No hot water, heating ok

2

Comments

  • Mister_G
    Mister_G Posts: 1,947 Forumite
    Part of the Furniture 1,000 Posts Name Dropper Combo Breaker
    AndyPK wrote: »
    Has nothing to do with the 3 way valve electrics

    Well on my system the microswitches in the head certainly control the HW and the CH.:)
  • When I went to check part numbers, I had another play....

    Setting Timer to CH on, causes CH to come on as hoped.
    Setting Timer to HW on, causes 3way to move to HW position but then nothing else happens.
    Setting Timer to CH on, again causes CH to come on. Then setting timer to HW on as well, causes 3way to move and then CH switches off.

    If that is food for thought as to whether this is more likely to be header or stat (or something else).

    Thanks
  • AndyPK
    AndyPK Posts: 4,371 Forumite
    Part of the Furniture 1,000 Posts
    The immersion and boiler use separate theromstats in the tank.


    Do you have a picture of your stat/tank ?


    For 3 way valves the switches only enable the boiler when in CH mode.
  • AndyPK
    AndyPK Posts: 4,371 Forumite
    Part of the Furniture 1,000 Posts
    It's never a bad idea to replace the valve heads, as they do wear/fail, but I don't honestly think its the problem in your case
  • Mister_G
    Mister_G Posts: 1,947 Forumite
    Part of the Furniture 1,000 Posts Name Dropper Combo Breaker
    It could still be either.

    If you try turning the temperature control on the stat, can you hear it click when it switches on? Ideally a multimeter would be the best thing to use.

    Failing that, if you are confident with electrics, then remove the cable from the stat and join the wires together (brown and blue only!), insulating them with tape. This will bypass the stat and will prove if the header is the problem.

    Only do this if you are Confident and AFTER you have switched off the supply!
  • I have recently changed the header unit, so it would seem unlikely that's the problem, though not impossible. It worked fine for 1 month until last weekend.

    There is no clicking from the stat at all, in either direction.

    I had thought about joining those wires, so now that you've suggested it I'll give it a go.

    I'll try to post a pic later, depending on the outcome of joining the stat wires.

    Thanks.
  • Sorry, there is a click on the stat, just it's so low down I didn't notice it at first. It clicks at what must be about 5 or 10 degrees (the scale only goes down to 40).
  • Mister_G
    Mister_G Posts: 1,947 Forumite
    Part of the Furniture 1,000 Posts Name Dropper Combo Breaker
    michaeljs wrote: »
    Sorry, there is a click on the stat, just it's so low down I didn't notice it at first. It clicks at what must be about 5 or 10 degrees (the scale only goes down to 40).

    That would be about right if the tank is cold. However, it clicking doesn't mean to say that the contacts are making correctly.

    Without a multimeter to check, I reckon joining the wires is the only sure fire way of checking.
  • 5XLbMEuoxNjFeg7c9

    When you say join the brown and blue wires..........
This discussion has been closed.
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 351.3K Banking & Borrowing
  • 253.2K Reduce Debt & Boost Income
  • 453.7K Spending & Discounts
  • 244.2K Work, Benefits & Business
  • 599.4K Mortgages, Homes & Bills
  • 177.1K Life & Family
  • 257.7K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16.2K Discuss & Feedback
  • 37.6K Read-Only Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.