    Hi just a thought you have changed an inverter lately is it set to g83 in the settings, i had similar grid over voltage when my system was installed the installer assumed that the inverter was set for the UK but came set to be German settings, got them to come and then reset it to g83.
  • JKenH
    JKenH Posts: 5,138 Forumite
    Seventh Anniversary 1,000 Posts Name Dropper
    The inverter has been in 3 years 8 months. Two identical ones were fitted, one for each roof but so far I have only had the West roof switch off. It may be they are set to different thresholds but I haven’t had a look. I mentioned to the NPG engineer about adjusting the settings on the inverter but he suggested I wait and see what the investigation turns up. He mentioned they might fit a recording monitor to the transformer.
    Northern Lincolnshire. 7.8 kWp system, (4.2 kw west facing panels , 3.6 kw east facing), Solis inverters, Solar IBoost water heater, Mitsubishi SRK35ZS-S and SRK20ZS-S Wall Mounted Inverter Heat Pumps, ex Nissan Leaf owner)
  • 1961Nick
    1961Nick Posts: 2,107 Forumite
    Tenth Anniversary 1,000 Posts Name Dropper
    "Only 251.8v" is too close the the threshold of 253v & it's more than likely that your inverter is doing it's job & shutting down correctly. As mentioned before, they will move your supply to another tap on the transformer which is an easy job.
    4kWp (black/black) - Sofar Inverter - SSE(141°) - 30° pitch - North Lincs
    Installed June 2013 - PVGIS = 3400
    Sofar ME3000SP Inverter & 5 x Pylontech US2000B Plus & 3 x US2000C Batteries - 19.2kWh
  • JKenH
    JKenH Posts: 5,138 Forumite
    Seventh Anniversary 1,000 Posts Name Dropper
    Todays output, voltage and combined plots. I had quite a long outage this afternoon. Maximum voltage was 259.8v
    Northern Lincolnshire. 7.8 kWp system, (4.2 kw west facing panels , 3.6 kw east facing), Solis inverters, Solar IBoost water heater, Mitsubishi SRK35ZS-S and SRK20ZS-S Wall Mounted Inverter Heat Pumps, ex Nissan Leaf owner)
  • JKenH
    JKenH Posts: 5,138 Forumite
    Seventh Anniversary 1,000 Posts Name Dropper
    gefnew said:
    Hi just a thought you have changed an inverter lately is it set to g83 in the settings, i had similar grid over voltage when my system was installed the installer assumed that the inverter was set for the UK but came set to be German settings, got them to come and then reset it to g83.

    It looks as though it is set to G83.
    Northern Lincolnshire. 7.8 kWp system, (4.2 kw west facing panels , 3.6 kw east facing), Solis inverters, Solar IBoost water heater, Mitsubishi SRK35ZS-S and SRK20ZS-S Wall Mounted Inverter Heat Pumps, ex Nissan Leaf owner)
  • 1961Nick
    1961Nick Posts: 2,107 Forumite
    Tenth Anniversary 1,000 Posts Name Dropper
    Are both inverters showing a similar plot on the ac voltage Ken?
    4kWp (black/black) - Sofar Inverter - SSE(141°) - 30° pitch - North Lincs
    Installed June 2013 - PVGIS = 3400
    Sofar ME3000SP Inverter & 5 x Pylontech US2000B Plus & 3 x US2000C Batteries - 19.2kWh
  • JKenH
    JKenH Posts: 5,138 Forumite
    Seventh Anniversary 1,000 Posts Name Dropper
    edited 10 June 2022 at 7:11PM
    1961Nick said:
    Are both inverters showing a similar plot on the ac voltage Ken?
    These are the two plots. 1 West roof and 2 East roof.




    Power output for East roof. Only one outage.

    Northern Lincolnshire. 7.8 kWp system, (4.2 kw west facing panels , 3.6 kw east facing), Solis inverters, Solar IBoost water heater, Mitsubishi SRK35ZS-S and SRK20ZS-S Wall Mounted Inverter Heat Pumps, ex Nissan Leaf owner)
  • 1961Nick
    1961Nick Posts: 2,107 Forumite
    Tenth Anniversary 1,000 Posts Name Dropper
    Similar plots which confirms that the problem is more than likely to be the supply. Other than being 15v too high, the shape of the graph is what you would expect. 252v at sunrise eliminates solar as the cause.

    Our mains voltage has been between 232v & 242v today (242v at sunrise).
    4kWp (black/black) - Sofar Inverter - SSE(141°) - 30° pitch - North Lincs
    Installed June 2013 - PVGIS = 3400
    Sofar ME3000SP Inverter & 5 x Pylontech US2000B Plus & 3 x US2000C Batteries - 19.2kWh
  • JKenH
    JKenH Posts: 5,138 Forumite
    Seventh Anniversary 1,000 Posts Name Dropper
    I forgot that my plug in energy meter shows voltage. It is quite variable and goes up and down with the sun but the house voltage is around 3v lower than what I am seeing at the inverters.
    Northern Lincolnshire. 7.8 kWp system, (4.2 kw west facing panels , 3.6 kw east facing), Solis inverters, Solar IBoost water heater, Mitsubishi SRK35ZS-S and SRK20ZS-S Wall Mounted Inverter Heat Pumps, ex Nissan Leaf owner)
  • 1961Nick
    1961Nick Posts: 2,107 Forumite
    Tenth Anniversary 1,000 Posts Name Dropper
    JKenH said:
    I forgot that my plug in energy meter shows voltage. It is quite variable and goes up and down with the sun but the house voltage is around 3v lower than what I am seeing at the inverters.
    That still puts the peak over 253v.

    However, plug in energy monitors are typically accurate to +/- 3% & many of them only have a range upto 250v. 
    4kWp (black/black) - Sofar Inverter - SSE(141°) - 30° pitch - North Lincs
    Installed June 2013 - PVGIS = 3400
    Sofar ME3000SP Inverter & 5 x Pylontech US2000B Plus & 3 x US2000C Batteries - 19.2kWh
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 351.1K Banking & Borrowing
  • 253.2K Reduce Debt & Boost Income
  • 453.6K Spending & Discounts
  • 244.1K Work, Benefits & Business
  • 599.1K Mortgages, Homes & Bills
  • 177K Life & Family
  • 257.4K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16.1K Discuss & Feedback
  • 37.6K Read-Only Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.