I don't understand how temperature is regulated with my ASHP
Redlander
Posts: 94 Forumite
in Heat pumps
I have a Vaillant aroTherm Plus 5kW heat pump and a SensoComfort 720f thermostatic controller.
The SensoComfort has a control called a heat curve which determines my system's flow temperature for any given outside temperature.
But there is also a control to set the desired ambient temperature.
What I don't understand is the relationship between these two controls. I can see that the Heat Curve determines what the flow temperature will be, and I presume that the flow temperature determines the ambient temperature.
But if I desire a different ambient temperature, this surely requires a different flow temperature from the temperature specified by the Heat Curve. So it looks as if the Heat Curve is only true for one ambient temperature. Is that the case?
The SensoComfort has a control called a heat curve which determines my system's flow temperature for any given outside temperature.
But there is also a control to set the desired ambient temperature.
What I don't understand is the relationship between these two controls. I can see that the Heat Curve determines what the flow temperature will be, and I presume that the flow temperature determines the ambient temperature.
But if I desire a different ambient temperature, this surely requires a different flow temperature from the temperature specified by the Heat Curve. So it looks as if the Heat Curve is only true for one ambient temperature. Is that the case?
1
Comments
-
There's also a very helpful Facebook group for Vaillant air source heat pumps you may find useful
https://www.facebook.com/groups/488794632317506/0 -
0
-
Your SensoComfort isn’t running two competing controls. The heat curve is the primary setting that tells the system what flow temperature to use for any outdoor temperature. The room-temperature set-point doesn’t override that curve, it only applies a small offset up or down. In practice you tune the heat curve so that, on continuous operation, the house naturally settles near your set indoor temperature. If it runs a bit cool, you raise the curve; if it overshoots, you lower it. The room setting then just trims things. Weather compensation works best when the curve does most of the work.1
Confirm your email address to Create Threads and Reply
Categories
- All Categories
- 352.7K Banking & Borrowing
- 253.8K Reduce Debt & Boost Income
- 454.6K Spending & Discounts
- 245.8K Work, Benefits & Business
- 601.8K Mortgages, Homes & Bills
- 177.7K Life & Family
- 259.7K Travel & Transport
- 1.5M Hobbies & Leisure
- 15.9K Discuss & Feedback
- 37.7K Read-Only Boards