frslam said:
It's very easy to do. My previous post shows how I did it today because of exactly the same problem. You could also turn up the pump to 3 if not already, but that's masking the real problem which is likely a blockage somewhere.
The delta you have is over spec (should be 6-10, alarms at 13) but it's not crazy high, so it needs sorting but it's not disastrous.
The - thing is nothing to worry about. When it gets to I think 32768 hours it rolls over to - 32768 and carries on counting up from there. It's because the rego 637 control unit holds that value in a variable that is too small really.1 -
It's very easy to do. My previous post shows how I did it today because of exactly the same problem. You could also turn up the pump to 3 if not already, but that's masking the real problem which is likely a blockage somewhere.
The delta you have is over spec (should be 6-10, alarms at 13) but it's not crazy high, so it needs sorting but it's not disastrous.
The - thing is nothing to worry about. When it gets to I think 32768 hours it rolls over to - 32768 and carries on counting up from there. It's because the rego 637 control unit holds that value in a variable that is too small really.
0 -
frslam said:It's very easy to do. My previous post shows how I did it today because of exactly the same problem. You could also turn up the pump to 3 if not already, but that's masking the real problem which is likely a blockage somewhere.
The delta you have is over spec (should be 6-10, alarms at 13) but it's not crazy high, so it needs sorting but it's not disastrous.
The - thing is nothing to worry about. When it gets to I think 32768 hours it rolls over to - 32768 and carries on counting up from there. It's because the rego 637 control unit holds that value in a variable that is too small really.
Turn off power to the unit.
Turn off all 4 external valves (2 x DHW and 2 x CH). No need to turn off the ground loop.
Turn off the internal valve on the return flow (the one with the filter in it, just after where the DHW and CH returns join)
Turn off the valve on the bottom of the heat carrier pump.
Undo the bottom flexible hose from the bottom of the pump and put the end in a bowl or some such
Undo the top flexible hose from the bottom of the electric cassette, but not completely. Just enough to let air in so that water flows out of the bottom hose.
Allow to drain. This will take a while. You can speed it up by removing the top hose completely, but you'll need to be ready to catch the water coming out of the cassette, which is a lot more than you think it'll be (trust me :-))
Completely remove both top and bottom flexible hoses at both ends
Flush through both
Refit, turn on all the valves and power up. I then ran the heat carrier pump manually for a bit until it stopped gurgling, otherwise you'll be running the heat exchanger with no water in it and likely to get a high pressure alarm on the compressor side.1 -
beardymarrow said:Patrol said:lstevensuk said:Anyone know of an engineer in Bedfordshire area? I normally use Alto Energy.
You could try just replacing the capacitors in the soft start. They are just cable tied into the soft start box and the most likely failure mode. Be very careful as even with the power disconnected they will pack an almighty punch if you touch the connectors and they aren't faulty.
Alternatively a whole new soft start unit is about £650.
https://www.ivtspares.co.uk/collections/ivt-greenline-ht-e9-1x230v/products/ivtsp10209
(although you'd need exactly the right one for your unit, this is just an example for an HT+ E9 which is what I have).
Compressor would be about £1500 https://www.ivtspares.co.uk/collections/ivt-greenline-ht-e9-1x230v/products/ivtsp10055 and that's definitely not a DIY job due to the refrigerant (so hopefully it's not that) :-)
JS Energi also do spares - https://jsenergi.co.uk/ivt-spare-parts/by-model/ivt-greenline-ht-plus-e9.html
Thank you again! Definitely going to try replacing the capcitors first. Wasn't expecting a bill that big
0 -
lstevensuk said:beardymarrow said:Patrol said:lstevensuk said:Anyone know of an engineer in Bedfordshire area? I normally use Alto Energy.
You could try just replacing the capacitors in the soft start. They are just cable tied into the soft start box and the most likely failure mode. Be very careful as even with the power disconnected they will pack an almighty punch if you touch the connectors and they aren't faulty.
Alternatively a whole new soft start unit is about £650.
https://www.ivtspares.co.uk/collections/ivt-greenline-ht-e9-1x230v/products/ivtsp10209
(although you'd need exactly the right one for your unit, this is just an example for an HT+ E9 which is what I have).
