F1001 said:ComicGeek said:F1001 said:ComicGeek said:F1001 said:ComicGeek said:F1001 said:twopenny said:Is there a void under the floor as per older houses?
Is there any insulation under the laminate?
What direction n,s,e,w does the room face?
The house was built by Barratts in 1997 in case anyone knows whether they would have added insulation at the time?
If you post some information on the size of room and size/type of current installed radiators, that can be checked.
What type of radiator is it - typically 3 types as below:
With a room 5.56x3.84 (total room area of circa 21.4 m2), this would be between 99 W/m2 - 110 W/m2 output. Should be more than capable of achieving a good temperature in that room without any unexpected issues.
If your party walls are ventilated and uninsulated however, then the heat loss will be much higher than expected. Assuming that the 3.84m dimension is the party wall length in the room, then the extra heat loss from this could add an additional 950W to the heat requirement for room.
First I would check that the boiler flow temperature is set high enough - that would normally need to be around 75 degrees on the coldest days for older systems. It's great money saving advice to turn it down on milder days, but you're not going to warm up the house on the colder days unless it's set higher on older systems.
If that doesn't work then you could swap the existing type 21 rads for type 22 rads of the same width/height (Myson still make imperial size radiators which might be a direct replacement without having to modify pipework centres) - that would give an extra 600-700W of heat output. If you have space, you could also make them 690mm high which would give an extra 1200-1400W of heat output. You could experiment by using a 1 kW electric heater in the room for a couple of days to see whether this extra heat output solves the issue.0 -
F1001 said:ComicGeek said:F1001 said:ComicGeek said:F1001 said:ComicGeek said:F1001 said:twopenny said:Is there a void under the floor as per older houses?
Is there any insulation under the laminate?
What direction n,s,e,w does the room face?
The house was built by Barratts in 1997 in case anyone knows whether they would have added insulation at the time?
If you post some information on the size of room and size/type of current installed radiators, that can be checked.
What type of radiator is it - typically 3 types as below:
With a room 5.56x3.84 (total room area of circa 21.4 m2), this would be between 99 W/m2 - 110 W/m2 output. Should be more than capable of achieving a good temperature in that room without any unexpected issues.
If your party walls are ventilated and uninsulated however, then the heat loss will be much higher than expected. Assuming that the 3.84m dimension is the party wall length in the room, then the extra heat loss from this could add an additional 950W to the heat requirement for room.
First I would check that the boiler flow temperature is set high enough - that would normally need to be around 75 degrees on the coldest days for older systems. It's great money saving advice to turn it down on milder days, but you're not going to warm up the house on the colder days unless it's set higher on older systems.
If that doesn't work then you could swap the existing type 21 rads for type 22 rads of the same width/height (Myson still make imperial size radiators which might be a direct replacement without having to modify pipework centres) - that would give an extra 600-700W of heat output. If you have space, you could also make them 690mm high which would give an extra 1200-1400W of heat output. You could experiment by using a 1 kW electric heater in the room for a couple of days to see whether this extra heat output solves the issue.
The advice normally wouldn't be to insulate within the party wall cavity, as that could cause issues for both you and your neighbour. But you could insulate internally onto the party walls on your side, which wouldn't affect your neighbour.1 -
ComicGeek said:F1001 said:ComicGeek said:F1001 said:ComicGeek said:F1001 said:ComicGeek said:F1001 said:twopenny said:Is there a void under the floor as per older houses?
Is there any insulation under the laminate?
What direction n,s,e,w does the room face?
The house was built by Barratts in 1997 in case anyone knows whether they would have added insulation at the time?
If you post some information on the size of room and size/type of current installed radiators, that can be checked.
What type of radiator is it - typically 3 types as below:
With a room 5.56x3.84 (total room area of circa 21.4 m2), this would be between 99 W/m2 - 110 W/m2 output. Should be more than capable of achieving a good temperature in that room without any unexpected issues.
If your party walls are ventilated and uninsulated however, then the heat loss will be much higher than expected. Assuming that the 3.84m dimension is the party wall length in the room, then the extra heat loss from this could add an additional 950W to the heat requirement for room.
First I would check that the boiler flow temperature is set high enough - that would normally need to be around 75 degrees on the coldest days for older systems. It's great money saving advice to turn it down on milder days, but you're not going to warm up the house on the colder days unless it's set higher on older systems.
