Curious Power Issue while using Chain Saw with Extension Cable!
Options
Comments
-
grumbler said:Jonboy_1984 said:They create additional resistance (and heat) when coiled due to the magnetic fields.I think, magnetic field is a myth as cable has two cores with opposite currents.And, again, heat (poor dissipation in this case) on its own cannot cause MCB tripping0
-
subjecttocontract said:Could it be a faulty extension lead ? If plugging the chainsaw directly into the wall socket works ok and plugging it into the ext lead doesn't work ok.....the fault is with the ext lead surely ?0
-
Keep_pedalling said:grumbler said:Section62 said:sujsuj said:I was trying to cut some wood using my RYOBI 2300W 40cm Chainsaw (RCS2340B). I used extension cables 13A rated its 25 meter long. But when I connect Chainsaw at end of extension cable power trips and Chainsaw stopped working. I could connect Chainsaw directly to plug and it works.If it is the MCB tripping then there's a good chance the issue is the volt drop over 50m of low-cost extension cable is resulting in a current draw high enough to cause the MCB to trip. What rating is the MCB, if it is that which is tripping? (a photo may be best)I would not use a cheap extension lead for such a high current device. I purchased a heavy duty lead for my EV granny charger for holiday use from these guys.0
-
tripped switch highlighted0
-
sujsuj said:Jonboy_1984 said:Also what else is on the same circuit as socket, e.g. is it a kitchen socket with a washing machine, fridge, freezer etc on the same switch and what is the rating on the switch in the consumer unit?There is a chance it’s the total load that’s exceeding the switch rating (I assume you are just running the saw rather than cutting anything when testing without the extension cables?).
1 -
danrv said:sujsuj said:Jonboy_1984 said:Also what else is on the same circuit as socket, e.g. is it a kitchen socket with a washing machine, fridge, freezer etc on the same switch and what is the rating on the switch in the consumer unit?There is a chance it’s the total load that’s exceeding the switch rating (I assume you are just running the saw rather than cutting anything when testing without the extension cables?).1
-
sujsuj said:grumbler said:Jonboy_1984 said:They create additional resistance (and heat) when coiled due to the magnetic fields.I think, magnetic field is a myth as cable has two cores with opposite currents.And, again, heat (poor dissipation in this case) on its own cannot cause MCB trippingsujsuj said:tripped switch highlightedThat isn't an RCD you've highlighted. It is an MCB.Move your wood pile closer to the power source... will be easier, safer and cheaper.1
-
This MCB (yes, MCB, not RCD) is just 16A.Your 2.3kW saw draws normally about 10A, more when it starts or is overloaded. Hardly a surprise that it trips the MCB occasionally and unpredictably.Extension leads (unless they are faulty) have nothing to do with this.Or it can be some fault with the saw.1
-
grumbler said:This MCB (yes, MCB, not RCD) is just 16A.Your 2.3kW saw draws normally about 10A, more when it starts or is overloaded. Hardly a surprise that it trips the MCB occasionally and unpredictably.Extension leads (unless they are faulty) have nothing to do with this.
1 -
Section62 said:grumbler said:This MCB (yes, MCB, not RCD) is just 16A.Your 2.3kW saw draws normally about 10A, more when it starts or is overloaded. Hardly a surprise that it trips the MCB occasionally and unpredictably.Extension leads (unless they are faulty) have nothing to do with this.As I said, "occasionally and unpredictably". Most likely, without the extensions lead the tests were short and without serious load.1
Confirm your email address to Create Threads and Reply

Categories
- All Categories
- 350.8K Banking & Borrowing
- 253K Reduce Debt & Boost Income
- 453.5K Spending & Discounts
- 243.8K Work, Benefits & Business
- 598.6K Mortgages, Homes & Bills
- 176.8K Life & Family
- 257K Travel & Transport
- 1.5M Hobbies & Leisure
- 16.1K Discuss & Feedback
- 37.6K Read-Only Boards