Ditching gas, going electric immersion only, a wee project

1246727

Comments

  • Solarchaser
    Solarchaser Posts: 1,758 Forumite
    Sixth Anniversary 1,000 Posts Name Dropper
    As an aside of sorts, I mentioned before and element thermostats being about 70C, but I notice a large variability in the 4 elements I have.
    I've been trying like a bear to find a double isolating high temperature replacement thermostat (x4) to run say 90C with a 95C manual reset, but the various stores I've visited and search terns I use have not came up with any usable solutions. 

    It seems the industry standard is a 10% tolerance too, which is mad, so a 70C stat could be somewhere between 63C and 77C, no wonder they are all different. 

    I've been carrying about a stat for a couple of weeks to try and get a replacement that will work, and suddenly noticed there was a couple of screws holding it together... I mistakenly assumed it was a sealed unit.

    So turns out these ones work by a fine threaded screw pushing against what I assume is a bimetallic strip,  this screw is the pointer you adjust for temperature, and the pointer sits on top of the screw in really hundreds of permutations so no wonder they are all so variable.

    So I now need to set up a wee jig to get water in a vessel at a pretty constant 90C and adjust them all to that, then test them all multiple times to ensure the manual reset cuts in at 95C.
    So I've saved some money, but gave myself more work.
    West central Scotland
    4kw sse since 2014 and 6.6kw wsw / ene split since 2019
    24kwh leaf, 75Kwh Tesla and Lux 3600 with 60Kwh storage
  • QrizB
    QrizB Posts: 18,528 Forumite
    10,000 Posts Fourth Anniversary Photogenic Name Dropper
    I've been trying like a bear to find a double isolating high temperature replacement thermostat (x4) to run say 90C with a 95C manual reset, but the various stores I've visited and search terns I use have not came up with any usable solutions.
    Have you thought of switching from cheap, passive thermostats and moving to a more industrial approach using thermocouples?
    This sort of thing (not a specific recommendattion, just the first likely-looking example I could see):
    https://www.ebay.co.uk/itm/224040936181
    I've run lots of lab- and pilot-scale rigs and controllers like these are pretty foolproof. Depending on how your tank would respond to boiling, if you want belt-and-braces you can run two controllers in series; one set to the working temperature and a second as an overtemperature trip.
    N. Hampshire, he/him. Octopus Intelligent Go elec & Tracker gas / Vodafone BB / iD mobile. Ripple Kirk Hill member.
    2.72kWp PV facing SSW installed Jan 2012. 11 x 247w panels, 3.6kw inverter. 34 MWh generated, long-term average 2.6 Os.
    Not exactly back from my break, but dipping in and out of the forum.
    Ofgem cap table, Ofgem cap explainer. Economy 7 cap explainer. Gas vs E7 vs peak elec heating costs, Best kettle!
  • Solarchaser
    Solarchaser Posts: 1,758 Forumite
    Sixth Anniversary 1,000 Posts Name Dropper
    I haven't considered thermocouples as such,  I understand what you are saying about the accuracy,  the problem with thermocouples is their fragility.
    In another life I did a fair bit of work with autoclaves using thermocouples and spent alot of time repairing them. 

    Actually that has sparked an idea on how to calibrate the thermostats as to calibrate thermocouples you use a calibrated heatbath, so if I can get a hold of one (maybe from my old job) I can calibrate all of the thermostats to a high degree, so thanks 👍
    West central Scotland
    4kw sse since 2014 and 6.6kw wsw / ene split since 2019
    24kwh leaf, 75Kwh Tesla and Lux 3600 with 60Kwh storage
  • michaels
    michaels Posts: 29,133 Forumite
    Part of the Furniture 10,000 Posts Photogenic Name Dropper
    You do have the pockets for a boiler thermostat so could you put one in there and compare it against the immersion thermal cut out to calibrate?

    The more I read this thread the more I think we should get a second hot water tank in the loft in series to our existing 180l so that we could run all our daily hot water off the 5 hour 4.5p window.  Should pay for itself in about 12 months by my calcs assuming we don't overload the max current on the 10A main fuse.
    I think....
  • Solarchaser
    Solarchaser Posts: 1,758 Forumite
    Sixth Anniversary 1,000 Posts Name Dropper
    Unfortunately not due to the distance between the stat pockets and the immersion, there is about 5.5C difference between top and bottom centres but immersion are out at the sides, so can't really be sure what temperature they are seeing. 
    For your super high hot water usage, id certainly agree that on the face of it, another tank would be useful for cheap rate and solar consumption in the brighter months
    West central Scotland
    4kw sse since 2014 and 6.6kw wsw / ene split since 2019
    24kwh leaf, 75Kwh Tesla and Lux 3600 with 60Kwh storage
  • Solarchaser
    Solarchaser Posts: 1,758 Forumite
    Sixth Anniversary 1,000 Posts Name Dropper
    edited 21 August 2022 at 8:33PM
    I crawled back under today to see the difference my modifications of a week or two ago have made, now that the tank is back up to 70C, specifically the destrat pump was always hot, and the hot water from the big tank was to some degree flowing to the smaller tank. Both of these increasing heat loss.
    I had added in two single check valves, 1 for the 500l tank to pump and one from 300l tank to pump, so I expected to find the destrat pump stone cold.
    I was disappointed. 


    This is the secondary returns which I'm using as the feed for the destrat 

    This is with 19mm insulation on the 22mm pipe, so there shouldn't be much heat escaping.
    The yellow circle is the 1 way valve /check valve and you can see both sides are hot, so it's doing sweet FA.
    The one from the 300l tank is doing well though, you can see the far left is all cold.

