Heres a Pressure PUZZLE for Ya All
Mr_Ted
Posts: 1,067 Forumite
G/worm 18si system boiler.
1/ Losing pressure.
2/ Found safety to be blowing.
3/ Checked expansion vessel, drained, recharged(BL**DY awkward coz of the shraeder valve location-Stupid designers), and refilled.
4/ Same problem persists???
5/ Goes through the motions several times more.
6/ Same problem persists:huh::doh::wall::whistle:
Also checked system water which is still clean as a whistle after 7 years, and has inhibitor;)
So what else could it be:huh:
Found it though :cheesy: but what do ya all think it could have been
and its summat I aint seen mentioned here b4
:whistle:
:beer: on me for correct answers :rotfl:
1/ Losing pressure.
2/ Found safety to be blowing.
3/ Checked expansion vessel, drained, recharged(BL**DY awkward coz of the shraeder valve location-Stupid designers), and refilled.
4/ Same problem persists???
5/ Goes through the motions several times more.
6/ Same problem persists:huh::doh::wall::whistle:
Also checked system water which is still clean as a whistle after 7 years, and has inhibitor;)
So what else could it be:huh:
Found it though :cheesy: but what do ya all think it could have been
:beer: on me for correct answers :rotfl:
Signature removed
0
Comments
-
Filling system letting by?0
-
I'm guessing that since the PRV is blowing each time and there is a subsequent loss of pressure, there must be an over-pressure situation to cause this?If my post hasn't helped you, then don't click the 'Thanks' button!
0 -
My experience of this is that once the PRV operates it VERY rarely seals again properly. This can be from trapped debris on the seat of the valve, but most likely its because the rubber washer sticks to its seat (because its held tightly shut for so long) within the PRV and then tears when it operates and therefore continues to let by. As a result I tend to change the PRV as a matter of course in these situations to save on call-backs.
Am I warm??
0 -
My experience of this is that once the PRV operates it VERY rarely seals again properly. This can be from trapped debris on the seat of the valve, but most likely its because the rubber washer sticks to its seat (because its held tightly shut for so long) within the PRV and then tears when it operates and therefore continues to let by. As a result I tend to change the PRV as a matter of course in these situations to save on call-backs.
Am I warm??
:)Nope
no beer 
Sorted that and PRV ok but still the problem;)Signature removed0 -
What's it connected to ?I'm only here while I wait for Corrie to start.
You get no BS from me & if I think you are wrong I WILL tell you.0 -
Mains pressure on DHW side of HEX is getting across to CH side.
CheersThe difference between genius and stupidity is that genius has it's limits. - Einstein0 -
This discussion has been closed.
Confirm your email address to Create Threads and Reply
Categories
- All Categories
- 354.2K Banking & Borrowing
- 254.3K Reduce Debt & Boost Income
- 455.3K Spending & Discounts
- 247.2K Work, Benefits & Business
- 603.8K Mortgages, Homes & Bills
- 178.4K Life & Family
- 261.3K Travel & Transport
- 1.5M Hobbies & Leisure
- 16.1K Discuss & Feedback
- 37.7K Read-Only Boards