Boiler water temp

Mikemoreton36
Posts: 2 Newbie

in Energy
Octopus suggest a combi boiler radiator water temp of 50°. Most of the advice from boiler companies suggest a temp of 70°. The lower the temp, the longer it will take to heat a space so, other than improving the efficiency of the boiler, the saving on gas is marginal. Lower temps means the room temp will take longer to reach the set temp and your boiler will be on longer thus consuming more gas. Remember the old adage"there's no such thing as a free lunch".
0
Comments
-
The idea of running at a lower temperature is to ensure the return flow is at a low enough temperature to fully exploit the condensing effect of the boiler, thus leading the better utilisation of gas. Modern boilers have modulating burners, so even though the boiler may be on for longer, the flame is smaller.
1 -
Mikemoreton36 said:Octopus suggest a combi boiler radiator water temp of 50°. Most of the advice from boiler companies suggest a temp of 70°. The lower the temp, the longer it will take to heat a space so, other than improving the efficiency of the boiler, the saving on gas is marginal. Lower temps means the room temp will take longer to reach the set temp and your boiler will be on longer thus consuming more gas. Remember the old adage"there's no such thing as a free lunch".
You'll still get there, but at 50 it will take a bit longer but will cost you a lot less.
At 70 your boiler will be firing up and shutting down rather than just idling at 50. The same with driving, blatting up to 70 and then slowing down and speeding up is a lot less efficient than cruising along at say 50. (my car does around 48mpg at 70mph and around 58-60mpg at 50mph which although a bit boring is a worthwhile saving)Never under estimate the power of stupid people in large numbers1 -
The science indicates the lower the boiler RETURN temperature the better for efficiency. Most research indicates that very few boilers installed in the UK are running in a condensing mode. A large plume of steam is not an indication that the boiler is condensing.1
-
Mikemoreton36 said:Octopus suggest a combi boiler radiator water temp of 50°.
However, for condensing boilers a return temp of 55C> (thereby ensuring condensing occurs) would typically mean a flow temp. of ~70-75C>. If you can run lower return temp than 55C the more efficient the boiler will be but it's single figure % gains.
Ultimately it's an individual's call on a balance between cost, comfort & convenience.
Running lower temps also tends to make life easier for the boiler & therefore improve reliability/life.
I do wonder though what impact on cost savings (given that electricity is much deare than gas per kWh) running the pump & fan for much longer causes?1 -
BUFF said:Mikemoreton36 said:Octopus suggest a combi boiler radiator water temp of 50°.I would counter by suggesting it will work fine so long as we don't have another Beast for the East. Heat loss calcs assume a sub-zero outdoor temp (varies by region) but most of the time it's warmer than that, so the reduced rad output is still sufficient to maintain the design temperature.If we do have a cold spell, it's only a moment's work to turn the flow temperature up.You can think of it as DIY weather compensation!N. Hampshire, he/him. Octopus Intelligent Go elec & Tracker gas / Vodafone BB / iD mobile. Ripple Kirk Hill member.
2.72kWp PV facing SSW installed Jan 2012. 11 x 247w panels, 3.6kw inverter. 33MWh generated, long-term average 2.6 Os.Not exactly back from my break, but dipping in and out of the forum.Ofgem cap table, Ofgem cap explainer. Economy 7 cap explainer. Gas vs E7 vs peak elec heating costs, Best kettle!0 -
You can think of it as DIY weather compensation!We all have to get our entertainment where we can.
1 -
QrizB said:BUFF said:Mikemoreton36 said:Octopus suggest a combi boiler radiator water temp of 50°.I would counter by suggesting it will work fine so long as we don't have another Beast for the East. Heat loss calcs assume a sub-zero outdoor temp (varies by region) but most of the time it's warmer than that, so the reduced rad output is still sufficient to maintain the design temperature.If we do have a cold spell, it's only a moment's work to turn the flow temperature up.You can think of it as DIY weather compensation!
However, I live in a pre-1919 building (which makeup ~20% of the UK's housing stock) with a condensing boiler & what would be considered oversize radiators on a traditional boiler system (but probably still too small for a heat pump). Even running at a flow temp of 53C during this mild winter I would say is pushing the boundaries of what I think most people would consider a reasonable comfort/convenience balance (you can also chuck in cost if you want). & I am someone who is happy at 16C when many are not ...
0 -
Even running at a flow temp of 53C during this mild winterIt's the return temperature that matters.
0 -
BUFF said:Mikemoreton36 said:Octopus suggest a combi boiler radiator water temp of 50°.
However, for condensing boilers a return temp of 55C> (thereby ensuring condensing occurs) would typically mean a flow temp. of ~70-75C>. If you can run lower return temp than 55C the more efficient the boiler will be but it's single figure % gains.
Ultimately it's an individual's call on a balance between cost, comfort & convenience.
Running lower temps also tends to make life easier for the boiler & therefore improve reliability/life.
I do wonder though what impact on cost savings (given that electricity is much deare than gas per kWh) running the pump & fan for much longer causes?
@Mikemoreton36 provided you have a condensing boiler I'd suggest you just give it a try. I dropped my boiler flow temperature from 70°C to 55°C about a week ago and it's working fine. It's a little slower to heat up obviously, but that's it. As per the graph posted above it's probably about 5% more efficient this way. Not enough to reliably be able to detect but it seems the smarter thing to do. Should the weather get really cold outside so that I can't heat my home OK this way, I'll just turn the flow temperature up again for that period.0 -
Verdigris said:Even running at a flow temp of 53C during this mild winterIt's the return temperature that matters.
so the return temp is even lower (usually 10C-20C lower depending upon system & setup)...
in the Octopus advice they advise a flow temp of 50C which, based on my own personal experience at a slightly higher temp, is imo probably a step too far for many. I think that a significant no. (mostly those living in older buildings) would not find it a comfortable/convenient way to run at that low a temp..0
Confirm your email address to Create Threads and Reply

Categories
- All Categories
- 349.7K Banking & Borrowing
- 252.6K Reduce Debt & Boost Income
- 452.9K Spending & Discounts
- 242.6K Work, Benefits & Business
- 619.3K Mortgages, Homes & Bills
- 176.3K Life & Family
- 255.5K Travel & Transport
- 1.5M Hobbies & Leisure
- 16.1K Discuss & Feedback
- 15.1K Coronavirus Support Boards