    So how much heat is going through the pump?

    Not sure how clear that is, but its 59.9C on the pump body, which is pretty disappointing. 
    So I'll need to empty the tank again and fit a double check valve and hope it can stand up to the thermosyphon.

    If you are thinking that tank seems to be leeching quite a lot of heat, I agree. Again 1 way valve circled yellow, just for perspective, this is the immersion heater which I've been using most, leeching quite a bit of heat too.


    What about the other end of the tank?


    So you can see where the tank end caps dome out, the manufacturers insulation is bloody poor.

    Just thinking it might help understanding of how the system works if i drew some arrows on flir pics I took today

    Red line is coming up from top of destrat pump and running along from right to left between the tanks to go to what would normally be the hot outlet. This water never leaves the tanks.

    The other arrows are tap water, first blue is cold water coming into the 300l tank, this preheats the water in its solar coil (if the tank is warm) and so leaves the solar coil as the light green line and goes into the 500l tank, then comes out as thr orange line, which is hot water after going through that tanks interal coil and comes into the house where it meets a mixer valve, the cold patch on the orange line is just a bit of undrr floor insulation that's hanging down.
    I was surprised to see that even as 57mm pipe where only the middle 15mm is hot, still I'm getting some heat coming off the hot water pipe, but what more can I do?
    I'll probably wrap some loft insulation round it, or some pipe wrap, a little of which you see after the motorised valve in the next pic.

    This picture is just to the left of the previous one, so orange line still represents the pipe coming from the destrat to the top of the hot inlet on both 300 and 500l tanks.
    Black circle is the motorised zone valve on the top of the 300L tank which, although obviously getting hot itself, seems to stop most of the heat from the 500l entering the 300l when I don't want it to.

    The background pieces are the central heating pump and the magnetic filter return into the central heating coil, and although the circuit has been drained of fluid, ready for me adding in check valves and loops, you can still see the effect of being bolted onto the top of the coil with the magnetic filter at 47C.

    This pic also shows both how little heat is reaching the 300L tank, and how much is pouring out of the top of the 500L .. disappointing!!

    Hope that helps with understanding it, and apologies for the pic heavy post.

    West central Scotland
    4kw sse since 2014 and 6.6kw wsw / ene split since 2019
    24kwh leaf, 75Kwh Tesla and Lux 3600 with 60Kwh storage
  • michaels
    michaels Posts: 29,133 Forumite
    Part of the Furniture 10,000 Posts Photogenic Name Dropper
    Interesting seeing the heat l0ss at different point, I wonder if we have similar around our immersions, were yours on when you saw this loss or was it loss from the hot water in the tank only?

    Interesting that you actively destrat.  In our last property where we ran a tank on its side as a heat store (direct to gas boiler with pumped circuit to plate heat exchanger for hot water we wanted to keep the top layer (where the draw off for the hot water was as hot as possible even when the rest of the tank cooled so the circuits were deliberately set up to minimise mixing and I seem to remember we had two themostatic valves set up so the boiler and rad circuits could draw a mix from the top and bottom of the tank to max efficiency.

    Wish I could remember the exact configuration.
    I think....
  • Solarchaser
    Solarchaser Posts: 1,758 Forumite
    Sixth Anniversary 1,000 Posts Name Dropper
    The immersion had not long switched off on the side with the pump, the other side hasn't been on for weeks, it's tripped the manual reset cutout, I'll reset it at some point.

    The destrat, I really don't know if it will be needed, but figured it was better to design one in and find it's not needed than not have one and find I needed it.... though right now, I wish I hadn't as its that pump that's wasting lots of heat just now.

    I have a double delay circuit linked to the destrat (or will do when the myenergi Eddi finally finally gets here) so that when the central heating is run for more than 10 mins, the detrat kicks in, just grabbing some water from the middle of the tank and pushing it to the top, but more importantly creating a flow from right to left outside the tank to create left to right inside, at 10 mins the pump kicks in, runs for 5 then kicks off again, resetting.

    However as normal solar heating goes it could heat only one side of the tank, and so the Eddi will have a direct line to the destrat to run as a destrat to allow it to heat the whole tank.

    That's the theory anyway.
    West central Scotland
    4kw sse since 2014 and 6.6kw wsw / ene split since 2019
    24kwh leaf, 75Kwh Tesla and Lux 3600 with 60Kwh storage
  • Heedtheadvice
    Heedtheadvice Posts: 2,776 Forumite
    Part of the Furniture 1,000 Posts Name Dropper
    Mainly been lurking on your thread but impressed with your work.

    On the question of temp control I am surprised that you are not keen on thermocouples from your experience. Certainly not mine and they are also used in many an application from monitoring to control systems requiring robustness. Take gas fired boilers as an example.

    I'm sure you appreciate the advantages of response speed, accuracy, repeatability etc. Those along with associated electronics make for better control without the huge variation in switching temp and the wide hysteresis. Obviously some of the latter is essential to prevent 'chatter' but the amount is far more controllable.

    Could be advantageous for you with the tight control spec you desire?
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 351.3K Banking & Borrowing
  • 253.2K Reduce Debt & Boost Income
  • 453.7K Spending & Discounts
  • 244.2K Work, Benefits & Business
  • 599.4K Mortgages, Homes & Bills
  • 177.1K Life & Family
  • 257.7K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16.2K Discuss & Feedback
  • 37.6K Read-Only Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.