Compressor would be about £1500 https://www.ivtspares.co.uk/collections/ivt-greenline-ht-e9-1x230v/products/ivtsp10055 and that's definitely not a DIY job due to the refrigerant (so hopefully it's not that) :-)
JS Energi also do spares - https://jsenergi.co.uk/ivt-spare-parts/by-model/ivt-greenline-ht-plus-e9.html
Thank you again! Definitely going to try replacing the capcitors first. Wasn't expecting a bill that big
I haven't looked into my soft starter box in depth to know if it's just that module and the caps that make it up, but I would assume so. I might do that over the weekend as you've sparked my interest.
Either way, I'd go for swapping the caps first myself as they're the most likely to fail and they'll be the cheapest. You might end up throwing money away and having to buy the whole unit anyway, but for me it's worth the chance.
Edit: Removed the link to the other supplier of the soft starter electronics as it's not the right one. The one on my HT+ E11 is a Danfoss TCI 25C 037N0086 (plus run and start caps).0 -
Yes agree don't want to throw money down the drain. Fingers crossed it's just them! Thanks a million!!Oh by the way I'm a software developer so would be very interested in the raspberry Pi bits on a geek level0
-
lstevensuk said:Yes agree don't want to throw money down the drain. Fingers crossed it's just them! Thanks a million!!Oh by the way I'm a software developer so would be very interested in the raspberry Pi bits on a geek level0
-
beardymarrow said:lstevensuk said:Yes agree don't want to throw money down the drain. Fingers crossed it's just them! Thanks a million!!Oh by the way I'm a software developer so would be very interested in the raspberry Pi bits on a geek level1
-
lstevensuk said:beardymarrow said:Patrol said:lstevensuk said:Anyone know of an engineer in Bedfordshire area? I normally use Alto Energy.
You could try just replacing the capacitors in the soft start. They are just cable tied into the soft start box and the most likely failure mode. Be very careful as even with the power disconnected they will pack an almighty punch if you touch the connectors and they aren't faulty.
Alternatively a whole new soft start unit is about £650.
https://www.ivtspares.co.uk/collections/ivt-greenline-ht-e9-1x230v/products/ivtsp10209
(although you'd need exactly the right one for your unit, this is just an example for an HT+ E9 which is what I have).
Compressor would be about £1500 https://www.ivtspares.co.uk/collections/ivt-greenline-ht-e9-1x230v/products/ivtsp10055 and that's definitely not a DIY job due to the refrigerant (so hopefully it's not that) :-)
JS Energi also do spares - https://jsenergi.co.uk/ivt-spare-parts/by-model/ivt-greenline-ht-plus-e9.html
Thank you again! Definitely going to try replacing the capcitors first. Wasn't expecting a bill that big
I was curious so I have just been out to check the resistance of my capacitors and the compressor, so I know in future if I have the same problem is it the capacitors or is it the compressor. This is on my IVT HT+ E9, so your values may differ slightly.
With everything wired up, but the GSHP switched off
Compressor Run Winding 1.5ohms - Terminal 2/N (Common Blue Wire) to 4/T1 (Run Black Wire) on the Danfoss Soft Starter
Compressor Start Winding 2.3ohms - Terminal 2/N (Common Blue Wire) to Brown Wire connected to Run Capacitor (Smaller silver one) (or Terminal 2 on Start Relay)
Capacitors - Check for short circuit. You should get a reading across the terminals which will then rise to open circuit (OL). This is easiest to check by checking between 1/N and 3/L1 on the Soft Starter.0
Confirm your email address to Create Threads and Reply

Categories
- All Categories
- 350.8K Banking & Borrowing
- 253.1K Reduce Debt & Boost Income
- 453.5K Spending & Discounts
- 243.8K Work, Benefits & Business
- 598.7K Mortgages, Homes & Bills
- 176.8K Life & Family
- 257.1K Travel & Transport
- 1.5M Hobbies & Leisure
- 16.1K Discuss & Feedback
- 37.6K Read-Only Boards