Moving a lightswicth 6 inches down the wall.
Options

Mr_Reeman
Posts: 102 Forumite
Hi, my gf has bought a lovely old antique shelving unit which she wants in our Edwardian home. The problem is, the alcove it is to go in means the light switch is covered by it!
I would like to just move the switch 6 inches down the wall by cutting a new box and channel out of the plaster. The only problem is extending the wire which currently wont reach further down the wall.
What would be the preferred method to join the wire and extend it by a few inches? I expect I will join the wire in the existing back box and use a cover plate to hide the join which would be covered by the shelving unit, but it would also allow access to the join if necessary.
Thanks.
I would like to just move the switch 6 inches down the wall by cutting a new box and channel out of the plaster. The only problem is extending the wire which currently wont reach further down the wall.
What would be the preferred method to join the wire and extend it by a few inches? I expect I will join the wire in the existing back box and use a cover plate to hide the join which would be covered by the shelving unit, but it would also allow access to the join if necessary.
Thanks.
0
Comments
-
I would use connecting strips like these. You could also use a box like these.
They come in various sizes/ratings. For normal lighting you only need a rating of 5 amps. Make sure the extra wire that you use is suitable for lighting and is also correctly rated for the load. 5 amps should be ok unless you have a lot of high wattage bulbs in the ceiling.
Just make sure that you connect all the wires correctly and firmly and don't leave any bits of wire sticking out either end. You could finish off by wrapping insulating tape around the connectors although that isn't essential.
And don't forget to isolate the power at the consumer unit (NOT the light switch) before starting the work.0 -
Thanks, I was thinking a choc blox too.
Cheers for the help.0 -
Using a flex outlet or fused connection plate (check they would fit in the back box as they are deeper than a switch) would be better than a terminal block as the terminals are better quality but more importantly the screws and metal back box would be connected to earth.
http://www.screwfix.com/p/mk-20a-1-gang-flex-outlet-white/70006
http://www.screwfix.com/p/marbo-13a-dp-fcu/64816
Connection guide here, just don't use the flex cord grip and use normal twin and earth cable :
http://www.diyfixit.co.uk/electrics/fused-connection-unit.html0 -
You either have to:
1. Renew the whole length of cable or;
2. Keep the back box, join the cables with choc block within the back box and then fit a removable blanking plate over the back box (this as you have already said is your preferred option) or;
3. Crimp (using a proper crimping tool) and heat shrink sleeve the joints. This you can plaster over.
You may not use choc block, even in a cover box, plaster over the whole thing and leave it inaccessible.
CheersThe difference between genius and stupidity is that genius has it's limits. - Einstein0 -
how difficult would it be to lift a floorboard upstairs and see if you can pull anything along ? (switch end & light end):cool: hard as nails on the internet . wimp in the real world :cool:0
-
why not move the light switch a few inches, up?Get some gorm.0
-
or the shelf !:cool: hard as nails on the internet . wimp in the real world :cool:0
-
Thanks guys. Shelf is going there whether the light switch is accessible or not unfortunately! She who must be obeyed!
I like the idea of the fused spur connector. Would mean its connected up properly then. I will see what I can get that is flush with the wall like the existing switch, so that the back of the shelving unit is flat against the wall.
I realise I cannot hide any connectors under the plaster, so I wont be doing that.
Thanks for your help.0 -
how difficult would it be to lift a floorboard upstairs and see if you can pull anything along ? (switch end & light end)Hi, we’ve had to remove your signature. If you’re not sure why please read the forum rules or email the forum team if you’re still unsure - MSE ForumTeam0
This discussion has been closed.
Confirm your email address to Create Threads and Reply

Categories
- All Categories
- 351K Banking & Borrowing
- 253.1K Reduce Debt & Boost Income
- 453.6K Spending & Discounts
- 244K Work, Benefits & Business
- 598.9K Mortgages, Homes & Bills
- 176.9K Life & Family
- 257.3K Travel & Transport
- 1.5M Hobbies & Leisure
- 16.1K Discuss & Feedback
- 37.6K Read-Only Boards