Ground Source Heat Pumps
Options
Comments
-
The output on that particular unit is 10.7Kw @35C. At 50C this decreases to 10.1 Kw. The company that installed it, ( who have been going for a number of years ) would have calculated the thermal requirements for the house, based on insulation and thermal loss so therefore the pump should be sized correctly.
A 16.7 Kw output pump requires 3.7Kw input @ 35C and 4.9Kw @ 50C.
I deal with these units on a daily basis, so I hope you can understand I have a lot of knowledge about them.
As posted earlier, in the 2 months on that tariff the OP has used approx 7,000kWh. If we 'allow' 1,000kWh for normal electrical consumption that is approx 6,000kWh taken by the GSHP.
2 months = 61 days = 1464 hours.
So the GSHP has used an average over 4kWh for every hour on a 24/7 basis.0 -
I think, that we should wait until we get the readings and then go from there. It is no good just questioning without the basic information.
I do agree with your comment regarding installers who do not know what they are talking about, but this is the norm with companies that jump on the bandwagon. Ice energy are a long established UK company. IVT is also one of the largest European suppliers of heat pumps.
Is there any other companies other than Ice Energy that you can recommend? i dont want to end up with a company selling us a GSHP when infact we dont really need it?
Also i dont have underfloor heating will this be a problem?Is a Bipolar bear0 -
Geotherm, I agree with those comments about that supplier and equipment.
But that model has the potential to have 3,6 or 9kw of additional resistance heating support.
If it is undersized for whatever reason, it will be running a lot more kw.
I haven't followed all this thread.
Do we know if the nosha123 and jdoddy systems have additional heaters?
Maybe they can let us know.0 -
JDoddy I am most intrigued to hear your story!!! Sounds like we are in the same boat here.. and with the same supplier!
I have emailed them already to ask for someone to do a site visit and check the set up. We had three leaks over Xmas too which didnt help as the whole system shut down.
Will get my readings and see what Geotherm recommends... Each day that goes by is currently costing us £10!!!!!
I suggest you get your readings too and see what the others here recommend!
Very interesting to have found you though!!!0 -
and to paceinternet - no.. we have no additional heaters!
More info will follow in the morning!
Standby all!0 -
As posted earlier, in the 2 months on that tariff the OP has used approx 7,000kWh. If we 'allow' 1,000kWh for normal electrical consumption that is approx 6,000kWh taken by the GSHP.
2 months = 61 days = 1464 hours.
So the GSHP has used an average over 4kWh for every hour on a 24/7 basis.
I need the pump data, as without it there is no way that I can work out if there is a problem or not. 7000kw in 2 months is far too high.As Manuel says in Fawlty Towers: " I Know Nothing"0 -
paceinternet wrote: »Geotherm, I agree with those comments about that supplier and equipment.
But that model has the potential to have 3,6 or 9kw of additional resistance heating support.
If it is undersized for whatever reason, it will be running a lot more kw.
I haven't followed all this thread.
Do we know if the nosha123 and jdoddy systems have additional heaters?
Maybe they can let us know.As Manuel says in Fawlty Towers: " I Know Nothing"0 -
dane-katie wrote: »Is there any other companies other than Ice Energy that you can recommend? i dont want to end up with a company selling us a GSHP when infact we dont really need it?
Also i dont have underfloor heating will this be a problem?
A correctly sized GSHP should be able to supply radiator heating, just make sure that it can cope with feed temperatures up to 65C.As Manuel says in Fawlty Towers: " I Know Nothing"0 -
and to paceinternet - no.. we have no additional heaters!
What paceinternet means is the heat pump itself having boosting heaters.
Most heat pump systems have 'normal' heaters (like immersion heaters) to provide additional heating when the heat pump cannot cope with the load.
The commonest cause of very high electricity bills is that a lot of the heating demand is being satisfied by these heaters.
Why these heaters are cutting in, Geotherm hopefully will be able to deduce from the info you supply0 -
This is a report that I completed about 2 weeks ago on a system that had a problem. It was resolved within 24 hrs. 14Kw output unit, 2 thermostatic controlled zones in the house 19C main floor/ 17C upper floor ..... 240 sq mtr, underfloor heating, buffer tank. DHW set at 50C.
For explanation, the unit was installed late Dec 2009.GT6 is compressor running temp, GT8/GT9 are heat transfer fluid temperatures. GT10/GT11 are ground loops in/out. GL= ground loop
Initial visit findings
Ground loop pressure 0 Bar
Alarm panel showing LP multiple times
When getting initial operation on the system the following
DHW:
GT6 66.7
GT8 readings from 52.6 - 54.0 - 55.2
GT9 " " 48.9 - 50.1 - 50.6
GT10/11 5.4 in/ 2.4 out
GL pressure increased to 2 Bar
Heating:
GT6 65.8 71.9 72.6
GT8 33.3 41.9 42.5
GT9 27.6 37.4 38.1
GT10 5.4 - 5.0
GT11 5.0 - 1.0
System left running as appeared to be okay, but the following alarms activated that evening:
16.28 LP
16.38 High HTF Delta
17.41 LP
19.07 LP
At that point the unit was shut down and returned to LPG gas heating instead of using the electric cartridge.
Fri 14th Jan
DHW reset to 53C
GT6 73.1 - 74.8
GT8 55.8 - 55.6
GT9 52.1 - 52.4
GL Pressure 1.Bar
With HTF pump set on level 2 speed the following for heating:
GT6 78.3 reducing to 72.1
GT8 36.1 - 37.0
GT9 31.0 - 32.8
Speed reset on HTF pump to level 1:
Heating cycle: ( untimed )
GT6 72.1 72.6 72.9
GT8 41.5 41.8 41.8
GT9 33.8 34.1 34.1
GT10 5.2 5.0 4.9
GT11 1.5 1.4 1.3
2nd test @14.00 hrs on DHW
GT6 76.7 80.7 84.0 87.3 89.2 Off
GT8 51.0 55.6 57.2 58.3 59.7
GT9 47.8 50.3 50.9 53.0 54.6
Heating: On 27.4/Off 32.4. Readings @ 5 min intervals
GT6 57.0 63.5 66.9 69.4 71.2
GT8 36.1 37.7 39.2 40.2 41.1
GT9 28.5 30.0 31.4 32.7 33.8
GT10 5.7 5.5 5.4 4.9 4.8
GT11 1.7 1.7 1.6 1.2 1.2
Final test @ 16.00 hrs. Heating only @5 min intervals
Off temp 33.1C
GT6 59.7 63.2 65.0 67.7 70.2
GT8 37.2 38.4 38.9 40.0 41.1
GT9 29.4 30.2 30.8 32.0 33.2
GT10 5.7 5.6 5.6 5.3 5.0
GT11 1.7 1.6 1.6 1.4 1.1
Total pump running time since installation = 2072 hrs
GL flow rate = 14ltr min
% DHW/ Heating = 16/84%
GL pressure left @ 1.2 Bar
Electrical boost over 1 year 6 hoursAs Manuel says in Fawlty Towers: " I Know Nothing"0
Categories
- All Categories
- 343.3K Banking & Borrowing
- 250.1K Reduce Debt & Boost Income
- 449.7K Spending & Discounts
- 235.3K Work, Benefits & Business
- 608.1K Mortgages, Homes & Bills
- 173.1K Life & Family
- 248K Travel & Transport
- 1.5M Hobbies & Leisure
- 15.9K Discuss & Feedback
- 15.1K Coronavirus Support Boards