshine decrease suddenly or the load increase suddenly, then inverter need time to adjust

     For reactive power setting, sorry that I forget that your inverter is AC coupled inverter, so the settings of AC coupled inverter will not have influence on on grid inverter power generation

     


     Q) Are you working with Octopus Energy in the UK on any kind of integration/API for their Agile tariff for battery charging?

    A) yes, we are working with Octopus and we have test several  units to charge at lowest cost automatically, it worked.  if you want to add in our test list, you can contact our UK partner Jake (I copied in the email)and he will help you.

    Q) Lastly is the parallel LUX invertor solution working now to run 2 invertors in parallels so I can get 7kWH output as I am looking to purchase a 2nd one, and is it better to run my 6 batteries shared or split into 2 x 3 ?

     A) For batteries, both solutions are OK, battery together or seperated.


    For octopus question, just use octolux? Works perfect. 
    5.41 kWp System, E-W. Installed Nov 2017
    Lux + 3 x US2000B + 2 x US3000C battery storage. Installed Mar 2020.
  • TheMaster_2
    TheMaster_2 Posts: 22 Forumite
    Part of the Furniture 10 Posts Name Dropper Combo Breaker
    chamelion said:
    htsoft said:
    martin2020 said:
    Very strange that it could effect solar,  i wonder what they mean by this.
    ive played around with these settings for weeks and the only stable setup for me is over reactive power at about 14%. yet the same settings dont  work as good for my brothers lux  which has to be on under reactive power, so i dunno maybe im overthinking it and asking for too much of it.
    Anything else and i see vast switching when the solar inverter comes on and takes over in a morning.

    Similar here: tried a few different setups there, lots of contactor switching at sunrise/sunset when the inverter goes into standby/charge/discharge. Right now it's on 3% over reactive, slight buzzing sometimes plus fewer switches than on "0" setup. Haven't tried under reactive yet though....
    I asked some more questions, here these are the responses, hope it help!

    Q) I am trying to stop the invertor from importing energy when there is power in the batteries, do these settings effect import/export at all? In your last email it mentions the below, how does this affect solar performance?

    "This setting may influence on the solar performance only when you set output reactive power very large and set output reactive power"

     

     A) For import power, can you please shoot some picture when you see import and then we will analysis for you, there are serveral reasons for import: 

    (1) Solar power + battery discharge power ability < the power your load take

    (2) when sunshine decrease suddenly or the load increase suddenly, then inverter need time to adjust

     For reactive power setting, sorry that I forget that your inverter is AC coupled inverter, so the settings of AC coupled inverter will not have influence on on grid inverter power generation

     


     Q) Are you working with Octopus Energy in the UK on any kind of integration/API for their Agile tariff for battery charging?

    A) yes, we are working with Octopus and we have test several  units to charge at lowest cost automatically, it worked.  if you want to add in our test list, you can contact our UK partner Jake (I copied in the email)and he will help you.

    Q) Lastly is the parallel LUX invertor solution working now to run 2 invertors in parallels so I can get 7kWH output as I am looking to purchase a 2nd one, and is it better to run my 6 batteries shared or split into 2 x 3 ?

     A) For batteries, both solutions are OK, battery together or seperated.


    For octopus question, just use octolux? Works perfect. 
    Yeah I was just wondering if they were doing something ala Tesla
  • mickyduck55
    mickyduck55 Posts: 676 Forumite
    Fifth Anniversary 500 Posts Name Dropper
    Looks like a new metric added top the LUX web portal usage  graph.. "consumption"

    3.995kWP SSW facing. Commissioned 7 July 2011. 24 degree pitch (£3.36 /W).
    17 Yingli 235 panels
    Sunnyboy 4000TL inverter
    Sunny Webox
    Solar Immersion installed May 2013, after two Solar Immersion lasting just over the guarantee period replaced with Solic 200... no problems since.

    13 Feb 2020 LUX AC 3600 and 3 X Pylon Tech 3.5 kW batteries added...

    20 January 2024 Daikin ASHP installed
  • EVandPV
    EVandPV Posts: 2,112 Forumite
    Fifth Anniversary 1,000 Posts Name Dropper
    Looks like Agile integration is here now .....

    https://www.homeenergygroup.co.uk/power-pod
    Scott in Fife, 2.9kwp pv SSW facing, 2.7kw Fronius inverter installed Jan 2012 - 14.3kwh Seplos Mason battery storage with Lux ac controller - Renault Zoe 40kwh, Corsa-e 50kwh, Zappi EV charger and Octopus Go
  • chamelion
    chamelion Posts: 483 Forumite
    Part of the Furniture 100 Posts Name Dropper
    EVandPV said:
    Looks like Agile integration is here now .....

    https://www.homeenergygroup.co.uk/power-pod
    I don't get it... it says lux power pod. Is that them just grouping together batts + the standard inverter with a firmware upgrade to manage agile fluctuations?
    Or is there added hardware expected?
    5.41 kWp System, E-W. Installed Nov 2017
    Lux + 3 x US2000B + 2 x US3000C battery storage. Installed Mar 2020.
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 350.1K Banking & Borrowing
  • 252.8K Reduce Debt & Boost Income
  • 453.1K Spending & Discounts
  • 243.1K Work, Benefits & Business
  • 597.4K Mortgages, Homes & Bills
  • 176.5K Life & Family
  • 256K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16.1K Discuss & Feedback
  • 37.6K Read-Only Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.