Is this boiler flue positioned incorrectly? Engineer won’t issue landlord certificate
Comments
-
Money_Grabber13579 said:jefaz07 said:ComicGeek said:jefaz07 said:ComicGeek said:jefaz07 said:ComicGeek said:This shows it better https://www.worcester-bosch.co.uk/downloads/gas-hoziontal-and-vertical-flue-terminal-positioning.pdf
Its 25mm minimum below the eaves as long as the boiler flue is extended beyond the line of the gutter - yours isn't, so needs to be either 200mm below eaves or extended out past the gutter.
Should also be minimum 300mm from the corner, which yours isn't.Definitely not installed correctly.
You don't need to extend beyond the eaves. That is fine!
Youre using a Worcester manual for a Baxi!
You could also look up the same diagram in Part J of the Building Regulations, it still says 300mm minimum from a corner (p50). That hasn't changed since 2005.
Here's a random Baxi install manual I had on a recent project https://www.baxi.co.uk/our-boilers/combi-boilers/-/media/websites/baxiuk/files/product-literature/baxi-600-combi/baxi_600_combi_installation_and_service_manual.pdf?la=en&hash=59F4684A32860F2FCAB0F51E652F9FD09EFC064D
See p33 - the flue is close to the downpipe so the multiple 25mm minimum distances can't be applied, see note 2. So 300mm from internal corner, and 200mm below eaves.
Pretty clear to me. You can always go back to BS 5440 for detail - don't blindly trust manufacturers info, they get it wrong sometimes.
Stop looking at all other ot random manuals that suit your arguments, look at the one for this boiler. What does it say? I agree the caveats are the same and in think looking at those pucs theyre above 25mm so in my opinion It is installed to MI's. Therefore it's absolutely fine.
BS do not in anyway get in the way of MI's.
But as I say, that’s a lay persons view…0 -
jefaz07 said:ComicGeek said:jefaz07 said:ComicGeek said:jefaz07 said:ComicGeek said:This shows it better https://www.worcester-bosch.co.uk/downloads/gas-hoziontal-and-vertical-flue-terminal-positioning.pdf
Its 25mm minimum below the eaves as long as the boiler flue is extended beyond the line of the gutter - yours isn't, so needs to be either 200mm below eaves or extended out past the gutter.
Should also be minimum 300mm from the corner, which yours isn't.Definitely not installed correctly.
You don't need to extend beyond the eaves. That is fine!
Youre using a Worcester manual for a Baxi!
You could also look up the same diagram in Part J of the Building Regulations, it still says 300mm minimum from a corner (p50). That hasn't changed since 2005.
Here's a random Baxi install manual I had on a recent project https://www.baxi.co.uk/our-boilers/combi-boilers/-/media/websites/baxiuk/files/product-literature/baxi-600-combi/baxi_600_combi_installation_and_service_manual.pdf?la=en&hash=59F4684A32860F2FCAB0F51E652F9FD09EFC064D
See p33 - the flue is close to the downpipe so the multiple 25mm minimum distances can't be applied, see note 2. So 300mm from internal corner, and 200mm below eaves.
Pretty clear to me. You can always go back to BS 5440 for detail - don't blindly trust manufacturers info, they get it wrong sometimes.
Stop looking at all other ot random manuals that suit your arguments, look at the one for this boiler. What does it say? I agree the caveats are the same and in think looking at those pucs theyre above 25mm so in my opinion It is installed to MI's. Therefore it's absolutely fine.
BS do not in anyway get in the way of MI's.
I'm a chartered engineer with over 20 years experience designing and inspecting systems. You won't find any building control officer who will agree that manufacturer's comments override building regs - ultimately it's BS 5440 Part 1 that everyone has to come back to, and that is very clear on this.This is the manual for a Potterton Promax HE https://www.acwilgar.co.uk/Boiler-Manual-PDF/Potterton/Potterton_Promax_15,24%20HE_Installation.pdf. This has corrected the clearances.1 -
dil1976 said:Money_Grabber13579 said:jefaz07 said:ComicGeek said:jefaz07 said:ComicGeek said:jefaz07 said:ComicGeek said:This shows it better https://www.worcester-bosch.co.uk/downloads/gas-hoziontal-and-vertical-flue-terminal-positioning.pdf
Its 25mm minimum below the eaves as long as the boiler flue is extended beyond the line of the gutter - yours isn't, so needs to be either 200mm below eaves or extended out past the gutter.
Should also be minimum 300mm from the corner, which yours isn't.Definitely not installed correctly.
You don't need to extend beyond the eaves. That is fine!
Youre using a Worcester manual for a Baxi!
You could also look up the same diagram in Part J of the Building Regulations, it still says 300mm minimum from a corner (p50). That hasn't changed since 2005.
Here's a random Baxi install manual I had on a recent project https://www.baxi.co.uk/our-boilers/combi-boilers/-/media/websites/baxiuk/files/product-literature/baxi-600-combi/baxi_600_combi_installation_and_service_manual.pdf?la=en&hash=59F4684A32860F2FCAB0F51E652F9FD09EFC064D
See p33 - the flue is close to the downpipe so the multiple 25mm minimum distances can't be applied, see note 2. So 300mm from internal corner, and 200mm below eaves.
