Combi boiler loses pressure when idle but regains it when working
Comments
-
Bendy_House said:
I don't think a boiler is going to quibble over a ~0.1bar discrepancy.FreeBear said:
Just reducing the CH pressure to zero still leaves water in the system - You need to take in to account the "head" of water still behind the diaphragm in the EV. There will always be some pressure there unless you drain the system down or disconnect the EV completely.Bendy_House said:I don't know that this is the correct way, but is how I've always done it for the above reason. When I did sil's boiler a good 2 years ago, I depressurised the system via a bleed screw, but then nipped it up again as it was only me there, and I didn't want a squirt spaffed across the wall (sorry - too visual?
) What I found was, the air pressure side rose dramatically with a single pump as the diaph couldn't go anywhere. Had I left it at that - supposedly 'correct' air pressure reading - there would hardly have been an air bubble inside the EV. So I had to keep running to the nearest rad and bleeding it back down to zero after every pump - and the air pressure reading fell accordingly. Took a bludy age... To fully air-charge the EV took, I dunno, around 20-30 strokes, and 20-30 runs.At this point - correct air pressure achieved, coupled with zero on the water side - the diaphragm would have been squished right tight against the far wall of the EV leaving no room for the water, just as if delivered new.Once the air side is at the recommended pressure (0.75b, I think it was), coupled with the system side being at 'zero', then the water side can be repressurised. At the recommended ~1bar, the diaph should then be somewhere in the middle again.
Tbh, I personally won't be bothering with anything as involved as draining a system, or even just a boiler. Bleed screw for me.Do not discount the pressure from even a modest head of water. Just 2.4m would equate to 3.5psi or 0.23Bar - That would be a significant error if you were trying to repressurise the EV to 1Bar (14.7psi).
Any language construct that forces such insanity in this case should be abandoned without regrets. –
Erik Aronesty, 2014
Treasure the moments that you have. Savour them for as long as you can for they will never come back again.2 -
I won't discount it. But I won't do it either
Solution - bleed a rad on t'same level as the boiler. (I think that would work...?)0 -
FreeBear said:Bendy_House said:
I don't think a boiler is going to quibble over a ~0.1bar discrepancy.FreeBear said:
Just reducing the CH pressure to zero still leaves water in the system - You need to take in to account the "head" of water still behind the diaphragm in the EV. There will always be some pressure there unless you drain the system down or disconnect the EV completely.Bendy_House said:I don't know that this is the correct way, but is how I've always done it for the above reason. When I did sil's boiler a good 2 years ago, I depressurised the system via a bleed screw, but then nipped it up again as it was only me there, and I didn't want a squirt spaffed across the wall (sorry - too visual?
) What I found was, the air pressure side rose dramatically with a single pump as the diaph couldn't go anywhere. Had I left it at that - supposedly 'correct' air pressure reading - there would hardly have been an air bubble inside the EV. So I had to keep running to the nearest rad and bleeding it back down to zero after every pump - and the air pressure reading fell accordingly. Took a bludy age... To fully air-charge the EV took, I dunno, around 20-30 strokes, and 20-30 runs.At this point - correct air pressure achieved, coupled with zero on the water side - the diaphragm would have been squished right tight against the far wall of the EV leaving no room for the water, just as if delivered new.Once the air side is at the recommended pressure (0.75b, I think it was), coupled with the system side being at 'zero', then the water side can be repressurised. At the recommended ~1bar, the diaph should then be somewhere in the middle again.
Tbh, I personally won't be bothering with anything as involved as draining a system, or even just a boiler. Bleed screw for me.Do not discount the pressure from even a modest head of water. Just 2.4m would equate to 3.5psi or 0.23Bar - That would be a significant error if you were trying to repressurise the EV to 1Bar (14.7psi).There’s clearly a problem with low pressure in the EV at the moment, but they normally work over a range of pressures, and they seem to continue to operate even when not at an optimal pressure.No reliance should be placed on the above! Absolutely none, do you hear?1 -
Yes, in most cases they seem to only cause issues that need resolving when they have nearly emptied!Don't get me wrong - Shiraz and FB are correct, but I know what's easier for me (and will be for most folk), what will give a full resolution, and what I'll continue to do.1
-
Bear in mind that most boilers are happy working with a pressure anywhere in the range 1-2 bars, anyway, and there’s bound to be a fair bit of leeway.No reliance should be placed on the above! Absolutely none, do you hear?0
Confirm your email address to Create Threads and Reply
Categories
- All Categories
- 352.9K Banking & Borrowing
- 253.9K Reduce Debt & Boost Income
- 454.7K Spending & Discounts
- 246K Work, Benefits & Business
- 602K Mortgages, Homes & Bills
- 177.8K Life & Family
- 259.9K Travel & Transport
- 1.5M Hobbies & Leisure
- 16K Discuss & Feedback
- 37.7K Read-Only Boards