Ecodan - are these COP figures correct?
Comments
-
I don't know. I'm not sure what 'prohibitive mode' is though. Can you explain?
I just switch the thermostats down and the heating stays off0 -
Ive just found this in the pdf handbook https://library.mitsubishielectric.co.uk/pdf/download_full/2387
Perhaps I need to actually Stop it rather than Prohibit it.
0 -
Maybe. I can't see how prohibiting would be any different to what I'm doing but I don't know.0
-
shinytop said:Maybe. I can't see how prohibiting would be any different to what I'm doing but I don't know.
Ive looked all through the Ecodan settings and cant find a Stop button. I only have Start/Prohibit/Schedule.
As it happens, Mitsubishi are sending an engineer out next week (for free!). I must say, they are responsive with their emails.
Im going to write a short list of questions to ask the engineer. If theres any specific questions you have Im happy to ask him for you.1 -
That's good of you to offer; I'll let you know.0
-
Hi guys,
An update:
The Mitsubishi engineer was here. Very helpful chap (he was here for about 4 hours!).
He said the strainer filter was partially blocked. This improved the flow from 6 litres to 23 litres. The Delta T has changed from 18 degrees to 4 degrees. He also insulated the pocket where the DMW sensor is, because even though it looks like I had the DHW set to 45 degrees, it may have actually been up to 10 degrees more. Now he's insulated the pocket it should give a more accurate reading.
He said the above should certainly help improve things.
I must say, the above is lost on me. does it make sense? He showed me how to clean the filter. It will be interesting to gauge how the next few week go.0 -
dllive said:Hi guys,
An update:
The Mitsubishi engineer was here. Very helpful chap (he was here for about 4 hours!).
He said the strainer filter was partially blocked. This improved the flow from 6 litres to 23 litres. The Delta T has changed from 18 degrees to 4 degrees. He also insulated the pocket where the DMW sensor is, because even though it looks like I had the DHW set to 45 degrees, it may have actually been up to 10 degrees more. Now he's insulated the pocket it should give a more accurate reading.
He said the above should certainly help improve things.
I must say, the above is lost on me. does it make sense? He showed me how to clean the filter. It will be interesting to gauge how the next few week go.
It's really important to install the temp sensors properly. If it's not insulated properly it will read low so the water will end up hotter than you've set it. You should just about be able to hold your hand under 45 degrees indefinitely whereas 55 can scald.1 -
shinytop said:dllive said:Hi guys,
An update:
The Mitsubishi engineer was here. Very helpful chap (he was here for about 4 hours!).
He said the strainer filter was partially blocked. This improved the flow from 6 litres to 23 litres. The Delta T has changed from 18 degrees to 4 degrees. He also insulated the pocket where the DMW sensor is, because even though it looks like I had the DHW set to 45 degrees, it may have actually been up to 10 degrees more. Now he's insulated the pocket it should give a more accurate reading.
He said the above should certainly help improve things.
I must say, the above is lost on me. does it make sense? He showed me how to clean the filter. It will be interesting to gauge how the next few week go.
It's really important to install the temp sensors properly. If it's not insulated properly it will read low so the water will end up hotter than you've set it. You should just about be able to hold your hand under 45 degrees indefinitely whereas 55 can scald.
He said that - if the flow rate had dropped any further - I would have got 'LF errors'.
So Im pleased I took action and the engineer came out. Ill give it a few weeks and post an update.3 -
Hi guys,
Just thought Id reignite this thread.
Ive just checked the air source heat pump stats, and its still showing a high consumption for doing nothing than heating the cylinder for 30 minutes every 2 days.
These are the last 2 logs Ive taken:1 September 2022Consumed: 85kwh (13 for DHW; 71 for heating); Delivered: 46kwh (46 for DHW; 0 for heating)Immersion: 0Heat pump meter reading: 13751kwhDHW COP: 3.5Heating COP: 0Overall COP = 0.5Meter reading: 49245kwhKWh used TWO weeks: 69_________________________15 September 2022Consumed: 37kwh (5 for DHW; 31 for heating); Delivered: 20kwh (20 for DHW; 0 for heating)Immersion: 0Heat pump meter reading: 13764kwhDHW COP: 4Heating COP: 4Overall COP = 0.5Meter reading: 49294KWh used TWO weeks: 49
So why has it consumed 31kwh for heating when it has delivered 0 (because I have the heating turned off) ?
And why does it shows its consumed 85kwh but the Heat pump meter reading shows the systems used 13kwh? (13764 - 13751 = 13)?
Very odd. Im probably missing something obvious.
Thanks
0
Confirm your email address to Create Threads and Reply

Categories
- All Categories
- 351.7K Banking & Borrowing
- 253.4K Reduce Debt & Boost Income
- 454K Spending & Discounts
- 244.7K Work, Benefits & Business
- 600.1K Mortgages, Homes & Bills
- 177.3K Life & Family
- 258.3K Travel & Transport
- 1.5M Hobbies & Leisure
- 16.2K Discuss & Feedback
- 37.6K Read-Only Boards