MeteredOut said:FreeBear said:MeteredOut said:FreeBear said:MeteredOut said:Nick_Dr1 said:MeteredOut said:
In the case of Heat Pumps, the starting position I hear is that any house can be converted to work with a heat pump with running costs lower than or equivalent to a gas boiler and that any negative reports we see are due to badly spec'd/installed/configured systems.
I'm not convinced it is a simple as that.
What can never be defined without more detailed investigation is what work is needed to get any individual house "heat pump ready" so that running costs are lower or equivalent to a gas boiler.
eg, I have a house with a large floor space with water underfloor heating throughout downstairs and traditional radiators upstairs, but fairly poorly insulated, all powered from a 40kW gas boiler. I know it should be possible to get a Heat Pump working, but there's a lot of work to do to get it there - my (admittedly fairly rudimentary to date) look into this makes me believe simply swapping out the gas boiler for a heat pump would never suffice.
A heatpump system needs to be designed, by someone who understands what they are doing. This includes understanding heat loss, heat transfer of radiators and heat flow rate though pipes. And that's it.
Get it wrong though and there's nowhere to go. With a gas boiler you normally have excess heat capability to allow for incompetent heat flow design.
What this means is that "standard" houses can have a "standard" design. Unusual houses need bespoke design by someone who knows what they are doing. So it is all about the spec.
Though maybe I will get someone out to see what they suggest might be possible. The boiler is 15+ years old now and had its first leak this year (simple parts replacement) so its probably best I plan ahead.A few solutions spring to mind.A horizontally mounted tank up in the loft. Downside is getting a tank up there, and ensuring there is sufficient structural support (but that would apply to a vertical tank also).Construct a well insulated shed just outside the house to house the DHW tank plus ancillaries - Extra expense, and may not be practical. But I do know of at least one installation that went that route.A Heat Geek mini store - Small enough to fit inside a kitchen cupboard, although total DHW supply from one charge may not be sufficient for your needs if you go for a smaller unit.Finally, if you don't need copious quantities of hot water and just have a shower, instant water heaters at the point of use could be used.I think....1 -
grumpypensioner said:QrizB said:benson1980 said:grumpypensioner said:I found a bit of a solution, I purchase a standalone air conditioner unit to supplement my old Baxi gas boiler, with a new Wessex 1.47kw 12000 BTU unit from ToolStation (over 200% efficiency) which cost me under £400 installed (needs a standard 10cm wall air duct and drain pipes and just plugs into a 13 amp socket)There's a place for those one-hose portable heat pumps (I've got one myself that only cools) but they all have the same limitation, namely that the (cold/hot) air that they vent when (heating/cooling) comes from inside the house and is air that you've previously (heated/cooled). And it's replaced by (cold/hot) air from outside.This limits their COP considerably, compared to a two hose, ducted or split system where the inside air stays inside and the outside air, outside.QrizB said:benson1980 said:grumpypensioner said:I found a bit of a solution, I purchase a standalone air conditioner unit to supplement my old Baxi gas boiler, with a new Wessex 1.47kw 12000 BTU unit from ToolStation (over 200% efficiency) which cost me under £400 installed (needs a standard 10cm wall air duct and drain pipes and just plugs into a 13 amp socket)There's a place for those one-hose portable heat pumps (I've got one myself that only cools) but they all have the same limitation, namely that the (cold/hot) air that they vent when (heating/cooling) comes from inside the house and is air that you've previously (heated/cooled). And it's replaced by (cold/hot) air from outside.This limits their COP considerably, compared to a two hose, ducted or split system where the inside air stays inside and the outside air, outside.
I think key factors may be the speed of response, it is powerful and circulates air around the house, and to quote an old tv clip is very on and offable!"And it's replaced by (cold/hot) air from outside."
