📨 Have you signed up to the Forum's new Email Digest yet? Get a selection of trending threads sent straight to your inbox daily, weekly or monthly!

Solar PV "Power failure"? Technicians in North East? Help!

1910111214

Comments

  • debitcardmayhem
    debitcardmayhem Posts: 12,914 Forumite
    Part of the Furniture 10,000 Posts Name Dropper Photogenic
    edited 19 August at 12:50PM
    Just ring one of the solar people that have been found for you . 
    4.8kWp 12x400W Longhi 9.6 kWh battery Giv-hy 5.0 Inverter, WSW facing Essex . Aint no sunshine ☀️ Octopus gas fixed dec 24 @ 5.74 tracker again+ Octopus Intelligent Flux leccy
  • paul991
    paul991 Posts: 457 Forumite
    Fourth Anniversary 100 Posts
    Are you actually trying to cure a problem or just on here to get attention?
  • Qyburn
    Qyburn Posts: 3,702 Forumite
    Fifth Anniversary 1,000 Posts Name Dropper
    paul991 said:
    The mcb protects the cable and circuit supplying the inverter. So should only be changed by a electrician who can take into account other things like installation method ect
    While agreeing that cable size etc needs to be checked to confirm disconnection times can be met, I'll just point out that at least one vendor (Solaredge) specifies that the protective device should be 20% over the rated current of the inverter. Obviously cable needs to match as well.
  • Qyburn
    Qyburn Posts: 3,702 Forumite
    Fifth Anniversary 1,000 Posts Name Dropper
    That being so it's unfortunate that, playing "safe" I have purchased a replacement 16 A MCB together with an RCD both to the original spec. 
    I believe that breakers for solar inverters are now require to switch both L and N. That’s what I was told when ours was being replaced. Ours is an RCBO, so I'm not 100% sure the same applies to an MCB, but I don't see why it wouldn't.

    Just while talking about this, a note about your RCD. We haven't seen a schematic but normally where you have separate RCD combined with MCBs for the final circuits, normally the RCD protects multiple circuits. So if it trips randomly that could be triggered by something elsewhere in the house


  • Netexporter
    Netexporter Posts: 2,052 Forumite
    1,000 Posts First Anniversary Name Dropper
    I checked my G98 inverter and was surprised to see the breaker was rated at 25A. The consumer unit was fitted as part of the install.
  • NedS
    NedS Posts: 4,662 Forumite
    Sixth Anniversary 1,000 Posts Photogenic Name Dropper
    Qyburn said:
    paul991 said:
    The mcb protects the cable and circuit supplying the inverter. So should only be changed by a electrician who can take into account other things like installation method ect
    While agreeing that cable size etc needs to be checked to confirm disconnection times can be met, I'll just point out that at least one vendor (Solaredge) specifies that the protective device should be 20% over the rated current of the inverter. Obviously cable needs to match as well.
    That was my point. My 3.0kW FoxESS inverter has a 20A MCB, and Tesla specify a 20A MCB for their latest PW3 when limited to 3.68kW, so it's not at all uncommon to specify a 20A MCB on a 3.6kW inverter.

    Our green credentials: 12kW Samsung ASHP for heating, 7.2kWp Solar (South facing), Tesla Powerwall 3 (13.5kWh), Net exporter
  • Netexporter
    Netexporter Posts: 2,052 Forumite
    1,000 Posts First Anniversary Name Dropper
    Probably as well the breaker on mine is a bit bigger as they seem to have forgotten to set the inverter at 3.68kW, so I get the full 4048W maximum continuous rating, on the rare occasions the sun shines properly.
  • Telegraph_Sam
    Telegraph_Sam Posts: 2,606 Forumite
    Part of the Furniture 1,000 Posts Name Dropper
    No no NO!
    Do not replace the 16A  breaker ( MCB) with  20Amp version.

    The 16 A breaker is rated to protect the wiring  ( and hence the subsequent equipment, but by design the wiring ). A 16A breaker ( as I wrote previously) reacts to the level of current passing through it and the duration of the overload. Typically it will break the circuit at twice the rating after a couple of seconds overload I.e. 32A for  16 A breaker and thus protecting the wiring from over heating 
     20 Amp breaker reacts similarly but at 40A.

    The inverter, under normal  generation circumstances will limit it's output to comply with the G98 spec of 16 A nominal.  Even under limit failure case it's output will not significantly increase more than the solar PV max output ( kWp ) so there is no need to increase the mcb rating and it could be positively dangerous to do so if the inverter were to fail and draw high current from the grid.

    At the moment your mcb is either doing it job ....or is itself in need of replacement specifically with the correct ratings.
    I think that the best route would be to get an electrician to replace the existing 16 A MCB with the identical new one in case there is a fault with the former - and/or any external fault responsible for the erratic behaviour. Ditto RCD.
    Telegraph Sam

    There are also unknown unknowns - the one's we don't know we don't know
  • Telegraph_Sam
    Telegraph_Sam Posts: 2,606 Forumite
    Part of the Furniture 1,000 Posts Name Dropper
    I think the task will be to establish if there is an "external fault" and/or a fault with one of the original breakers. Does the same [16 / 20 Amp] limit apply to both the RCD and the MCB, or can they differ?
    Telegraph Sam

    There are also unknown unknowns - the one's we don't know we don't know
  • Qyburn
    Qyburn Posts: 3,702 Forumite
    Fifth Anniversary 1,000 Posts Name Dropper

    Does the same [16 / 20 Amp] limit apply to both the RCD and the MCB, or can they differ?
    The current rating of an RCD is simply a rating for the maximum current it's designed to carry. Typically 63A or more. It doesn't trip if that limit's exceeded.
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 351.6K Banking & Borrowing
  • 253.3K Reduce Debt & Boost Income
  • 453.9K Spending & Discounts
  • 244.5K Work, Benefits & Business
  • 599.8K Mortgages, Homes & Bills
  • 177.2K Life & Family
  • 258.1K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16.2K Discuss & Feedback
  • 37.6K Read-Only Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.