  • lohr500
    lohr500 Posts: 1,637
    Part of the Furniture 1,000 Posts Name Dropper Combo Breaker
    Forumite

    So a quick update :

    It turns out that the standard PodPoint installer App is configured with a range of selectable whole home loads but with the maximum being 60 Amps.

    Higher settings can be pushed to the PodPoint remotely by PodPoint technical support, but only when they have confirmation from the DNO that a higher current fuse has been fitted and the supply is up to it.

    So I need to wait now for the DNO visit at the end of this month to hopefully "upgrade" the existing 100 Amp fuse to 80 Amps and sort out the mystery of the disappearing cable from the main fuse cutout which I believe has been wrongly identified as a looped supply.

  • NedS
    NedS Posts: 5,926
    Seventh Anniversary 1,000 Posts Photogenic Name Dropper
    Ambassador

    @lohr500 wrote:

    I can't modify the charging rate for the battery storage as this is controlled by Tesla's built in logic and the AGA needs the full 7 hours off-peak to fully reheat.

    As you have a Tesla Gateway, then the Gateway can limit site import to 60A. This will throttle back PW3 charging to stay within the 60A site limit. I am not sure how older PW2 systems manage this.

    You can see the configured site limits in the Tesla App under home info as Import Limit and Export Limit. Your Import Limit has likely been set to None, meaning no limit applied, but it's an easy change for your installer to make and can be done remotely. If it doesn't work as you expect, you can ask them to remove it again.

    I am a Forum Ambassador and I support the Forum Team on the Benefits & tax credits, Heat pumps and Green & Ethical MoneySaving forums. If you need any help on those boards, do let me know. Please note that Ambassadors are not moderators. Any post you spot in breach of the Forum Rules should be reported via the report button, or by emailing forumteam@moneysavingexpert.com. All views are my own & not the official line of Money Saving Expert.
  • lohr500
    lohr500 Posts: 1,637
    Part of the Furniture 1,000 Posts Name Dropper Combo Breaker
    Forumite

    Thanks @NedS

    I'm hoping the DNO will just sort out the main fuse and confirm that the house can operate on an 80 Amp total import load.

    But if not, I'll look at getting the Gateway site import load setting.
    I may even be able to change that myself if it is a setting in the Tesla One installer App as I have access to that.

  • NedS
    NedS Posts: 5,926
    Seventh Anniversary 1,000 Posts Photogenic Name Dropper
    Ambassador

    Correct, it's set in the Telsa One installer App, so you can make that change yourself if you have access.

    I am a Forum Ambassador and I support the Forum Team on the Benefits & tax credits, Heat pumps and Green & Ethical MoneySaving forums. If you need any help on those boards, do let me know. Please note that Ambassadors are not moderators. Any post you spot in breach of the Forum Rules should be reported via the report button, or by emailing forumteam@moneysavingexpert.com. All views are my own & not the official line of Money Saving Expert.
  • lohr500
    lohr500 Posts: 1,637
    Part of the Furniture 1,000 Posts Name Dropper Combo Breaker
    Forumite

    So a quick update :

    Northern Powergrid (DNO) came out today to survey the installation.

    The engineer didn't open up the cut out but concluded that the thinner black wire leaving the cutout was almost certainly an earth. He agreed it was highly unlikely to be a looped supply feed given the fact that there are no properties or outbuildings anywhere near us.

    He has said that the cutout needs updating and when they do this they will "upgrade" the existing 100 Amp fuse to 80 Amps.

    So I'm now waiting for an appointment date for them to do the work.
    Once the work is done and I have proof from the DNO that an 80 Amp fuse has been fitted, PodPoint will then remotely set the charger to an 80 Amp whole house limit.

★ ★ ★ Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 355.7K Banking & Borrowing
  • 254.9K Reduce Debt & Boost Income
  • 456.1K Spending & Discounts
  • 248.3K Work, Benefits & Business
  • 605.9K Mortgages, Homes & Bills
  • 179K Life & Family
  • 263.7K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16.2K Discuss & Feedback
  • 37.7K Read-Only Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.