  • skitler
    skitler Posts: 3,065 Forumite
    now where getting somewhere.


    the cable will then be a 3 core, + earth


    brown, black and grey, earth should be sleeved green/yellow


    that cable should be re couloured


    brown, brown, and blue.


    however if you swap the live and sw live over in the connections at the fan and leave the neutral alone, that should rectify the matter. failing that you will need it look at.


    it should work as thus


    when light is switched on the fan comes on and stay on as long as the light is still on, when you switch off the light the fan should stay on for aprox 15 mins and then go off till light is switched on again.


    there is a small timer near the fan connections that is adjustable with a flat screwdriver to increase or decrease the time the fan stays on after light has been switched off
  • Ruski
    Ruski Posts: 1,628 Forumite
    Why would swapping the lives make a difference? The issue isn't that the 'timer' function doesn't work, it is that the fan shuts off after half an hour when the light (s/l) is still active...

    Unless I've misread the diagnosis.. which is more than possible :D

    Russ
    Perfection takes time: don't expect miracles in a day :D
  • Ruski
    Ruski Posts: 1,628 Forumite
    Does it have a humidistat function? This may be a cause?

    Russ
    Perfection takes time: don't expect miracles in a day :D
  • cyclonebri1
    cyclonebri1 Posts: 12,827 Forumite
    The OP only has to wires running to the fan, at least only 2 they can see. I'd suspect a permanent feed has been taken separately from elsewhere, linked into the ceiling rose for eg. Does sound like these wires are reversed.
    I like the thanks button, but ,please, an I agree button.

    Will the grammar and spelling police respect I do make grammatical errors, and have carp spelling, no need to remind me.;)

    Always expect the unexpected:eek:and then you won't be dissapointed
  • aetbaar
    aetbaar Posts: 134 Forumite
    Risk You are correct the fan switches off after half an hour even with the light on and no it does not have a humidistat just a timer

    I am sure the wires are taken from the circuit feeding the ceiling spot lights as there are only two wires - as suggested I will swap the wires around

    If there are only two wires should they go in live and neutral or switched lived and neutral they are currently in live and neutral
  • Ruski
    Ruski Posts: 1,628 Forumite
    I very much doubt that swapping the wire around will make a difference, and certainly using SL instead of L would doubtfully work either.
    Identify the exact model of fan and get the manufacturers inctructions - modern energy efficient fans may well have a 'max on' factory setting in order to conserve energy.....

    HTH

    Russ
    Perfection takes time: don't expect miracles in a day :D
  • skitler
    skitler Posts: 3,065 Forumite
    well this is more info


    if you only have 2 wires then swapping them wont make any difference.


    in post 11 you say it has 3 wires.


    the neutral needs to stay where it is


    put the sw live in its correct terminal and then put a link from there to the other live terminal.


    that will solve the problem


    however you will not have a over run. ie light on fan on, light off fan will go off.


    essentially it works but its wired wrong and not to building regs.
  • Ruski
    Ruski Posts: 1,628 Forumite
    Bit ambiguous in #11 - three terminals, two wires is what is meant :)

    +1 for above solution tho.

    Russ
    Perfection takes time: don't expect miracles in a day :D
  • cyclonebri1
    cyclonebri1 Posts: 12,827 Forumite
    Wonder if the neutral is actually there and the wires are live and switched live.

    I know I know that should not work but if there is some sort of return through wherever it was fed from then............. Straw clutching of course;);)
    I like the thanks button, but ,please, an I agree button.

    Will the grammar and spelling police respect I do make grammatical errors, and have carp spelling, no need to remind me.;)

    Always expect the unexpected:eek:and then you won't be dissapointed
  • aetbaar
    aetbaar Posts: 134 Forumite
    Thanks all

    So as per skitlers recommendation I should have the two wires in neutral and live then a separate bit of wire joining neutral and switched live ?

    If that is right I will try it and report back

    Thanks again
This discussion has been closed.
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 350.9K Banking & Borrowing
  • 253.1K Reduce Debt & Boost Income
  • 453.5K Spending & Discounts
  • 243.9K Work, Benefits & Business
  • 598.7K Mortgages, Homes & Bills
  • 176.9K Life & Family
  • 257.2K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16.1K Discuss & Feedback
  • 37.6K Read-Only Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.