Which power of induction hob can I fit?
fabs35
Posts: 120 Forumite
Our current hob state 5.8KW but when we use two of the four burners, they all turn off and show E signs.
It seems to be on its on its own 32KW circuit and so I wanted to ask what the maximum hob size I could go for. My wife would like a larger (80cm) wide hob but I am worried that it might be too powerful for the connection. If it helps, the grey cable that is running from the consumer unit to the hob is approx12mm x 8mm and was fitted in 2015.
It seems to be on its on its own 32KW circuit and so I wanted to ask what the maximum hob size I could go for. My wife would like a larger (80cm) wide hob but I am worried that it might be too powerful for the connection. If it helps, the grey cable that is running from the consumer unit to the hob is approx12mm x 8mm and was fitted in 2015.
0
Comments
-
Have you looked in the manual to see what the E sign signifies ?0
-
Good question! Just looked it up and it seems to be something internal.
I'll still need to change the hob and want to get a higher powered one that can hopefully have all four plates operating at the same time.0 -
It's 32A, not 32kW.I don't think that a hob can identify what sort of circuit it is connected to. If its maximum power is higher than the circuit can bear, I think it can be restricted in the settings.Again, read the manual.ETA: IIRC, 4mm2 cable is rated for more than 32A and is about 6.5*12mm, i.e. yours is at least 4mm2. 32A ~ 7.5kW.1
-
That's brilliant information and advice. Hopefully the settings can restrict the power.
Thank you!0 -
Hi Fab.
You need to have it determined what cable size you have, and also the associated MCB in your fuse box.
As said, a larger hob won't necessarily draw more power, unless it has an additional 'ring' - which it likely will.
Most will be around the 7.5kW size, but others can be higher. But, many models can be preset to suit the available supply; if too much power is drawn - eg all the rings running at the same time, it'll try and juggle them on and off to keep within the limit, or even reduce them all a small amount to cope. So you'd need to choose a model with this feature.
But, good chance your existing supply is fine, but needs confirming.0 -
Sorry WIAWSNB - just seen your reply.
I think I have an issue. Looking a little closer at the cable from the fuseboard, it says 2 x 6 +2.5mm which is connected to a dedicated 32A fuse. The hob I have bought is 7.4KW so I don't think it will work. The model is Samsung NZ84C5047GK/U1. According to Google AI:
No, 2.5mm cable is not enough for a 7.4kW hob; a dedicated circuit with a 6mm cable is required, as 7.4kW is roughly equivalent to a 30-32 Amp load, and 2.5mm cable is typically suitable for loads up to around 20-24 Amps. Using a 2.5mm cable would not only be undersized but also potentially unsafe, as the cable could overheat.
I have someone booked in to widen the hob cutout, to accommodate the 80cm hob, but I think I need to cancel him and try and sell the hob
Any thoughts. Maybe I could make the suggested restriction in the settings?
TIA1 -
fabs35 said:Sorry WIAWSNB - just seen your reply.
I think I have an issue. Looking a little closer at the cable from the fuseboard, it says 2 x 6 +2.5mm which is connected to a dedicated 32A fuse. The hob I have bought is 7.4KW so I don't think it will work. The model is Samsung NZ84C5047GK/U1. According to Google AI:
No, 2.5mm cable is not enough for a 7.4kW hob; a dedicated circuit with a 6mm cable is required, as 7.4kW is roughly equivalent to a 30-32 Amp load, and 2.5mm cable is typically suitable for loads up to around 20-24 Amps. Using a 2.5mm cable would not only be undersized but also potentially unsafe, as the cable could overheat.
I have someone booked in to widen the hob cutout, to accommodate the 80cm hob, but I think I need to cancel him and try and sell the hob
Any thoughts. Maybe I could make the suggested restriction in the settings?
TIA
Don't be too quick to write the cable off. The 2x6 will be the live and neutral, both 6mm². The bare earth wire will be 2.5mm².If it sticks, force it.
If it breaks, well it wasn't working right anyway.1 -
Almost certainly as Ecto says - looks like you are good to go
Obvs your sparky will confirm, but it's promising.0 -
2.5mm2 is a normal sockets cable with solid cores.6mm2 cable has two stranded cores (although so does 4mm2).
0 -
Amazing news (hopefully)!
I've attached a picture of the cables - grey from the fusebox and black from the new hob.
I have some wago connectors which have capacity upto 32A, but the wires are too thick to fit. Are there specific connectors I should be using? I assume I then put them in a junction box.0
Confirm your email address to Create Threads and Reply
Categories
- All Categories
- 354.5K Banking & Borrowing
- 254.4K Reduce Debt & Boost Income
- 455.4K Spending & Discounts
- 247.4K Work, Benefits & Business
- 604.2K Mortgages, Homes & Bills
- 178.5K Life & Family
- 261.7K Travel & Transport
- 1.5M Hobbies & Leisure
- 16K Discuss & Feedback
- 37.7K Read-Only Boards