Pretty clear to me. You can always go back to BS 5440 for detail - don't blindly trust manufacturers info, they get it wrong sometimes.
Stop looking at all other ot random manuals that suit your arguments, look at the one for this boiler. What does it say? I agree the caveats are the same and in think looking at those pucs theyre above 25mm so in my opinion It is installed to MI's. Therefore it's absolutely fine.
BS do not in anyway get in the way of MI's.
But as I say, that’s a lay persons view…There may be other parts of the overall boiler installation that may be subject to differences between manufacturers, ie installation clearances to the side of the boiler etc. But ultimately it is still the designer/installer's responsibility to install it in accordance with BS 5440 - 'but Baxi said I could put it there' is not going to win any court case when there is clear guidance on this.0 -
Out of interest, if the flue did not 'conform', could a solution be to add a plume kit?
0 -
Jeepers_Creepers said:Out of interest, if the flue did not 'conform', could a solution be to add a plume kit?1
-
jefaz07 said:ComicGeek said:jefaz07 said:ComicGeek said:This shows it better https://www.worcester-bosch.co.uk/downloads/gas-hoziontal-and-vertical-flue-terminal-positioning.pdf
Its 25mm minimum below the eaves as long as the boiler flue is extended beyond the line of the gutter - yours isn't, so needs to be either 200mm below eaves or extended out past the gutter.
Should also be minimum 300mm from the corner, which yours isn't.Definitely not installed correctly.
You don't need to extend beyond the eaves. That is fine!
Youre using a Worcester manual for a Baxi!
You could also look up the same diagram in Part J of the Building Regulations, it still says 300mm minimum from a corner (p50). That hasn't changed since 2005.Sorry I can't think of anything profound, clever or witty to write here.0 -
Thank you everyone for the feedback, some questions asked, the boiler is in its own cupboard just inside where it vents out, and is what I would say washing machine height, above the boiler is the slant of the roof you can see, so positioned as low as it could have been in its own full height cupboard.
it’s a Bloor house and quite highly specked.
im the third owner and I had a full Rics survey when I bought it 5 years ago. Nothing was flagged on my survey.
this is the first time I’ve had it serviced as it’s been empty but that’s another story.
chap found no problem whatsoever with the boiler when serviced.So are a couple of you saying it’s all correctly installed?
I am at a loss what to do, can I just get another engineer out to check it and if he thinks ok issue a certificate? Does the at risk notice go anywhere that the chap has told me this now has?This is my boiler manual, it’s not the same as the one the person posted a couple of posts back
https://www.wolseley.co.uk/wcsstore7.00.922.258/ExtendedSitesCatalogAssetStore/images/products/AssetPush/DTP_AssetPushHighRes/std.lang.all/ti/on/Potterton_PromaxCombiHE_Installation.pdf0 -
tillycat123 said:Thank you everyone for the feedback, some questions asked, the boiler is in its own cupboard just inside where it vents out, and is what I would say washing machine height, above the boiler is the slant of the roof you can see, so positioned as low as it could have been in its own full height cupboard.
it’s a Bloor house and quite highly specked.
im the third owner and I had a full Rics survey when I bought it 5 years ago. Nothing was flagged on my survey.
this is the first time I’ve had it serviced as it’s been empty but that’s another story.
chap found no problem whatsoever with the boiler when serviced.So are a couple of you saying it’s all correctly installed?
I am at a loss what to do, can I just get another engineer out to check it and if he thinks ok issue a certificate? Does the at risk notice go anywhere that the chap has told me this now has?
Baxi Assure Customer Support for New Build | Baxi
Sorry I can't think of anything profound, clever or witty to write here.0 -
I tried several times Friday to reach Baxi with no avail. I kept being transferred to technical and nobody picks up the calls, I tried all afternoon to speak to someone
will try again Monday0 -
tillycat123 said:This is my boiler manual, it’s not the same as the one the person posted a couple of posts back
This is exactly what I was saying above. The installation is not compliant with either the manufacturers info or BS 5440.
Para 7.8.1 states 'The following guidelines indicate the general requirements for siting balanced flue terminals. For GB recommendations are given in BS 5440 Pt 1.'So not to be taken as gospel, but referred back to BS 5440.
Further down under Important, 'The terminal position must ensure the safe and nuisance - free dispersal of combustion products.' The current position stuck in the corner by the down pipe and eaves does not achieve this.The flue needs be moved away from the downpipe and corner - if it can't be lowered due to the boiler height, then it needs extending beyond the eaves and gutter as well. Annoyingly it probably wouldn't have taken any longer to install it properly in the first place.0
Confirm your email address to Create Threads and Reply

Categories
- All Categories
- 351.3K Banking & Borrowing
- 253.2K Reduce Debt & Boost Income
- 453.8K Spending & Discounts
- 244.3K Work, Benefits & Business
- 599.5K Mortgages, Homes & Bills
- 177.1K Life & Family
- 257.8K Travel & Transport
- 1.5M Hobbies & Leisure
- 16.2K Discuss & Feedback
- 37.6K Read-Only Boards