Hi
I have a conventional boiler, with hot water tank. Heating works fine.
Hot water isn’t working.
F&e tank is fine.
Header to 3 way valve is working as expected.
When valve is set to HW, nothing happens. If heating is on and then HW turned on, valve moves to HW position correctly but then all is turned off incl heating.
Immersion heats water fine.
To me, problem is either 3 way valve is not working (even though its header is), or thermostat on hot water tank is not working.
Any ideas as to what I can do or what else I should consider before calling someone out to replace the valve?
Many thanks
I have a conventional boiler, with hot water tank. Heating works fine.
Hot water isn’t working.
F&e tank is fine.
Header to 3 way valve is working as expected.
When valve is set to HW, nothing happens. If heating is on and then HW turned on, valve moves to HW position correctly but then all is turned off incl heating.
Immersion heats water fine.
To me, problem is either 3 way valve is not working (even though its header is), or thermostat on hot water tank is not working.
Any ideas as to what I can do or what else I should consider before calling someone out to replace the valve?
Many thanks
0
Comments
-
Try taking the motor unit off the three way valve and see if it can be turned witha spanner or pair of pliers.
Some three way valves have auxiliary contacts which fire up the boiler and pump.
There are a few things to check such as the valve, the tank stat, the programmer if you've got one to ensure that the valve is operating and the boiler & pump are being energised when the tank stat calls for heat.
It helps if you've got a wiring diagram of your set-up and you know how to prod around it with a multimeter - not a good idea if you dont know what you are doing as mains electricity can kill.Never under estimate the power of stupid people in large numbers0 -
Thanks for the reply.
Do you mean to take the whole head off or to remove the motor from within the head unit?
I have taken the head unit off and I can move the switch underneath (ie. On the valve) easily with my fingers.
Turning HW on activates the valve switch as expected.0 -
No further input from anyone?0
-
Turn thermostat to full on same with boiler .
See if you have HW .
No then probable valve is faulty and not opening HW port.
But clueless as to actual valve type .
https://www.heatingcontrolsonline.co.uk/acl-drayton-invensys-ma16793-midposition-motorised-valve-p-110.html0 -
Thanks JJ.
I have tried turning thermostat up full. No HW.
So it seems the valve is faulty. Many thanks for your help.0 -
Do you know what make and model of valve motor/valve assy it is? Is it a separate motor and valve body assy?Feudal Britain needs land reform. 70% of the land is "owned" by 1 % of the population and at least 50% is unregistered (inherited by landed gentry). Thats why your slave box costs so much..0
-
It's a Honeywell 3 way, V4073A1039. So yes it separates into two parts.
As mentioned earlier, I have already tried removing the head (motor) unit - which appears to be functioning fine. I can manually move the knob on top of the valve with my fingers (after removing the head unit) easily.
I don't think there's anything wrong with the motor unit. Possibly the valve itself is broken, but I was wondering whether anything else is worth investigating before replacing the valve (seeing as that would require a drain-down).
The only other thing I could think is wrong, is the thermostat on the tank.0 -
It's a Honeywell 3 way, V4073A1039. So yes it separates into two parts.
As mentioned earlier, I have already tried removing the head (motor) unit - which appears to be functioning fine. I can manually move the knob on top of the valve with my fingers (after removing the head unit) easily.
I don't think there's anything wrong with the motor unit. Possibly the valve itself is broken, but I was wondering whether anything else is worth investigating before replacing the valve (seeing as that would require a drain-down).
The only other thing I could think is wrong, is the thermostat on the tank.
I have exactly the same valve and the issue I had was with the microswitches in the actuator head. It is those that tell the programmer when heat is required, along with the appropriate thermostats (tank and room).
So although the motor was turning the valve to the correct position, there was no demand for heat as the microswitch hadn't made contact
Replacing the head solved the problem.
Before I did this, I did check that the tank stat was functioning correctly with a multimeter.0 -
The tank thermostat is responsible for firing the boiler and pump up for HW. So that must be the issue.
Has nothing to do with the 3 way valve electrics
Could also be the timer.
Ideally need to test for power at the stat.
or rotate it round and see if it clicks at least (ideally when the water is warm but not hot)0 -
Thank you Mister G and AndyPK.
Someone else I spoke to did mention microswitches in the header unit.
AndyPK, if the thermostat is gone, would the immersion still heat the water? Or does the immersion not pay any attention to the stat?
Either way, what I was trying to establish is whether it was the valve (not the motorised head) or something else that requires a system drain. I think you've given me enough info to make it worthwhile replacing the stat and/or header unit of the 3way before doing anything else.
Thank you.0
This discussion has been closed.
Confirm your email address to Create Threads and Reply

Categories
- All Categories
- 351.3K Banking & Borrowing
- 253.2K Reduce Debt & Boost Income
- 453.7K Spending & Discounts
- 244.2K Work, Benefits & Business
- 599.4K Mortgages, Homes & Bills
- 177.1K Life & Family
- 257.7K Travel & Transport
- 1.5M Hobbies & Leisure
- 16.2K Discuss & Feedback
- 37.6K Read-Only Boards