Armoured Cable Thickness?

Options
We are currently building stables and I need to run a power supply. I think 6mm cable will do (just) but should I err on the side of caution and get 10mm?

My thoughts on maximum output (not all at the same time) will be:-

Kettle:- (3kW?)
Lights:- 300W
Freezer:- ? (but small)
Clippers:- 200W

I don't have one but if I say used a pressure washer (1.4kW) or similar would I pushing my luck.

Any views appreciated.

Oh one other thing I presume I want 3 core?
«134

Comments

  • Andy_L
    Andy_L Posts: 13,028 Forumite
    Part of the Furniture 10,000 Posts Name Dropper
    How long is the cable run?
    How is it routed? Buried, Clipped to wall, suspended from a catenary?
  • Hintza
    Hintza Posts: 19,420 Forumite
    10,000 Posts Combo Breaker
    Sorry thought I had mentioned length. That will be 60m and buried coming in at gable end before going up wall to roof space before dropping back to consumer unit.
  • Ich_2
    Ich_2 Posts: 1,087 Forumite
    It isn't all about the load, it is also about the voltage drop along the cable.
    You need to know the length & the volt drop per metre of cable. The overall figure cannot exceed 5% of the nominal mains voltage.
    Have you looked at the earthing arrangements, what sort of earthing have you got, can it be safely and within the regs exported to the stables.
    Work of this sort should be notified to the local building regs department, properly tested and certified.
  • Quiet_Spark
    Quiet_Spark Posts: 1,093 Forumite
    60m of 6mm² PVC insulated SWA will withstand a continuous load of 6KW in the configuration you describe.
    You will only need 2 core as the armour is the earth conductor.
    Understeer is when you hit a wall with the front of your car
    Oversteer is when you hit a wall with the back of your car
    Horsepower is how fast your car hits the wall
    Torque is how far your car sends the wall across the field once you've hit it
  • Hintza
    Hintza Posts: 19,420 Forumite
    10,000 Posts Combo Breaker
    Thanks guys, that's a great help. Looks like the 6mm will be ample, I thought it was but just wanted to check I wasn't trying to skimp.
  • Ich_2
    Ich_2 Posts: 1,087 Forumite
    Which will give a volt drop of 4%, If your earthing is TNC-S and you intend exporting it you need a MINIMUM of a 10mm2 earth, 3 core 6mm2 with one core & the armours being used as the earth will just comply
  • keystone
    keystone Posts: 10,916 Forumite
    Ich wrote: »
    ...........as the earth will just comply
    Just being the operative. Perhaps TT for the stables would be best.

    Cheers
    The difference between genius and stupidity is that genius has it's limits. - Einstein
  • Hintza
    Hintza Posts: 19,420 Forumite
    10,000 Posts Combo Breaker
    OK guys you are now confusing me again (last two posts)...eek.
  • keystone
    keystone Posts: 10,916 Forumite
    Quick google on earthing systems will help you rather than a detailed explanation but basically with TN-C-S (known as protective multiple earthing (PME) in the UK and is where the combined neutral-and-earth conductor of the supply is connected to real earth at many locations) in your house you will be exporting the earth to the stables and it will only just comply with requirements using 6mm cable. Having a separate and independent TT (terre - terre or ground to ground) earth system for the stables using a nice big conductive stake driven into the ground. But with TT ALL circuits must be RCD protected.

    Cheers
    The difference between genius and stupidity is that genius has it's limits. - Einstein
  • Ich_2
    Ich_2 Posts: 1,087 Forumite
    I would suggest that you need to learn a lot more about electricity, or employ an electrician.
    At the end of the day it is a stable so if it goes wrong and you end up with a dead horse or worse a person, the cost of an electrician would seem minor.

    There is nothing stopping you doing the excavation and donkey work under supervision to save costs
This discussion has been closed.
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 351.1K Banking & Borrowing
  • 253.2K Reduce Debt & Boost Income
  • 453.6K Spending & Discounts
  • 244.1K Work, Benefits & Business
  • 599.1K Mortgages, Homes & Bills
  • 177K Life & Family
  • 257.5K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16.1K Discuss & Feedback
  • 37.6K Read-Only Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.