Think it is called ventilation.0 -
FreeBear said:A very rough rule of thumb to determine the size of a heat pump needed is to take your annual gas consumption (in kWh) and divide it by 2900. But if you are like me and supplement heating with a wood stove, it is going to throw the calculation out. In which case, Heat Geek has a handy rough estimation table -> https://www.heatgeek.com/how-to-size-my-heat-pump-or-boiler-heat-loss-cheat-sheet/Hmm, my usage last year was 2800 and something, I also use a woodburner, rarely have the GCH on and not bothered about heating upstairs unless in very cold weather: up to bed and under the covers and getting up and moving in the morning.. Electric shower and towel rail which I sometimes heat at cheap overnight rate or surplus solar which also goes into the immersion. In a cavity wall insulated older 3 bed terrace losses aren't great.Which rate did you use in your calculations? Seems to me an A2A heat pump for downstairs (lounge and diner) would have to be one of the lowest powered available?
0 -
grumpypensioner said:grumpypensioner said:QrizB said:benson1980 said:grumpypensioner said:I found a bit of a solution, I purchase a standalone air conditioner unit to supplement my old Baxi gas boiler, with a new Wessex 1.47kw 12000 BTU unit from ToolStation (over 200% efficiency) which cost me under £400 installed (needs a standard 10cm wall air duct and drain pipes and just plugs into a 13 amp socket)There's a place for those one-hose portable heat pumps (I've got one myself that only cools) but they all have the same limitation, namely that the (cold/hot) air that they vent when (heating/cooling) comes from inside the house and is air that you've previously (heated/cooled). And it's replaced by (cold/hot) air from outside.This limits their COP considerably, compared to a two hose, ducted or split system where the inside air stays inside and the outside air, outside.QrizB said:benson1980 said:grumpypensioner said:I found a bit of a solution, I purchase a standalone air conditioner unit to supplement my old Baxi gas boiler, with a new Wessex 1.47kw 12000 BTU unit from ToolStation (over 200% efficiency) which cost me under £400 installed (needs a standard 10cm wall air duct and drain pipes and just plugs into a 13 amp socket)There's a place for those one-hose portable heat pumps (I've got one myself that only cools) but they all have the same limitation, namely that the (cold/hot) air that they vent when (heating/cooling) comes from inside the house and is air that you've previously (heated/cooled). And it's replaced by (cold/hot) air from outside.This limits their COP considerably, compared to a two hose, ducted or split system where the inside air stays inside and the outside air, outside.
I think key factors may be the speed of response, it is powerful and circulates air around the house, and to quote an old tv clip is very on and offable!"And it's replaced by (cold/hot) air from outside."
Think it is called ventilation.
You can control ventilation, with your single hose AC the external air is always fighting against you, if it's cold and you're trying to warm the interior, it's pulling more cold air through every crack and crevice as the unit is pumping interior air, outside, and vise versa when it's hot outside and you're trying to cool4.29kWp Solar system, 45/55 South/West split in cloudy rainy Cumbria.1 -
silverwhistle said:FreeBear said:A very rough rule of thumb to determine the size of a heat pump needed is to take your annual gas consumption (in kWh) and divide it by 2900. But if you are like me and supplement heating with a wood stove, it is going to throw the calculation out. In which case, Heat Geek has a handy rough estimation table -> https://www.heatgeek.com/how-to-size-my-heat-pump-or-boiler-heat-loss-cheat-sheet/Hmm, my usage last year was 2800 and something, I also use a woodburner, rarely have the GCH on and not bothered about heating upstairs unless in very cold weather: up to bed and under the covers and getting up and moving in the morning.. Electric shower and towel rail which I sometimes heat at cheap overnight rate or surplus solar which also goes into the immersion. In a cavity wall insulated older 3 bed terrace losses aren't great.Which rate did you use in your calculations? Seems to me an A2A heat pump for downstairs (lounge and diner) would have to be one of the lowest powered available?When I refitted my heating system in '23, I used the Stelrad calculator to determine the radiator sizing, and then added a bit on top. Once the gas boiler was installed, I fitted a heat meter to measure just how much energy was being put in to the radiators. In my mind, a much more accurate method of determining heat demand than feeding numbers in to a spreadsheet or MCS calculator. The graphs are telling me that I only need mean of 3kW to maintain a steady 18-19°C temperature when it is around freezing point outside. Peak demand is between 7kW and 12kW depending on how fast I want the place to heat up and the maximum flow temperature.Based on that data, I reckon an ASHP of around 7kW would be sufficient. Could perhaps get away with a 6kW unit, but certainly don't need any more than 8kW. Although to be sure, really need a sustained period of subzero temperatures in order to collect more data.Her courage will change the world.
