    NigeWick said:
    Interesting about the microbore. 
    When the Cosy 6 comes out it won't matter as that heat pump can produce the same temperature as a gas boiler.
    Yes, but at a cost in COP. A heat pump will always be more efficient at lower flow temperatures. Also, an overlay underfloor heating system will add a bit of insulation to the uninsulated solid concrete floor. Getting rid of radiators will also be more aesthetically pleasing, as well as making rooms more adaptable in use.
  • Reed_Richards
    Reed_Richards Posts: 5,341 Forumite
    Part of the Furniture 1,000 Posts Photogenic Name Dropper
    edited 6 October 2023 at 7:10AM
    Just to echo @Netexporter's comment.  The thing you absolutely have to realise about heat pumps is that even if they can produce the same water temperature as a gas boiler (older type) you don't want them to!  

    Heat pumps tend to be set up for a small temperature drop across your radiators, typically 5 C.  To achieve this they pump the water round the heating system a lot faster than with gas or oil.  The reason microbore pipes have been disliked is that they cannot sustain these high flow rates if they get a bit clogged.  If Octopus thinks they can cope with microbore pipes then good for them, but I wonder what they would do if there turned out to be a problem. 
    Reed
  • Meatballs
    Meatballs Posts: 587 Forumite
    Part of the Furniture 500 Posts Name Dropper Combo Breaker
    Afaik most octopus installs use a buffer (from pictures I have seen) which helps to eliminate the issues with microbore, but comes at a slight drop in efficiency.

    Buffer maybe  helps (slightly as I don't think they use huge ones) with time of use tariffs as it is a small heat store...
  • saf87
    saf87 Posts: 27 Forumite
    Part of the Furniture 10 Posts Combo Breaker
    I recently had a survey with octopus. My property is 10mm plastic microbore and they said this was no longer a problem for them and that they will even accept 8mm microbore as long as it's copper. My issue was not having enough space for the cylinder, buffer and expansion vessel. A bit gutted as it was only going to be £1,100 after the grant. 
  • NigeWick
    NigeWick Posts: 2,729 Forumite
    Part of the Furniture 1,000 Posts Name Dropper Debt-free and Proud!
    At a tariff specifically designed for it. I'm curious what the heat pumps efficiency/ SCOP will be when running anything over 55 degrees flow temperature. 
    Ask Octopus. Are you sure there's only the one tariff allowed with the Cosy 6?
    The mind of the bigot is like the pupil of the eye; the more light you pour upon it, the more it will contract.
    Oliver Wendell Holmes
  • Screwdriva
    Screwdriva Posts: 1,525 Forumite
    Fifth Anniversary 1,000 Posts Name Dropper Photogenic
    edited 6 October 2023 at 9:52AM
    NigeWick said:
    Ask Octopus. Are you sure there's only the one tariff allowed with the Cosy 6?
    When I did ask for SCOP details, I was told "to be announced". The tariff is designed to be lucrative for the Cosy 6 owner, so while it's not exclusive to one tariff, it is likely to be the one that makes the most financial sense. When I asked if Octopus were planning to use financial incentives to overcome suboptimal system efficiency, I got radio silence back. 
    -  10 x 400w LG + 6 x 550W SHARP BiFacial Panels + SE 3680 HD Wave Inverter + SE Optimizers. SE London.
    -  Triple aspect. (22% ENE/ 33% SSE/ 45% WSW)
    -  Viessmann 200-W on Advanced Weather Comp. (the most efficient gas boiler sold)

    Feel free to DM me if I can help with any energy saving!
  • 1961Nick
    1961Nick Posts: 2,107 Forumite
    Tenth Anniversary 1,000 Posts Name Dropper
    NigeWick said:
    Ask Octopus. Are you sure there's only the one tariff allowed with the Cosy 6?
    When I did ask for SCOP details, I was told "to be announced". The tariff is designed to be lucrative for the Cosy 6 owner, so while it's not exclusive to one tariff, it is likely to be the one that makes the most financial sense. When I asked if Octopus were planning to use financial incentives to overcome suboptimal system efficiency, I got radio silence back. 
    They're being very tight lipped about the SCOP - even off the record. My hypothesis of 3 was met with virtually no resistance & the added comment that a customised tariff would ensure parity with the cost of gas heating.

    If they have achieved an SCOP of 3 with the capability to flow at over 70C when required, then that's a significant achievement imo.
    4kWp (black/black) - Sofar Inverter - SSE(141°) - 30° pitch - North Lincs
    Installed June 2013 - PVGIS = 3400
    Sofar ME3000SP Inverter & 5 x Pylontech US2000B Plus & 3 x US2000C Batteries - 19.2kWh
  • QrizB said:
    I can only dream of getting a quote from Octopus for solar or a heat pump.
    Have you tried the "quote me" link?
    Yes, frequently. They don't do Wales. I was mildly shocked to find that you can't even get a quote in Cardiff. I live in the middle of nowhere in middlest Mid-Wales, so I can understand it, to an extent. Took nearly a year to get my smart meter fitted because the nearest installers are in Swansea.
    I live in Cardiff.  I registered my interest in a HP with Octopus, who emailed me to say 'Not yet, but we hope to have approved installers by end of summer 2023'  - not been contacted yet ......
  • orbit500
    orbit500 Posts: 54 Forumite
    Tenth Anniversary 10 Posts Name Dropper Combo Breaker
    If they have achieved an SCOP of 3 with the capability to flow at over 70C when required, then that's a significant achievement imo.
    I will believe that when I see it. I’m sure many here already know this but there is a limit to heat pump efficiency given by:
    COP=T1/deltaT where T1=flow temp in kelvin and deltaT=flow-outdoor temp.
    so at 70c and 0c outdoor (which is when you’d want 70c flow):
    CoP=343/(70-0) = 4.9
    in real life more likely 2, I’d say.
  • Reed_Richards
    Reed_Richards Posts: 5,341 Forumite
    Part of the Furniture 1,000 Posts Photogenic Name Dropper
    It's the people who don't know this that you need to reach.  Those who get really enthusiastic about high temperature heat pumps.
    Reed
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 351.2K Banking & Borrowing
  • 253.2K Reduce Debt & Boost Income
  • 453.7K Spending & Discounts
  • 244.2K Work, Benefits & Business
  • 599.2K Mortgages, Homes & Bills
  • 177K Life & Family
  • 257.6K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16.1K Discuss & Feedback
  • 37.6K Read-Only Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.