Heat pump without a paddle
Just moved into a bungalow, no instructions. Have an air source heat pump, wet underfloor heating, solar panels and battery. I have found most answers that I need from this site except one and that is this - is it just as economical to run the heating in all zones as it is to run in say one of two rooms? Theory being that the pump is on anyway or is that not the case? I have 7 zones (rooms), each has it's own thermostat. Some rooms don't get regular use. Hope I have explained well. Thank you.
Comments
-
I would run it in all zones but for rooms that are not being used set the thermostats in those rooms several degrees lower and keep the doors to those rooms shut.
It will cost more if your are heating things like a spare bedroom to the same level as your main living areas.
2 -
I'd generally disagree with the above. When heat pumps are fitted the system should be set up to keep each room to it's target temperature, something like 20C for living rooms/kitchen/bathrooms and 18C for bedrooms. The whole house is treated like an envelope.
If you turn down temperatures in unused rooms, heat from other rooms will be lost (through walls, under doors) trying to replace it. It can also cause the heat pump to cycle a lot if the loops in several rooms have closed, as there will be less water circulating the system and it won't be a able to release the heat properly.
It could be worth trying it as an experiment for a few days to see but you would need to compare against days with similar temperatures and wind speeds.
Barnsley, South Yorkshire
Solar PV 5.25kWp SW facing (14 x 375) installed Mar 22
Lux 3.6kw hybrid inverter and 9.6kw Pylontech batteries
Daikin 8kW ASHP installed Jan 25
Octopus Cosy/Fixed Outgoing
Kia EV63 -
In theory (and AIUI):
UFH should be balanced, using the manifold flow gauges, to get the rooms to the required / design temperatures when the heat pump is using a Weather compensating water flow temperature… (So higher flow when outside is cold, lower temp when warm).
Thus the heat into floor(s) balances the heat lost, regardless of the outside temperature.
Getting a Weather Compensation curve setting just right can take a long time as UFH responds very slowly.
Only if, after all that flow balancing, particular rooms still overheat should the room stats then be used to shut the floor loop(s) to control an overheat situation… (Or reduce room from a design of 21 'living' to 18 'bedroom' perhaps if rebalancing is not desirable).
Room stats can also sometimes be used to
stopmitigate solar gain overheating of specific rooms.Some retrofit Heat Pump Installers may remove all the manifold actuators (replaced with manual caps to open the loop) so the thermostats, while still in place, do nothing. Those rely on the loops being balanced via the flow meter controls.
It's a black art to get things 'just right'.
1 -
I'm with Alnat1 on this. If you turn down the thermostats in the unused rooms, the other emitters in the house will try compensate for it. The emitters have been sized to assume the rooms are at a specific temperature, e.g. 20C for living areas and 17C for bedroom. If you move away from the design temperatures, the other emitters have to work harder and this will mean that the heat pump will cycle more as the emitters can't emit all the heat needed to get the property up to temperature.
The comments I post are my personal opinion. While I try to check everything is correct before posting, I can and do make mistakes, so always try to check official information sources before relying on my posts.1 -
Unfortunately, you'll get multiple different answers. It depends on many factors including:
- the heat pump you have, as some will be good at modulating output to low levels, others are good at cycling on and off with minimal impact on efficiency
- the heat loss from your bungalow and how effective the underfloor heating is in each room
- the size of the rooms that you don't need to be warm and how much heat they lose
- the effectiveness of the walls between rooms at preventing heat transfer
- the tariff you are on for your electricity supply
Generally, if you have large or poorly insulated rooms that you don't use, then heating them to the same temperature as the rest of the house is wasteful. An extreme example of this is a conservatory. Limiting the heat to those rooms by restricting flow through the manifold will often yield better results overall than using the thermostat to switch heating on/off at a set temperature. This can be a bit of trial and error to get the flow correct and, if you really want to optimise it, may need adjusting when weather gets colder/warmer.
6.4kWp (16 * 400Wp REC Alpha) facing ESE + 5kW Huawei inverter + 10kWh Huawei battery. Vaillant Arotherm Pro 7kW heat pump.1 -
Both camps have a point. Alnat1 and tacpot12 are right that the system was designed with every room at its design temperature, and Keep_pedalling and Magnitio are right that a spare room you rarely use doesn't need to be as warm as the lounge. They fit together if you do it the way Rodders53 and Magnitio describe: leave every zone on and turn the spare rooms down a couple of degrees by closing their loops a little at the manifold flow gauges, rather than letting the thermostats shut them off. A couple of degrees, not several: the water keeps moving through most of the floor so the heat pump doesn't cycle, and the warm rooms lose little through the walls.
On the 'pump is on anyway' idea: a heat pump's electricity follows the heat it puts in, so fewer warm rooms does use a bit less, just less of a saving than it looks.
Two things nobody has mentioned yet:
- Keep one steady temperature day and night rather than on/off times or big setbacks. Underfloor takes hours to warm back up, and the catch-up runs at a higher water temperature, which is when a heat pump is least efficient.
- As you have no instructions, find the make and model on the outdoor unit's label and download the manual (the installer manual too if you can find it). It shows how to check it runs on weather compensation and where that curve is set, which is the setting Rodders53 is talking about.
0 -
Have you actually got a heat pump?
What makes you think that `catch up runs' are at a higher water temperature for all heat pumps?
My Daikin runs at a fixed lwt, either one I set or one set by the wdc
If the house is colder because the heating was off my heat pump still runs at the same lwt, more heat is produced because the dt between the room temperature and the mean dt of my emitters is higher.
That may result in extra electricity use due to a faster flow rate and/or a bigger dT between flow and return temperatures, but that is also likely to be at a better efficiency too.
I would suggest you need to know what make and model of heat pump the op has before giving such general advice, it could well be wrong!
0
Categories
- All Categories
- 356K Banking & Borrowing
- 255K Reduce Debt & Boost Income
- 456.3K Spending & Discounts
- 248.5K Work, Benefits & Business
- 606.3K Mortgages, Homes & Bills
- 179.1K Life & Family
- 264.1K Travel & Transport
- 1.6M Hobbies & Leisure
- 16.2K Discuss & Feedback
- 37.7K Read-Only Boards