13 amp Cooker / hob question

2

Comments

  • subjecttocontract
    subjecttocontract Posts: 3,806 Forumite
    Part of the Furniture 1,000 Posts Photogenic Name Dropper

    Ive never heard of any property other than a caravan that doesn't have a 30amp supply for a cooker. A 13amp 4 ring hob is going to seriously limit what can be cooked and I wish you luck but it wouldn't be for me. Are you 100% sure there isn't a 30 amp supply in the kitchen ?

  • jennifernil
    jennifernil Posts: 5,857 Forumite
    Part of the Furniture 1,000 Posts Name Dropper

    You could buy a portable 2 ring hob, either induction or traditional, to sit on a worktop, and either a large air fryer or a mini oven. I would not get one that has the 2 hobs on top of the oven. That would be absolutely fine for one or two people.

  • johnnyren
    johnnyren Posts: 194 Forumite
    Part of the Furniture 100 Posts Name Dropper Combo Breaker

    I’m not an electrician but there is a single fused spur box next to a double electric socket , But what that is for I’ve no idea , The old oven and hob had already been removed

    There is a cooker hood still in place with has a large socket and a large sealed plug if that makes any sense . I don’t know if that’s what the spur dockets for

    Maybe I’m better just getting an electrician out , We thought it might be simpler going down the 13 amp route , But I think I’ll sleep better getting it all done right , Now where’s my wallet lol

  • QrizB
    QrizB Posts: 24,659 Forumite
    10,000 Posts Fifth Anniversary Photogenic Name Dropper

    When the future Mrs QrizB and I moved into our first shared home, we had a Baby Belling.

    A bit like this but with coiled electric hotplates rather than solid ones, and it was white not black:

    https://business.currys.co.uk/catalogue/domestic-appliances/cooking/free-standing-cookers/belling-baby-321r-electric-tabletop-cooker-black/B172644B

    It was all we needed for our first years together.

    N. Hampshire, he/him. Octopus Intelligent Go elec / Fuse gas / Vodafone BB / iD mobile. Kirk Hill Co-op member.
    2.72kWp PV facing SSW installed Jan 2012. 11 x 247w panels, 3.6kw inverter. 37 MWh generated, long-term average 2.6 Os.
    Ofgem cap table, Ofgem cap explainer. Economy 7 cap explainer. Gas vs E7 vs peak elec heating costs, Best kettle!
  • Rodders53
    Rodders53 Posts: 3,015 Forumite
    Part of the Furniture 1,000 Posts Name Dropper Photogenic

    Picture of the Falt's Consumer Unit (aka fusebox) with cover open. Clear in focus so the printing and any labelling can be read. Ditto for the Kitchen worktop / oven area plugs sockets and switches…

    From that some slightly more accurate advice can be provided. (E.g. a 32A breaker labelled COOKER or OVEN may be present). ;)

    My Bosch 4-burner induction hob can be electronically hobbled to a max 13A power draw. My youngest son has a plug-in 13A 4 burner induction hob he cooks for the family of 4 plus us (and even more people) with… No major issues (though as said it limits the power to any individual burner by pulsing/switching them on/off quite quickly). So they can work OK.

  • Marmaduke123
    Marmaduke123 Posts: 869 Forumite
    Part of the Furniture 500 Posts Name Dropper

    I have a Bosch induction hob with 4 "burners" two of which can be joined together to make a bigger cooking area if required.

    It is built in to the worktop and plugs in to a standard 13 amp socket under the worktop which was previously used for the ignition system for the gas hob I used to have.

    I was doubtful about a 13 amp induction hob but haven't encountered any problems with it and it's more than sufficient for my needs.

    I also have a built in fan oven which plugs into a 13 amp socket. There are loads of these on the market.

  • Section62
    Section62 Posts: 11,713 Forumite
    10,000 Posts Fifth Anniversary Name Dropper

    From that some slightly more accurate advice can be provided. (E.g. a 32A breaker labelled COOKER or OVEN may be present). ;)

    Though the presence of a 32A MCB/RCBO with "Cooker" or "Oven" written under it doesn't necessarily mean there is a connection point in the kitchen which can safely supply 32A.

  • Rodders53
    Rodders53 Posts: 3,015 Forumite
    Part of the Furniture 1,000 Posts Name Dropper Photogenic
  • Section62
    Section62 Posts: 11,713 Forumite
    10,000 Posts Fifth Anniversary Name Dropper

    Which won't help much because pictures won't show whether there is a cable between the consumer unit and whatever is in the kitchen, nor whether the cable (if there is one) has the capacity for 32A and/or is in a satisfactory condition.

    One of the possible reasons the OP's daughter has been told the 13A max thing, and the somewhat unusual situation of apparently not having a proper cooker feed, might be that the cooker feed (if there ever was one) has been condemned due to the cable being underrated or damaged.

    Even if there is a cooker point in the kitchen, the reason for the 13A max thing needs to be understood/clarified, which may mean getting an electrician in to do a check.

    (No need for the "Doh!!!)

  • jimi_man
    jimi_man Posts: 1,580 Forumite
    Part of the Furniture 1,000 Posts Photogenic Name Dropper

    It is actually relatively common depending on the type of home. New places or conversions might not have them, or sometimes older places that were designed with gas cooking in mind.

    Usually they are induction hobs and they are designed for a 13 amp supply (with a moulded plug) and the hobs themselves contain circuitry that doesn't overload the system. So the hob won't let you run all four elements at once on full power and they are usually limited to around 3kw, so if all four are on then they are limited.

    Obviously a dedicated CCU is best but you have to work with what you have and if just want to be able to cook a few things without the expense of installing a 30amp supply then they are a compromise.

Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 355.5K Banking & Borrowing
  • 254.8K Reduce Debt & Boost Income
  • 456.1K Spending & Discounts
  • 248.1K Work, Benefits & Business
  • 605.6K Mortgages, Homes & Bills
  • 179K Life & Family
  • 263.4K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16.1K Discuss & Feedback
  • 37.7K Read-Only Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.