If that doesn't work then you could swap the existing type 21 rads for type 22 rads of the same width/height (Myson still make imperial size radiators which might be a direct replacement without having to modify pipework centres) - that would give an extra 600-700W of heat output. If you have space, you could also make them 690mm high which would give an extra 1200-1400W of heat output. You could experiment by using a 1 kW electric heater in the room for a couple of days to see whether this extra heat output solves the issue.
The advice normally wouldn't be to insulate within the party wall cavity, as that could cause issues for both you and your neighbour. But you could insulate internally onto the party walls on your side, which wouldn't affect your neighbour.0 -
F1001 said:ComicGeek said:F1001 said:ComicGeek said:F1001 said:ComicGeek said:F1001 said:ComicGeek said:F1001 said:twopenny said:Is there a void under the floor as per older houses?
Is there any insulation under the laminate?
What direction n,s,e,w does the room face?
The house was built by Barratts in 1997 in case anyone knows whether they would have added insulation at the time?
If you post some information on the size of room and size/type of current installed radiators, that can be checked.
What type of radiator is it - typically 3 types as below:
With a room 5.56x3.84 (total room area of circa 21.4 m2), this would be between 99 W/m2 - 110 W/m2 output. Should be more than capable of achieving a good temperature in that room without any unexpected issues.
If your party walls are ventilated and uninsulated however, then the heat loss will be much higher than expected. Assuming that the 3.84m dimension is the party wall length in the room, then the extra heat loss from this could add an additional 950W to the heat requirement for room.
First I would check that the boiler flow temperature is set high enough - that would normally need to be around 75 degrees on the coldest days for older systems. It's great money saving advice to turn it down on milder days, but you're not going to warm up the house on the colder days unless it's set higher on older systems.
If that doesn't work then you could swap the existing type 21 rads for type 22 rads of the same width/height (Myson still make imperial size radiators which might be a direct replacement without having to modify pipework centres) - that would give an extra 600-700W of heat output. If you have space, you could also make them 690mm high which would give an extra 1200-1400W of heat output. You could experiment by using a 1 kW electric heater in the room for a couple of days to see whether this extra heat output solves the issue.
The advice normally wouldn't be to insulate within the party wall cavity, as that could cause issues for both you and your neighbour. But you could insulate internally onto the party walls on your side, which wouldn't affect your neighbour.Having insulated a couple of walls internally, I doubt very much you will notice a 50-75mm loss of floor space.The box room here was (nominally) 2.4m x 2.7m, and I've lost ~75mm on both measurements. Have yet to notice it feeling cramped as a result, but the improvement in comfort level sure makes up for it.
Her courage will change the world.
Treasure the moments that you have. Savour them for as long as you can for they will never come back again.1 -
Hi everyone,
So combi boiler now installed and more insulation in loft so it does feel a bit warmer alreadyI now am considering moving one of the radiators in the living area from an internal wall to a vertical one on the exterior wall (pic below). I also borrowed a thermal imaging camera and the photos showed that actually the concrete floor with barely any insulation doesn't look too bad. I am wondering whether it is poor adhesive application when putting in the plasterboards... Am also getting a new plinth heater as the old one seems busted and only blows out dusty cold air.
Any views on changing and moving the radiator to a vertical one on the external wall? Builder suggests that is always how they should be installed (i.e. on the external wall not internal - is how they do in other cold countries). New builds apparently put them on interior walls because its easier.
Appreciate any thoughts or advice please?
@FreeBear
@ComicGeek0 -
I should mention that the projections in the left side of the living room are the soil pipe, and a plugged in electric fireplace (which I have now removed). I borrowed a thermal imaging camera and floor and walls don't look that bad - not blue! Front door looks awful, and the bottom of the french doors (can put in extra heavy curtains).0
-
Op, have you checked the seals around the doors? Almost 30 years old so they might benefit from being replaced. Cheap and simple DIY fix and will definitely reduce draughts2006 LBM £28,000+ in debt.
2021 mortgage and debt free, working part time and living the dream1 -
jonnydeppiwish! said:Op, have you checked the seals around the doors? Almost 30 years old so they might benefit from being replaced. Cheap and simple DIY fix and will definitely reduce draughts1
Confirm your email address to Create Threads and Reply

Categories
- All Categories
- 350.9K Banking & Borrowing
- 253.1K Reduce Debt & Boost Income
- 453.5K Spending & Discounts
- 243.9K Work, Benefits & Business
- 598.7K Mortgages, Homes & Bills
- 176.9K Life & Family
- 257.2K Travel & Transport
- 1.5M Hobbies & Leisure
- 16.1K Discuss & Feedback
- 37.6K Read-Only Boards