Megaflo must be totally vertical

6.6K Posts
Forumite
in Water bills
Megaflo is a nightmare!
After six years of living with a Megaflo, which never worked properly, a few words from a guy who KNOWs solved it!
The ground the cylinder we installed it on was a little slopy, so we put in a little padding to make it level: or so we thought! :mad:
When you heat hot water using a boiler, the water expands, and the pressure was blowing the pressure valve at 6 bars, and the pressure made the face basin tap spew water at my lap. The internal diaphragm was supposed to absorb the pressure, and release it slowly when you use water. The original plumber tried regenerating the air gap multiple times, and even replaced the pressure valve on the cylinder, with zero success. And then he died! For years, I had to let the hot tap drip while heating hot water, to prevent the pressure build up.
Various plumbers subsequently suggested things like an external expansion vessel to take the pressure, and then never turned up to do the work.
Finally, an engineer turned up and says he has seen lots of Megaflo cylinder misbehaving, simply because the internal diaphragm tilts when the cylinder is not PEREFECTLY VERTICAL.
So we put in a few millimetres more of padding under two legs, regenerated the air gap, and it has been working how it is supposed to work for two days: BLISS!
It seems other manufacturers offer the same idea, it's just that Megaflo has the patent on the internal diaphragm, so other people have to sell you a system with an external pressure vessel, and they work EVEN IF the cylinder isn't level!
So, if you are going for a Megaflo cylinder, demand the Gas Safe engineer use a proper spirit level check all the way around the cylinder before plumbing it in. It's either that, or have a pressure vessel that looks like a big red zit.
I already have a big red zit, due to the under floor heating pipes having more water than normal radiators, so the built-in pressure vessel inside the boiler isn't enough.
I hope this helps to end the misery for Megaflo sufferers.
It was just millimetres!
After six years of living with a Megaflo, which never worked properly, a few words from a guy who KNOWs solved it!
The ground the cylinder we installed it on was a little slopy, so we put in a little padding to make it level: or so we thought! :mad:
When you heat hot water using a boiler, the water expands, and the pressure was blowing the pressure valve at 6 bars, and the pressure made the face basin tap spew water at my lap. The internal diaphragm was supposed to absorb the pressure, and release it slowly when you use water. The original plumber tried regenerating the air gap multiple times, and even replaced the pressure valve on the cylinder, with zero success. And then he died! For years, I had to let the hot tap drip while heating hot water, to prevent the pressure build up.
Various plumbers subsequently suggested things like an external expansion vessel to take the pressure, and then never turned up to do the work.
Finally, an engineer turned up and says he has seen lots of Megaflo cylinder misbehaving, simply because the internal diaphragm tilts when the cylinder is not PEREFECTLY VERTICAL.
So we put in a few millimetres more of padding under two legs, regenerated the air gap, and it has been working how it is supposed to work for two days: BLISS!
It seems other manufacturers offer the same idea, it's just that Megaflo has the patent on the internal diaphragm, so other people have to sell you a system with an external pressure vessel, and they work EVEN IF the cylinder isn't level!
So, if you are going for a Megaflo cylinder, demand the Gas Safe engineer use a proper spirit level check all the way around the cylinder before plumbing it in. It's either that, or have a pressure vessel that looks like a big red zit.
I already have a big red zit, due to the under floor heating pipes having more water than normal radiators, so the built-in pressure vessel inside the boiler isn't enough.
I hope this helps to end the misery for Megaflo sufferers.
It was just millimetres!
0
This discussion has been closed.
Latest MSE News and Guides
Replies
Although a Megaflo does not need an external expansion vessel, I was informed it was mandatory in UK. This extract from the Megaflo website seems to confirm that view.
Of course this might be a recently introduced regulation.
The idea is that the heating up process compresses the air, which pushes back when you run the taps, giving extra pressure, but it only lasts briefly.