AS Heat Pump in Old Farmhouse - Radiator Size?

Nsar1
Nsar1 Posts: 53 Forumite
Fifth Anniversary 10 Posts
edited 23 January at 2:47PM in Heat pumps
Hi we are on oil, no gas and our farmhouse has rubble walls and solid ground floors. I get that everyone says 'you'll need bigger radiators' but I can't get a sense of how big that means in practice. 10% bigger, 90% bigger? For context, roof insulation could be improved but probably not by much and windows are DG and doors pretty well draft proofed. I'm not going to insulate the walls, either outside or inside. 

Comments

  • You may not need bigger radiators at all.

    Before installing an air source heat pump you should carry out a survey to work out the heat loss of each room in your home.

    The heat loss of each room is calculated with reference to the lowest outside temperature that you will usually experience and the temperature each room is desired to be.

    The heat loss of your home is the same whatever your heating source.

    An ASHP is most efficient at low flow temperatures, usually lower than those with a gas or oil boiler.

    That lower flow temperature may require bigger radiators to provide the required heat than those that worked with your oil boiler.

    But they may not, I didn't need any radiator changes when I replaced my gas boiler for an ASHP.
  • matelodave
    matelodave Posts: 8,771 Forumite
    Part of the Furniture 1,000 Posts Name Dropper Photogenic
    As Matt say, the radiator size is related to the amount of heat that your room requires based on its heat loss calculated from the building construction, the inside temperature required v the outside temperatures. There are heat loss calculators on t'interweb which help you determine how much heat the room requires.

    Likewise the heat delivered to the room is the product of the radiator dissipation between it and the room it's heating, based on the size and construction of the rad (single panel, double panel, finned etc) the size of the radiator and the temperature difference between the room and radiator. Again their are calculators on the web, which help you determine the heat output of the radiator.

    The heat output from a radiator is specified at what's called DeltaT, which is usually around 50degrees - meaning that if you want the room at 20 degrees the water through the rad has to be around 70 degrees and most existing rads would be sized for high flow temps.

    As the efficiency of a heatpump is much higher at lower flow temperatures then you need a rad that will provide the same heat output but with a much lower temp of say 40-50 degrees, giving a Delta T of 20-30 degrees. Again there are radiator output specifications and derating tables on the web which allow you to calculate the heat output of radiators at various Delta T.

    For instance a radiator which outputs 1000 watts at a delta T of 50 will only output 510watts at a deltaT of 30 and 300 watts with a deltaT of 20 degrees.

    To do it properly you have to do the calculations and not just a wet finger in the air guess. Some rooms the rads may well have been oversized and are perfectly capable of delivering the heat you require at lower flow temps, but some may not

    Have shufti at this - https://www.bing.com/videos/riverview/relatedvideo?&q=radiators+suitable+for+heat+pumps&&mid=241501E2BBAC07AB121B241501E2BBAC07AB121B&&FORM=VRDGAR
    Never under estimate the power of stupid people in large numbers
  • When I got a heat pump I replaced virtually all of my radiators but my new ones all had internal fins to give a larger surface area.  The old radiators were all basic single or double panel types, quite a few of the new ones actually occupy less wall area than the old ones did.
    Reed
  • All  of our radiators were also replaced. 

    In the kitchen I previously had a very small radiator, the replacement is the same width but reaches to the ceiling! Most of the others are marginally bigger, just a few cm. But in the hall it is smaller than before. 

    In the bathrooms we have towel radiators and the also extend higher than previously. 

    We have one extra radiator that is in the upstairs hall, where none previously existed. 

    We have a sunroom with five exterior walls.  Initially it was suggested that it required 2 radiators. However I objected and they agreed to leave it with just one as it has a door separating it from our living accommodation. It gets very hot in there and I’ve never needed the radiator on! 
  • markin
    markin Posts: 3,860 Forumite
    Sixth Anniversary 1,000 Posts Name Dropper Photogenic
    Are the floors insulated, If not you may as well rip them up and do underfloor heating.
  • gm0
    gm0 Posts: 1,041 Forumite
    Sixth Anniversary 1,000 Posts Name Dropper
    Stelrad K3 (triple, finned) or similar would be my preferred approach.  But beware.  If you already have double finned the improvement of triples is real but not enough like for like.  Size has to go up.  1.5x or so. 

    You can get the current temperature "power output" data for your current radiatiors.  Based on their size/type. 
    You can lookup the sizes of "the same" output in room for a given size radiator at the different DeltaT of a lower operating temperature heat pump.  If the room needs 800W to stay comfy.  Then it needs 800W.  How you provide it and how you heat the water and by how much - is secondary.  This provides a route to a rule of thumb first approximation.  Clearly heat loss calculations and actual measurement are superior.

    The 2nd issue is current pipework and flow.  In a bigger system even the hotter water may not get to the end.  With losses.  At a lower operating temperature this can get dicey if the expectation is that the heatpump runs long and cool and the radiators are drawing from it.  The far end of the system may become another design issue to be overcome.

    Microbore is pretty much a no go

    UFH clearly a good solution if not for all retrofit cases.  Floors up, dig down insulate, support walls if foundations are of convered building type - it gets into serious renovation territory.




  • FreeBear
    FreeBear Posts: 16,791 Forumite
    Ninth Anniversary 10,000 Posts Name Dropper Photogenic
    edited 17 October 2023 at 1:07AM
    gm0 said: The 2nd issue is current pipework and flow.  In a bigger system even the hotter water may not get to the end.  With losses.  At a lower operating temperature this can get dicey if the expectation is that the heatpump runs long and cool and the radiators are drawing from it.  The far end of the system may become another design issue to be overcome.

    Microbore is pretty much a no go
    Even with gas boilers and the push to run at lower flow temperatures, current recommendation is to use 22mm or even 28mm for the feed/return pipes. The tails going to the radiators should be kept as short as possible, and ideally, use 15mm pipe. Best practice also recommends insulating feed/return pipes in all voids (no point in heating dead spaces).
    I had taken the above on board when replumbing my central heating system - When I eventually switch from a gas boiler to a heat pump, I shouldn't need to make any drastic changes to the plumbing.
    Her courage will change the world.

    Treasure the moments that you have. Savour them for as long as you can for they will never come back again.
Meet your Ambassadors

Categories

  • All Categories
  • 347.2K Banking & Borrowing
  • 251.6K Reduce Debt & Boost Income
  • 451.8K Spending & Discounts
  • 239.5K Work, Benefits & Business
  • 615.4K Mortgages, Homes & Bills
  • 175.1K Life & Family
  • 252.8K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16K Discuss & Feedback
  • 15.1K Coronavirus Support Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.