Treasure the moments that you have. Savour them for as long as you can for they will never come back again.1 -
FreeBear said:silverwhistle said:FreeBear said:A very rough rule of thumb to determine the size of a heat pump needed is to take your annual gas consumption (in kWh) and divide it by 2900. But if you are like me and supplement heating with a wood stove, it is going to throw the calculation out. In which case, Heat Geek has a handy rough estimation table -> https://www.heatgeek.com/how-to-size-my-heat-pump-or-boiler-heat-loss-cheat-sheet/Hmm, my usage last year was 2800 and something, I also use a woodburner, rarely have the GCH on and not bothered about heating upstairs unless in very cold weather: up to bed and under the covers and getting up and moving in the morning.. Electric shower and towel rail which I sometimes heat at cheap overnight rate or surplus solar which also goes into the immersion. In a cavity wall insulated older 3 bed terrace losses aren't great.Which rate did you use in your calculations? Seems to me an A2A heat pump for downstairs (lounge and diner) would have to be one of the lowest powered available?When I refitted my heating system in '23, I used the Stelrad calculator to determine the radiator sizing, and then added a bit on top. Once the gas boiler was installed, I fitted a heat meter to measure just how much energy was being put in to the radiators. In my mind, a much more accurate method of determining heat demand than feeding numbers in to a spreadsheet or MCS calculator. The graphs are telling me that I only need mean of 3kW to maintain a steady 18-19°C temperature when it is around freezing point outside. Peak demand is between 7kW and 12kW depending on how fast I want the place to heat up and the maximum flow temperature.Based on that data, I reckon an ASHP of around 7kW would be sufficient. Could perhaps get away with a 6kW unit, but certainly don't need any more than 8kW. Although to be sure, really need a sustained period of subzero temperatures in order to collect more data.I think....0
-
michaels said:FreeBear said:silverwhistle said:FreeBear said:A very rough rule of thumb to determine the size of a heat pump needed is to take your annual gas consumption (in kWh) and divide it by 2900. But if you are like me and supplement heating with a wood stove, it is going to throw the calculation out. In which case, Heat Geek has a handy rough estimation table -> https://www.heatgeek.com/how-to-size-my-heat-pump-or-boiler-heat-loss-cheat-sheet/Hmm, my usage last year was 2800 and something, I also use a woodburner, rarely have the GCH on and not bothered about heating upstairs unless in very cold weather: up to bed and under the covers and getting up and moving in the morning.. Electric shower and towel rail which I sometimes heat at cheap overnight rate or surplus solar which also goes into the immersion. In a cavity wall insulated older 3 bed terrace losses aren't great.Which rate did you use in your calculations? Seems to me an A2A heat pump for downstairs (lounge and diner) would have to be one of the lowest powered available?When I refitted my heating system in '23, I used the Stelrad calculator to determine the radiator sizing, and then added a bit on top. Once the gas boiler was installed, I fitted a heat meter to measure just how much energy was being put in to the radiators. In my mind, a much more accurate method of determining heat demand than feeding numbers in to a spreadsheet or MCS calculator. The graphs are telling me that I only need mean of 3kW to maintain a steady 18-19°C temperature when it is around freezing point outside. Peak demand is between 7kW and 12kW depending on how fast I want the place to heat up and the maximum flow temperature.Based on that data, I reckon an ASHP of around 7kW would be sufficient. Could perhaps get away with a 6kW unit, but certainly don't need any more than 8kW. Although to be sure, really need a sustained period of subzero temperatures in order to collect more data.Reed3
-
