Water not getting fully hot

3 Posts

Hi I was hoping to get some clues as to why my hot water is only getting luke warm in the cylinder. It used to get hot after about 30 minutes, now after 1hr 30 mins it's only luke warm even though the pipe to the cylinder is getting hot. I have an indirect cylinder fed from a tank in the loft. The heating works fine and the 3 way motorised valve seems to be working as it should, i.e the heating and HW systems only kick in when called for. I recently balanced the radiators and everything has been absolutely fine for about a month. I wanted to balance the HW coil but I'm not sure where the valve for this is located. There is one on a pipe that connects near the bottom of the 3 way valve which I've adjusted in and out but it makes no difference. There is also a flat headed screw on the inlet or outlet pipe on the tank (on the top pipe halfway up the cylinder). I wondered if there might be a blockage or an airlock? Many thanks in advance.
0
Latest MSE News and Guides
Replies
2. It's possible the valve you have altered (near bottom of 3 way valve) is to balance flow between hot water and heating. If you have nearly closed it, you won't get so much heat in the cylinder coil.
.withdrawal, NOT withdrawel ..bear with me, NOT bare with me
.definitely, NOT definately ......separate, NOT seperate
should have, NOT should of .....guaranteed, NOT guarenteed
Motorised valves can become sloppy and sticky, I think more likely than a blockage is a 22mm pipe.
The cylinder stat works ok? Clicks at the correct temp?
I've had the valve half open and fully open.It's the one in the first pic
It was new 18 months ago but I'll look into testing it.
This forum can be dangerous with the advice posted
The fault is likely to be the cylinder stat. Has it stopped calling for heat when the water temp is still lukewarm? Has the temp control on it been knocked/adjusted? It's tied to the cylinder by that elastic band. Pull back the insulation to check it's located & set properly.
The install is a bit scrappy too. Looks like the plumber chucked all the parts onto the floor and joined them up where they fell.
Treasure the moments that you have. Savour them for as long as you can for they will never come back again.
Treasure the moments that you have. Savour them for as long as you can for they will never come back again.
I can't follow the pipe layout on my phone, so need to wait before I'm home to see it on a big screen.
Theoretically, yes - the more the by-pass is closed, the more the hot water is forced through the cylinder loop, so the faster the water is heated up. I have to say, I am struggling to understand the logic of the bypass valve, tho' - why do you want any water going straight back to the boiler, unless it's on the CH circuit which has TRVs that can close off? Never fully understood that.
Have you fitted a magnetic filter to the return to the boiler? If you can, do so. You can add chemicals via it, but you'll also soon know if what the plumber said - you have sludge - is true. AND, you want to catch that sludge if it does exist...