Solarchaser said:This is you using your smart meter Nick or something else?4kWp (black/black) - Sofar Inverter - SSE(141°) - 30° pitch - North LincsInstalled June 2013 - PVGIS = 3400Sofar ME3000SP Inverter & 5 x Pylontech US2000B Plus & 3 x US2000C Batteries - 19.2kWh1
-
1961Nick said:EVandPV said:I find the myenergi ct readings the most inaccurate.
I also have an optismart sensor on the pv meter which reads the blinking led but the Lux seems to be the most accurate of the lot.
Our Octopus account shows consumption of 10.94kwh yesterday, the Lux shows 10.7kwh and myenergi shows 11.9kwh.
We've had a zappi since 2019 so could older/inferior ct clamps ??
I take it your led sensor readings match your smart meter ?Scott in Fife, 2.9kwp pv SSW facing, 2.7kw Fronius inverter installed Jan 2012 - 14.3kwh Seplos Mason battery storage with Lux ac controller - Renault Zoe 40kwh, Corsa-e 50kwh, Zappi EV charger and Octopus Go0 -
EVandPV said:I find the myenergi ct readings the most inaccurate.
I also have an optismart sensor on the pv meter which reads the blinking led but the Lux seems to be the most accurate of the lot.
Our Octopus account shows consumption of 10.94kwh yesterday, the Lux shows 10.7kwh and myenergi shows 11.9kwh.
So myenergi yesterday says
75.2kwh
Lux says 70.4kwh
Octopus says 73.78kwh
So myenergi is 1.4kwh adrift
Lux is 3.3kwh adrift
Never thought about comparing with Octopus, good shout👍
Edit. My myenergi stuff is all from this year, so yeah possible improvements in their clamps /software/firmwareWest central Scotland
4kw sse since 2014 and 6.6kw wsw / ene split since 2019
24kwh leaf, 75Kwh Tesla and Lux 3600 with 60Kwh storage0 -
Yesterday's import figures from various devices...
Geo (LED) 27.4kWh
MyEnergi (CT) 27.4kWh
IHD: 27.45kWh
Solarman (CT): 26.87kWh
4kWp (black/black) - Sofar Inverter - SSE(141°) - 30° pitch - North LincsInstalled June 2013 - PVGIS = 3400Sofar ME3000SP Inverter & 5 x Pylontech US2000B Plus & 3 x US2000C Batteries - 19.2kWh0 -
Solarchaser said:How are you monitoring charge vs discharge?
I ask because it used to be on the app, but there is only charge now.
I think I previously worked out my round trip with pylons at 82% using charge vs discharge figures0 -
1961Nick said:I think I previously worked out my round trip with pylons at 82% using charge vs discharge figures
A 22kWh charge would therefore be expected to yield around 17.5kWh.
80% is what I would expect for a round trip, but I'm only measuring half the round trip. They are being fully charged (to 24kWh capacity using about 26-27kWh)
On reflection, the 99% I expected should be 90% - since I'm (probably) measuring after it's been converted to AC. That's still a long way from 72%, though.
Also the (obviously) misreported SOCs shouldn't matter as I'm going from full to empty.0 -
Hi Folks,I have just come back to check my config using the web app and note that the ability to set 'On Grid cut off %'. and 'Off grid cut off' seems have disappeared.Any thoughts as to why, or am I having a Saga moment?
0 -
I noticed that too, was looking yesterday. I thought senior moment as I was sure it used to be there
It still there on my phone app though 🤔Barnsley, South Yorkshire
Solar PV 5.25kWp SW facing (14 x 375) Lux 3.6kw hybrid inverter installed Mar 22 and 9.6kw Pylontech battery
Daikin 8kW ASHP installed Jan 25
Octopus Cosy/Fixed Outgoing0 -
im seeing a charge rate of 7.5a on my 3 pylontecs in my garage which is currently 8 degrees, ive never seen the charge rate so low and curtainly not at 8 degrees.
even more strange is after checjing the charge graph from last night it only charged at a constant 300w and looks like the same is happening tonight.
any clue to whats happening, normally i would say the tempature but 8c isnt below the threshhold0 -
I'd be temped to switch off lux, switch off batteries.
Disconnect positive feed from batteries and all comms leads and switch the batteries on, and see if they are all at the same level, or charging each other.
If they seem OK, connect it all back up and switch it all on and see if it resets back to normalWest central Scotland
4kw sse since 2014 and 6.6kw wsw / ene split since 2019
24kwh leaf, 75Kwh Tesla and Lux 3600 with 60Kwh storage0
Confirm your email address to Create Threads and Reply

Categories
- All Categories
- 350.9K Banking & Borrowing
- 253.1K Reduce Debt & Boost Income
- 453.5K Spending & Discounts
- 243.9K Work, Benefits & Business
- 598.7K Mortgages, Homes & Bills
- 176.9K Life & Family
- 257.2K Travel & Transport
- 1.5M Hobbies & Leisure
- 16.1K Discuss & Feedback
- 37.6K Read-Only Boards