ComicGeek said:F1001 said:ComicGeek said:F1001 said:twopenny said:Is there a void under the floor as per older houses?
Is there any insulation under the laminate?
What direction n,s,e,w does the room face?
The house was built by Barratts in 1997 in case anyone knows whether they would have added insulation at the time?
If you post some information on the size of room and size/type of current installed radiators, that can be checked.
What type of radiator is it - typically 3 types as below:0 -
Just saw on another forum that someone's house was also built in 1997 and has 25mm thick Jablite type insulation under the ground floor concrete slab - enough to meet Part L with a reasonably good Sap rating and comply with building regs at that time. Without lifting up flooring i'm guessing that the floor has 25mm-50mm insulation. Is it worth adding more, or better use of money spent on other ways to improve heat retention?0
-
F1001 said: Without lifting up flooring i'm guessing that the floor has 25mm-50mm insulation. Is it worth adding more, or better use of money spent on other ways to improve heat retention?It will cost a small fortune to dig up the existing slab in order to put in more insulation. On top of that, the sheer disruption of the work will probably put you off. Whilst you could put a 25mm or even 50mm layer of insulation on top of the floor, you'd then need to raise the threshold on all the doors - More hassle & inconvenience.Spend the money by insulating walls, roof, and perhaps fitting (very) low e sealed units in the doors & windows.
Any language construct that forces such insanity in this case should be abandoned without regrets. –
Erik Aronesty, 2014
Treasure the moments that you have. Savour them for as long as you can for they will never come back again.2 -
FreeBear said:F1001 said: Without lifting up flooring i'm guessing that the floor has 25mm-50mm insulation. Is it worth adding more, or better use of money spent on other ways to improve heat retention?It will cost a small fortune to dig up the existing slab in order to put in more insulation. On top of that, the sheer disruption of the work will probably put you off. Whilst you could put a 25mm or even 50mm layer of insulation on top of the floor, you'd then need to raise the threshold on all the doors - More hassle & inconvenience.Spend the money by insulating walls, roof, and perhaps fitting (very) low e sealed units in the doors & windows.
0 -
Might be worth seeing if you can get a thermal imaging camera from your energy provider or hire one from Library of Things to help identify where the coldest spots are coming from.
The floor in our dining room seemed colder than others and it was due to the kitchen door (despite the door being a good 2 meter away) - granted it wasn't the main reason but as a stop-gap thing, we put in a draught thing at the bottom of the door and it made quite a difference.2 -
You certainly won't be adding any more insulation under the concrete!
A thermal camera sounds a good idea. See what the walls are like, as well as the floor.
You ideally want to find out if the floor is a cause of the coldness, and how. Is it actually 'cold', in which case it's lacking insulation, so the answer is to add as much as you can on top - and anything will make a significant difference - or is the floor draughty. Or, is your heating just not up to the task.1 -
moneysaver1978 said:Might be worth seeing if you can get a thermal imaging camera from your energy provider or hire one from Library of Things to help identify where the coldest spots are coming from.
The floor in our dining room seemed colder than others and it was due to the kitchen door (despite the door being a good 2 meter away) - granted it wasn't the main reason but as a stop-gap thing, we put in a draught thing at the bottom of the door and it made quite a difference.In the meantime will test out the other suggestions on here. Thanks everyone!
1 -
F1001 said:ComicGeek said:F1001 said:ComicGeek said:F1001 said:twopenny said:Is there a void under the floor as per older houses?
Is there any insulation under the laminate?
What direction n,s,e,w does the room face?
The house was built by Barratts in 1997 in case anyone knows whether they would have added insulation at the time?
If you post some information on the size of room and size/type of current installed radiators, that can be checked.
What type of radiator is it - typically 3 types as below:
With a room 5.56x3.84 (total room area of circa 21.4 m2), this would be between 99 W/m2 - 110 W/m2 output. Should be more than capable of achieving a good temperature in that room without any unexpected issues.
If your party walls are ventilated and uninsulated however, then the heat loss will be much higher than expected. Assuming that the 3.84m dimension is the party wall length in the room, then the extra heat loss from this could add an additional 950W to the heat requirement for room.
First I would check that the boiler flow temperature is set high enough - that would normally need to be around 75 degrees on the coldest days for older systems. It's great money saving advice to turn it down on milder days, but you're not going to warm up the house on the colder days unless it's set higher on older systems.
If that doesn't work then you could swap the existing type 21 rads for type 22 rads of the same width/height (Myson still make imperial size radiators which might be a direct replacement without having to modify pipework centres) - that would give an extra 600-700W of heat output. If you have space, you could also make them 690mm high which would give an extra 1200-1400W of heat output. You could experiment by using a 1 kW electric heater in the room for a couple of days to see whether this extra heat output solves the issue.1 -
moneysaver1978 said:Might be worth seeing if you can get a thermal imaging camera from your energy provider or hire one from Library of Things to help identify where the coldest spots are coming from.
Any language construct that forces such insanity in this case should be abandoned without regrets. –
Erik Aronesty, 2014
Treasure the moments that you have. Savour them for as long as you can for they will never come back again.2 -
ComicGeek said:F1001 said:ComicGeek said:F1001 said:ComicGeek said:F1001 said:twopenny said:Is there a void under the floor as per older houses?
Is there any insulation under the laminate?
What direction n,s,e,w does the room face?
The house was built by Barratts in 1997 in case anyone knows whether they would have added insulation at the time?
If you post some information on the size of room and size/type of current installed radiators, that can be checked.
What type of radiator is it - typically 3 types as below:
With a room 5.56x3.84 (total room area of circa 21.4 m2), this would be between 99 W/m2 - 110 W/m2 output. Should be more than capable of achieving a good temperature in that room without any unexpected issues.
If your party walls are ventilated and uninsulated however, then the heat loss will be much higher than expected. Assuming that the 3.84m dimension is the party wall length in the room, then the extra heat loss from this could add an additional 950W to the heat requirement for room.
First I would check that the boiler flow temperature is set high enough - that would normally need to be around 75 degrees on the coldest days for older systems. It's great money saving advice to turn it down on milder days, but you're not going to warm up the house on the colder days unless it's set higher on older systems.
If that doesn't work then you could swap the existing type 21 rads for type 22 rads of the same width/height (Myson still make imperial size radiators which might be a direct replacement without having to modify pipework centres) - that would give an extra 600-700W of heat output. If you have space, you could also make them 690mm high which would give an extra 1200-1400W of heat output. You could experiment by using a 1 kW electric heater in the room for a couple of days to see whether this extra heat output solves the issue.0
Confirm your email address to Create Threads and Reply

Categories
- All Categories
- 351.7K Banking & Borrowing
- 253.4K Reduce Debt & Boost Income
- 454K Spending & Discounts
- 244.6K Work, Benefits & Business
- 600K Mortgages, Homes & Bills
- 177.3K Life & Family
- 258.3K Travel & Transport
- 1.5M Hobbies & Leisure
- 16.2K Discuss & Feedback
- 37.6K Read-Only Boards