michaels said:FreeBear said:silverwhistle said:FreeBear said:A very rough rule of thumb to determine the size of a heat pump needed is to take your annual gas consumption (in kWh) and divide it by 2900. But if you are like me and supplement heating with a wood stove, it is going to throw the calculation out. In which case, Heat Geek has a handy rough estimation table -> https://www.heatgeek.com/how-to-size-my-heat-pump-or-boiler-heat-loss-cheat-sheet/Hmm, my usage last year was 2800 and something, I also use a woodburner, rarely have the GCH on and not bothered about heating upstairs unless in very cold weather: up to bed and under the covers and getting up and moving in the morning.. Electric shower and towel rail which I sometimes heat at cheap overnight rate or surplus solar which also goes into the immersion. In a cavity wall insulated older 3 bed terrace losses aren't great.Which rate did you use in your calculations? Seems to me an A2A heat pump for downstairs (lounge and diner) would have to be one of the lowest powered available?When I refitted my heating system in '23, I used the Stelrad calculator to determine the radiator sizing, and then added a bit on top. Once the gas boiler was installed, I fitted a heat meter to measure just how much energy was being put in to the radiators. In my mind, a much more accurate method of determining heat demand than feeding numbers in to a spreadsheet or MCS calculator. The graphs are telling me that I only need mean of 3kW to maintain a steady 18-19°C temperature when it is around freezing point outside. Peak demand is between 7kW and 12kW depending on how fast I want the place to heat up and the maximum flow temperature.Based on that data, I reckon an ASHP of around 7kW would be sufficient. Could perhaps get away with a 6kW unit, but certainly don't need any more than 8kW. Although to be sure, really need a sustained period of subzero temperatures in order to collect more data.0
-
MarzipanCrumble said:michaels said:FreeBear said:silverwhistle said:FreeBear said:A very rough rule of thumb to determine the size of a heat pump needed is to take your annual gas consumption (in kWh) and divide it by 2900. But if you are like me and supplement heating with a wood stove, it is going to throw the calculation out. In which case, Heat Geek has a handy rough estimation table -> https://www.heatgeek.com/how-to-size-my-heat-pump-or-boiler-heat-loss-cheat-sheet/Hmm, my usage last year was 2800 and something, I also use a woodburner, rarely have the GCH on and not bothered about heating upstairs unless in very cold weather: up to bed and under the covers and getting up and moving in the morning.. Electric shower and towel rail which I sometimes heat at cheap overnight rate or surplus solar which also goes into the immersion. In a cavity wall insulated older 3 bed terrace losses aren't great.Which rate did you use in your calculations? Seems to me an A2A heat pump for downstairs (lounge and diner) would have to be one of the lowest powered available?When I refitted my heating system in '23, I used the Stelrad calculator to determine the radiator sizing, and then added a bit on top. Once the gas boiler was installed, I fitted a heat meter to measure just how much energy was being put in to the radiators. In my mind, a much more accurate method of determining heat demand than feeding numbers in to a spreadsheet or MCS calculator. The graphs are telling me that I only need mean of 3kW to maintain a steady 18-19°C temperature when it is around freezing point outside. Peak demand is between 7kW and 12kW depending on how fast I want the place to heat up and the maximum flow temperature.Based on that data, I reckon an ASHP of around 7kW would be sufficient. Could perhaps get away with a 6kW unit, but certainly don't need any more than 8kW. Although to be sure, really need a sustained period of subzero temperatures in order to collect more data.
If you presently have GCH, why are you considering getting a heatpump. Its unlikely to save you much if any money unless you can get it properly optimised and run it properly and even then you need to get an SCOP of better than four and maybe fiddle around with TOU electricity tariffs.
I've got a heatpump, had it for 15 years and I'm more than happy with it but I wouldn't swap out a functioning gas boiler for one and, TBH, I'd still replace a gas boiler like for like at the moment until HP's get cheaper to install and the price of leccy gets a lot closer to the price of gas.
Never under estimate the power of stupid people in large numbers2 -
Hope all you pundits watched the channel 5 programme called "Heat Pumps: Are They Really Worth It?" on 21 May 2025 19.00. Mind and cash boggling. Definitely convinces me that one large all encompassing system is not the way to go.0
Confirm your email address to Create Threads and Reply

Categories
- All Categories
- 351.2K Banking & Borrowing
- 253.2K Reduce Debt & Boost Income
- 453.7K Spending & Discounts
- 244.2K Work, Benefits & Business
- 599.3K Mortgages, Homes & Bills
- 177K Life & Family
- 257.6K Travel & Transport
- 1.5M Hobbies & Leisure
- 16.2K Discuss & Feedback
- 37.6K Read-Only Boards