Electric meter replaced, now gas heating not working (boiler has electric starter and thermostat)

Options
dekaspace1
dekaspace1 Posts: 477 Forumite
Fifth Anniversary 100 Posts Name Dropper
I am with Scottish Power.

Now the meter has been replaced theres no electrical power going into the thermostat in living room, or the boiler.

I have gas supply with British Gas and SP are saying BG fault as they supply the gas, but it's an electrical issue.

About to phone BG but wanted advice first.
«1

Comments

  • Netexporter
    Netexporter Posts: 1,986 Forumite
    1,000 Posts First Anniversary Name Dropper
    Have you checked to see if the circuit breaker for the boiler has tripped?
  • dekaspace1
    dekaspace1 Posts: 477 Forumite
    Fifth Anniversary 100 Posts Name Dropper
    Checked all the trip switches and they are up, but I would assume the thermostat in another room would be a different circuit.
  • Netexporter
    Netexporter Posts: 1,986 Forumite
    1,000 Posts First Anniversary Name Dropper
    edited 19 July at 3:53PM
    A wired thermostat will take its power from the boiler. Have you tried the reset button on the boiler? 

    Also check that the gas hasn't been switched off at the meter. No gas pressure would prevent the boiler attempting to fire up.
  • QrizB
    QrizB Posts: 18,392 Forumite
    10,000 Posts Fourth Anniversary Photogenic Name Dropper
    When was your meter replaced? Yesterday?
    Can you share a photo of the meter, your consumer unit and the wiring between the two?
    Do ythavena photo of your old meter that you could also share?
    N. Hampshire, he/him. Octopus Intelligent Go elec & Tracker gas / Vodafone BB / iD mobile. Ripple Kirk Hill member.
    2.72kWp PV facing SSW installed Jan 2012. 11 x 247w panels, 3.6kw inverter. 34 MWh generated, long-term average 2.6 Os.
    Not exactly back from my break, but dipping in and out of the forum.
    Ofgem cap table, Ofgem cap explainer. Economy 7 cap explainer. Gas vs E7 vs peak elec heating costs, Best kettle!
  • dekaspace1
    dekaspace1 Posts: 477 Forumite
    Fifth Anniversary 100 Posts Name Dropper
    Just a few hours ago, 

    The boiler I assume is connected to electric, the pressure looks ok but the boiler display is blank it has a switch on wall which I have flipped off and on tested off for a minute then back on too.

    The new meter is a SMETS2, old meter was 2 analog meters as was the teleswitch ones even though gas heating was installed prior to my tenancy by a few years.

    I do have some old photos of the meter but not the wiring, there was an old consumer unit from the storage heater days but it's disconnected, but I have just in case made sure they are up.
  • molerat
    molerat Posts: 34,633 Forumite
    Part of the Furniture 10,000 Posts Name Dropper Photogenic
    edited 19 July at 4:08PM
    If it is "odd" off peak wiring there is a chance the circuit has not been reconnected or connected to the off peak side of the meter - do you still have multi rate ?  Photos of the new set up ?
  • dekaspace1
    dekaspace1 Posts: 477 Forumite
    Fifth Anniversary 100 Posts Name Dropper
    Will get some up soon, it's downstairs and I have to use a stick to go up and down stairs so having a quick rest.

    I notice so far it's saying zero usage on the meter.
  • QrizB
    QrizB Posts: 18,392 Forumite
    10,000 Posts Fourth Anniversary Photogenic Name Dropper
    molerat said:
    If it is "odd" off peak wiring there is a chance the circuit has not been reconnected or connected to the off peak side of the meter - do you still have multi rate ?  Photos of the new set up ?
    That was my thought too, that somehow the circuit feeding the boiler hasn't been (re)connected to the new meter feed.

    N. Hampshire, he/him. Octopus Intelligent Go elec & Tracker gas / Vodafone BB / iD mobile. Ripple Kirk Hill member.
    2.72kWp PV facing SSW installed Jan 2012. 11 x 247w panels, 3.6kw inverter. 34 MWh generated, long-term average 2.6 Os.
    Not exactly back from my break, but dipping in and out of the forum.
    Ofgem cap table, Ofgem cap explainer. Economy 7 cap explainer. Gas vs E7 vs peak elec heating costs, Best kettle!
  • dekaspace1
    dekaspace1 Posts: 477 Forumite
    Fifth Anniversary 100 Posts Name Dropper
    And it did have off peak and regular meter (so 2 meters) before and the teleswitch, the meters if I remember had 2008 writen on them as when installed.
  • molerat
    molerat Posts: 34,633 Forumite
    Part of the Furniture 10,000 Posts Name Dropper Photogenic
    edited 19 July at 4:21PM
    If you had 2 meters, known as complex metering, and changed to a single meter there is a fair possibility something has been missed.
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 351.2K Banking & Borrowing
  • 253.2K Reduce Debt & Boost Income
  • 453.7K Spending & Discounts
  • 244.2K Work, Benefits & Business
  • 599.2K Mortgages, Homes & Bills
  • 177K Life & Family
  • 257.6K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16.1K Discuss & Feedback
  • 37.6K Read-Only Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.