GSHP - I need help with making it as efficient as possible!
Comments
-
If it is indeed 'thermosyphoning', it wouldn't use any electricity to move heat around the house. However, if that results in the tank cooling down you can expect the heat exchanger to fire up which will use power.ccbrowning said:
We have a meter which shows just heating electricity usage and I checked 24 hours after changing to summer mode and it’s not gone up at all. Hope it doesn’t cause issues later. So maybe the installers did a passable job? lolEricMears said:Very likely the system is running due to 'thermosyphon' : i.e. the hot water from tank downstairs is lifting itself up and displacing colder water in the floors. You'll only stop that if you can put a valve into the line.NE Derbyshire.4kWp S Facing 17.5deg slope (dormer roof).24kWh of Pylontech batteries with Lux controller BEV : Hyundai Ioniq51 -
Thanks! You appear to be right - used 1 kWh overnight.
I’ll have to check the timer settings to see if I can get it to do this during the day so it may use the solar power. 0 -
A 'proper' solution (which I ought to do but have never got round toccbrowning said:Thanks! You appear to be right - used 1 kWh overnight.
I’ll have to check the timer settings to see if I can get it to do this during the day so it may use the solar power.
) would be to put a solenoid operated valve alongside the main pump and use existing <pump on> signal to operate the valve then the valve's output to operate pump. NE Derbyshire.4kWp S Facing 17.5deg slope (dormer roof).24kWh of Pylontech batteries with Lux controller BEV : Hyundai Ioniq50 -
You'd be better off using a motorised valve with auxiliary contacts to eliminate thermosyphon rather than a solenoid. A solenoid valve requires current to hold it open or closed whereas a motorised valve just uses power when its operating.EricMears said:
A 'proper' solution (which I ought to do but have never got round toccbrowning said:Thanks! You appear to be right - used 1 kWh overnight.
I’ll have to check the timer settings to see if I can get it to do this during the day so it may use the solar power.
) would be to put a solenoid operated valve alongside the main pump and use existing <pump on> signal to operate the valve then the valve's output to operate pump.Never under estimate the power of stupid people in large numbers0
Confirm your email address to Create Threads and Reply
Categories
- All Categories
- 352.1K Banking & Borrowing
- 253.6K Reduce Debt & Boost Income
- 454.3K Spending & Discounts
- 245.2K Work, Benefits & Business
- 600.9K Mortgages, Homes & Bills
- 177.5K Life & Family
- 259K Travel & Transport
- 1.5M Hobbies & Leisure
- 16K Discuss & Feedback
- 37.7K Read-Only Boards