Ectophile said:
Unless all the radiators are off, and the water is flowing through a bypass valve instead.Signature on holiday for two weeks0 -
for me to get a 10-12 degree difference between the flow and return at the rads im having to turn the valves right down on 4 rads, to the point they aren't working properly as there isn't enough flow, As soon as i start opening the valves to get more flow the furthest 3 radiators stop working properly as they aren't getting enough flow.
0 -
piperm87 said:for me to get a 10-12 degree difference between the flow and return at the rads im having to turn the valves right down on 4 rads, to the point they aren't working properly as there isn't enough flow, As soon as i start opening the valves to get more flow the furthest 3 radiators stop working properly as they aren't getting enough flow.
The principle of balancing is to restrict the flow sufficiently to let the energy from the heated water dissipate through the radiator and into the room. Fully open, the water rushes around, the rad still gets hot but the return temperature to the boiler is too high and the boiler will shut down thinking there is no demand for heated water and the whole system runs a whole lot less efficiently.
Have a look at any radiator specifications, you will see references to their output based on the temperature drop across the rad, called "delta t" for difference in temperature, eg 12∆T is a 12 degree drop between inlet and outlet. Balancing is always done with the system & house just coming up to temperature (but stats not satisfied so as to keep the boiler & pump running) and with the opposite side to the lockshield fully open (whether it's a manual valve or thermostatic type) and then adjust the delta with the lockshield. A handheld digital thermometer is best and taking your time a bonus. It could take half a day to balance a 4 bed house since each adjustment then has a knock on effect on the other radiators. As you found.
Signature on holiday for two weeks0 -
Mutton_Geoff said:piperm87 said:for me to get a 10-12 degree difference between the flow and return at the rads im having to turn the valves right down on 4 rads, to the point they aren't working properly as there isn't enough flow, As soon as i start opening the valves to get more flow the furthest 3 radiators stop working properly as they aren't getting enough flow.
The principle of balancing is to restrict the flow sufficiently to let the energy from the heated water dissipate through the radiator and into the room. Fully open, the water rushes around, the rad still gets hot but the return temperature to the boiler is too high and the boiler will shut down thinking there is no demand for heated water and the whole system runs a whole lot less efficiently.
Have a look at any radiator specifications, you will see references to their output based on the temperature drop across the rad, called "delta t" for difference in temperature, eg 12∆T is a 12 degree drop between inlet and outlet. Balancing is always done with the system & house just coming up to temperature (but stats not satisfied so as to keep the boiler & pump running) and with the opposite side to the lockshield fully open (whether it's a manual valve or thermostatic type) and then adjust the delta with the lockshield. A handheld digital thermometer is best and taking your time a bonus. It could take half a day to balance a 4 bed house since each adjustment then has a knock on effect on the other radiators. As you found.Thanks, I get what your saying and i totally agree but to achieve the 10 -12 degree difference on the closest rads the lockshields are almost closed which is restricting flow to the point where only the top half of the radiators get heat, the bottoms half stay cold or take an age to warm up - if i open the valves more then the whole rad will get hot but im losing rads further down the line. It feels like a lose lose situation really.. I've lost count of the amount of hours i've spent going around the house with my digital thermometer trying to get everything balanced up but once done im only getting use of half the capacity of each radiator.0 -
piperm87 said:Mutton_Geoff said:piperm87 said:for me to get a 10-12 degree difference between the flow and return at the rads im having to turn the valves right down on 4 rads, to the point they aren't working properly as there isn't enough flow, As soon as i start opening the valves to get more flow the furthest 3 radiators stop working properly as they aren't getting enough flow.
The principle of balancing is to restrict the flow sufficiently to let the energy from the heated water dissipate through the radiator and into the room. Fully open, the water rushes around, the rad still gets hot but the return temperature to the boiler is too high and the boiler will shut down thinking there is no demand for heated water and the whole system runs a whole lot less efficiently.
Have a look at any radiator specifications, you will see references to their output based on the temperature drop across the rad, called "delta t" for difference in temperature, eg 12∆T is a 12 degree drop between inlet and outlet. Balancing is always done with the system & house just coming up to temperature (but stats not satisfied so as to keep the boiler & pump running) and with the opposite side to the lockshield fully open (whether it's a manual valve or thermostatic type) and then adjust the delta with the lockshield. A handheld digital thermometer is best and taking your time a bonus. It could take half a day to balance a 4 bed house since each adjustment then has a knock on effect on the other radiators. As you found.Thanks, I get what your saying and i totally agree but to achieve the 10 -12 degree difference on the closest rads the lockshields are almost closed which is restricting flow to the point where only the top half of the radiators get heat, the bottoms half stay cold or take an age to warm up - if i open the valves more then the whole rad will get hot but im losing rads further down the line. It feels like a lose lose situation really.. I've lost count of the amount of hours i've spent going around the house with my digital thermometer trying to get everything balanced up but once done im only getting use of half the capacity of each radiator.
Her courage will change the world.
Treasure the moments that you have. Savour them for as long as you can for they will never come back again.1 -
piperm87 said:Thanks, I get what your saying and i totally agree but to achieve the 10 -12 degree difference on the closest rads the lockshields are almost closed which is restricting flow to the point where only the top half of the radiators get heat, the bottoms half stay cold or take an age to warm up - if i open the valves more then the whole rad will get hot but im losing rads further down the line. It feels like a lose lose situation really.. I've lost count of the amount of hours i've spent going around the house with my digital thermometer trying to get everything balanced up but once done im only getting use of half the capacity of each radiator.Signature on holiday for two weeks1
-
Pump isn't working properly or blocked magnaclean filter assuming you have one. If both of these are OK then system flush. I'm assuming you have done the balancing correctly.Living the dream in the Austrian Alps.1
Confirm your email address to Create Threads and Reply

Categories
- All Categories
- 351.2K Banking & Borrowing
- 253.2K Reduce Debt & Boost Income
- 453.7K Spending & Discounts
- 244.1K Work, Benefits & Business
- 599.2K Mortgages, Homes & Bills
- 177K Life & Family
- 257.5K Travel & Transport
- 1.5M Hobbies & Leisure
- 16.1K Discuss & Feedback
- 37.6K Read-Only Boards