Boiler losing pressure, need help finding the cause (leak?)
Comments
-
I understand a useful aspect of a 'combi' boiler is that it can be kept running for DHW with the radiator system fully isolated from it via the valves under the boiler. If the pressure continues to drop, the leak will be from within the boiler.But - pressure check and discharge pipe check first.2
-
ThisIsWeird said:I understand a useful aspect of a 'combi' boiler is that it can be kept running for DHW with the radiator system fully isolated from it via the valves under the boiler. If the pressure continues to drop, the leak will be from within the boiler.But - pressure check and discharge pipe check first.
What I was going to post
Check if there is any evidence of dried water/gunge under the boiler/pipes
However, I'm almost 100 cetain thei is a leak, pinhole type and the reason ti is not showing is it drys out with the heat.
So check and check the combi, exposed pipes etc and if still leaking, try a leak sealer and IMO that will fix it, at least massively reduce the loss of waters
NB: Once you have done that at the same time add more inhibitor as pin leaks are often a result of rust/gunge - but it could be a poor connection on new pipes somewhere
Good luck
1 -
Yes, there could be a heat-affected leak. The pressure loss is pretty dramatic, tho', with sometimes a drop from 2bar to zero in a few days - that would usually represent a few cupfuls of water - and it doesn't happen when the CH is not being used.0
-
locky123 said:Checked the pressure relief valve isnt dripping from the discharge pipe? Checked the expansion vessel is holding the correct pressure? Cracked heat exchanger?0
-
Bullit_2600 said:locky123 said:Checked the pressure relief valve isnt dripping from the discharge pipe? Checked the expansion vessel is holding the correct pressure? Cracked heat exchanger?
Don't touch the EV. Please do this - locate the safety discharge pipe going outside your house from the boiler - it'll likely be on the nearest wall to the boiler. It'll be 15mm copper, and either point down close to the ground, or will bend back on itself and point against the wall. When you find it, tie or tape a small clear plastic bag over the end to monitor any discharge - there should be none.
0 -
Bullit_2600 said:locky123 said:Checked the pressure relief valve isnt dripping from the discharge pipe? Checked the expansion vessel is holding the correct pressure? Cracked heat exchanger?1
-
ThisIsWeird said:Bullit_2600 said:locky123 said:Checked the pressure relief valve isnt dripping from the discharge pipe? Checked the expansion vessel is holding the correct pressure? Cracked heat exchanger?
Don't touch the EV. Please do this - locate the safety discharge pipe going outside your house from the boiler - it'll likely be on the nearest wall to the boiler. It'll be 15mm copper, and either point down close to the ground, or will bend back on itself and point against the wall. When you find it, tie or tape a small clear plastic bag over the end to monitor any discharge - there should be none.
Isn't it highly unlikely that both vessels are at fault here and therefore that the pressure release valve is not being triggered or is dripping?
An easy thing to check though.1 -
JohnB47 said:ThisIsWeird said:Bullit_2600 said:locky123 said:Checked the pressure relief valve isnt dripping from the discharge pipe? Checked the expansion vessel is holding the correct pressure? Cracked heat exchanger?
Don't touch the EV. Please do this - locate the safety discharge pipe going outside your house from the boiler - it'll likely be on the nearest wall to the boiler. It'll be 15mm copper, and either point down close to the ground, or will bend back on itself and point against the wall. When you find it, tie or tape a small clear plastic bag over the end to monitor any discharge - there should be none.
Isn't it highly unlikely that both vessels are at fault here and therefore that the pressure release valve is not being triggered or is dripping?
An easy thing to check though.Fair enough - an external one should be easy to check. The results could largely be meaningless, tho', as the air side will be affected by the water side, regardless of how much - or how little - air is inside it. Unless water spurts out, of course :-)If the 'system' is currently pressurised to 2bar, then the air side of the EV will also indicate this pressure, so a deceptive reading. Really, it needs the system side to first be depressurised, and then a reading taken of the air charge pressure.I think.The easy, layman, check is to see if owt is coming out t'pipe.0 -
Expansion vessel pressure is checked when the system and/or boiler is depressurised.1
-
Just responding to some previous comments, the reason we were topping up the pressure to 2 bar was on advice from the plumber to give us a few days where we didnt have to top it up and we've just kept doing it.And during winter we are doing this once / twice a week.
In the summer we didnt need to do it so the problem only occurs when the central heating is on.Unfortunately the pipes are boxed in but I cannot see any signs of leaks under the boiler which the same plumber has also checked for leaks and did not find any.Doesnt mean that isnt the cause though maybe it was missed.As mentioned boiler is only 2 years old so I'd hope it wasnt a cracked heat exchanger (which was previously checked) and also all radiators are new. May mean there is a chance of error at installation?I have just completed the following actions today:1. Bleed radiators - DONE - all ok as had bled them last week so no air.2. Check they are all tight - DONE3. Tighten valves on radiators - DONE4. Place paper tissue round each rad pipe - DONE5. Tie clear bag around discharge pipe (comes straight out the wall by boiler) - DONE6. Top up boiler to 1.2 - DONE (was at 2 so I had to bleed a radiator to get it down to 1.2 (2.5l of water)7. Confirm what pressure gauge is after turning on(a) after 1 min = 1.5(b) after 30 mins = 1.9(c) after 60 mins = 1.9 with dial flickering to 2(d) 10 mins off = 1.5(e) 30 mins off = 1.4(f) 60 mins = 1.2I'll keep an eye on the pressure gauge and the tissue paper for any signs of leaks.
Really appreciate all the comments and help1
Confirm your email address to Create Threads and Reply

Categories
- All Categories
- 350.6K Banking & Borrowing
- 253K Reduce Debt & Boost Income
- 453.3K Spending & Discounts
- 243.6K Work, Benefits & Business
- 598.3K Mortgages, Homes & Bills
- 176.7K Life & Family
- 256.7K Travel & Transport
- 1.5M Hobbies & Leisure
- 16.1K Discuss & Feedback
- 37.6K Read-Only Boards