ASHP - Pipe size

waqasahmed
waqasahmed Posts: 1,994 Forumite
Part of the Furniture 1,000 Posts Name Dropper Combo Breaker
edited 23 January 2024 at 3:33PM in Heat pumps
Let's say you don't have good insulation 

Could you theoretically still achieve the same low flow temps with oversized pipes, and oversized rads?

Obviously, you should insulate your house anyway, but I was wondering if you'd basically achieve the same COP without having done that?

And then basically having pipes that are already "oversized" so to speak 

Comments

  • COP has nothing to do with insulation.  The amount of insulation you have will affect the amount of energy needed to heat your house but this has nothing to do with the efficiency of a heat pump.

    The efficiency (and hence COP) of a heat pump (ASHP) depends on the temperature difference between the outside air and the water leaving the heat pump.  If you can keep this as low as possible you will achieve the best efficiency.  You can do that with "oversized" radiators (or Underfloor Heating).  For any give water temperature the poorer the insulation the bigger the radiator you will need for a room of some particular size, if that is what you mean.

    You can also boost the heat output from your radiators by increasing the flow rate through them to reduce the temperature drop across the radiator.  This does not require "oversized" pipes but if the pipes are too narrow if may be difficult to achieve the flow rate you want.      
    Reed
  • shinytop
    shinytop Posts: 2,158 Forumite
    Eighth Anniversary 1,000 Posts Name Dropper Photogenic
    edited 22 January 2023 at 12:20AM
    Yes, as long as your rads are sized correctly to give off enough heat at the flow temp you want.   COP has nothing directly to do with insulation.  
  • waqasahmed
    waqasahmed Posts: 1,994 Forumite
    Part of the Furniture 1,000 Posts Name Dropper Combo Breaker
    COP has nothing to do with insulation.  The amount of insulation you have will affect the amount of energy needed to heat your house but this has nothing to do with the efficiency of a heat pump.

    The efficiency (and hence COP) of a heat pump (ASHP) depends on the temperature difference between the outside air and the water leaving the heat pump.  If you can keep this as low as possible you will achieve the best efficiency.  You can do that with "oversized" radiators (or Underfloor Heating).  For any give water temperature the poorer the insulation the bigger the radiator you will need for a room of some particular size, if that is what you mean.

    You can also boost the heat output from your radiators by increasing the flow rate through them to reduce the temperature drop across the radiator.  This does not require "oversized" pipes but if the pipes are too narrow if may be difficult to achieve the flow rate you want.      
    Thanks. That's what my impression was too. That's not too bad then, if you're willing to seriously oversize your pipes anyway
  • With radiators it's the bigger the better.  Not so with pipes, they just need to be more than a minimum size.  Typically it is 15 mm to individual radiators, 22 mm feeding multiple radiators and 28mm from the heat pump to the DHW cylinder and buffer tank.  
    Reed
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 350.1K Banking & Borrowing
  • 252.8K Reduce Debt & Boost Income
  • 453.1K Spending & Discounts
  • 243.1K Work, Benefits & Business
  • 597.5K Mortgages, Homes & Bills
  • 176.5K Life & Family
  • 256K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16.1K Discuss & Feedback
  • 37.6K Read-Only Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.