We’d like to remind Forumites to please avoid political debate on the Forum.

This is to keep it a safe and useful space for MoneySaving discussions. Threads that are – or become – political in nature may be removed in line with the Forum’s rules. Thank you for your understanding.

📨 Have you signed up to the Forum's new Email Digest yet? Get a selection of trending threads sent straight to your inbox daily, weekly or monthly!

I don't understand how temperature is regulated with my ASHP

I have a Vaillant aroTherm Plus 5kW heat pump and a SensoComfort 720f thermostatic controller.

The SensoComfort has a control called a heat curve which determines my system's flow temperature for any given outside temperature.

But there is also a control to set the desired ambient temperature.

What I don't understand is the relationship between these two controls. I can see that the Heat Curve determines what the flow temperature will be, and I presume that the flow temperature determines the ambient temperature.

But if I desire a different ambient temperature, this surely requires a different flow temperature from the temperature specified by the Heat Curve. So it looks as if the Heat Curve is only true for one ambient temperature. Is that the case? 

Comments

  • Fatferds12
    Fatferds12 Posts: 44 Forumite
    Sixth Anniversary 10 Posts Name Dropper Photogenic
    There's also a very helpful Facebook group for Vaillant air source heat pumps you may find useful
    https://www.facebook.com/groups/488794632317506/
  • Netexporter
    Netexporter Posts: 2,238 Forumite
    1,000 Posts Second Anniversary Name Dropper
    You might find this video helpful:

    Just Set Your Heat Pump Curve to 40 Degrees!
  • Vitor
    Vitor Posts: 1,094 Forumite
    1,000 Posts First Anniversary Photogenic Name Dropper
    edited 16 November at 11:27AM
    Your SensoComfort isn’t running two competing controls. The heat curve is the primary setting that tells the system what flow temperature to use for any outdoor temperature. The room-temperature set-point doesn’t override that curve, it only applies a small offset up or down. In practice you tune the heat curve so that, on continuous operation, the house naturally settles near your set indoor temperature. If it runs a bit cool, you raise the curve; if it overshoots, you lower it. The room setting then just trims things. Weather compensation works best when the curve does most of the work.
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 352.7K Banking & Borrowing
  • 253.8K Reduce Debt & Boost Income
  • 454.6K Spending & Discounts
  • 245.8K Work, Benefits & Business
  • 601.8K Mortgages, Homes & Bills
  • 177.7K Life & Family
  • 259.7K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 15.9K Discuss & Feedback
  • 37.7K Read-Only Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.