  • QrizB
    QrizB Posts: 16,496 Forumite
    10,000 Posts Fourth Anniversary Photogenic Name Dropper
    QrizB said:
    Presumably the rating of a HP system in kW is not the power that it requires from the grid but an indication of its output based on a nominal COP?
    Yes, the heat pump rating is the nominal output power.

    Is it a nominal COP used for every similar system, or a more complex formula perhaps based on testing by the manufacturer, akin to a miles-per-gallon figure for cars?
    Reputable manufacturers publish good data on their heat pumps, including COPs at varying internal and external temperatures.
    That particular heat pump claims a SCOP of 3.47 when producing water at 55C, and 4.79 when producing water at 35C.
    I would expect there to be more data available on Mitsubishi's websites if you waqnt to go looking.
    N. Hampshire, he/him. Octopus Intelligent Go elec & Tracker gas / Vodafone BB / iD mobile. Ripple Kirk Hill member.
    2.72kWp PV facing SSW installed Jan 2012. 11 x 247w panels, 3.6kw inverter. 33MWh generated, long-term average 2.6 Os.
    Not exactly back from my break, but dipping in and out of the forum.
    Ofgem cap table, Ofgem cap explainer. Economy 7 cap explainer. Gas vs E7 vs peak elec heating costs, Best kettle!
  • coffeehound
    coffeehound Posts: 5,741 Forumite
    Tenth Anniversary 1,000 Posts Photogenic Name Dropper
    Presumably the rating of a HP system in kW is not the power that it requires from the grid but an indication of its output based on a nominal COP?
    My heat pump is specified to perform down to -15 C.  At that temperature I suspect its actual CoP will be close to 1.  Presumably it will then be using something close to its rated output in electrical power.  But most of the time the power requirement will be much less.

    Edit.  It has a dedicated circuit with a 40 A fuse 
    I would guess that would work the other way around and that the output power of the HP would trail off as OAT falls.  At the end of the day, the HP is an electric pump and fans which work at a given input power.  If it starts powering up the resistive heater and immersion, then that is an additional load.  
  • QrizB
    QrizB Posts: 16,496 Forumite
    10,000 Posts Fourth Anniversary Photogenic Name Dropper
    If you're feeling really nerdy, here is the data book for a slightly different model of Mitsubishi heat pump.
    See section 5.2 under "Performance data" for heating performance.

    N. Hampshire, he/him. Octopus Intelligent Go elec & Tracker gas / Vodafone BB / iD mobile. Ripple Kirk Hill member.
    2.72kWp PV facing SSW installed Jan 2012. 11 x 247w panels, 3.6kw inverter. 33MWh generated, long-term average 2.6 Os.
    Not exactly back from my break, but dipping in and out of the forum.
    Ofgem cap table, Ofgem cap explainer. Economy 7 cap explainer. Gas vs E7 vs peak elec heating costs, Best kettle!
  • coffeehound
    coffeehound Posts: 5,741 Forumite
    Tenth Anniversary 1,000 Posts Photogenic Name Dropper
    QrizB said:
    QrizB said:
    Presumably the rating of a HP system in kW is not the power that it requires from the grid but an indication of its output based on a nominal COP?
    Yes, the heat pump rating is the nominal output power.

    Is it a nominal COP used for every similar system, or a more complex formula perhaps based on testing by the manufacturer, akin to a miles-per-gallon figure for cars?
    Reputable manufacturers publish good data on their heat pumps, including COPs at varying internal and external temperatures.
    That particular heat pump claims a SCOP of 3.47 when producing water at 55C, and 4.79 when producing water at 35C.
    I would expect there to be more data available on Mitsubishi's websites if you waqnt to go looking.

    Thanks so they seem to have quoted the nominal COP as that obtained for delivering water at 45 C between -10 to +20 OAT.   So is that the basic criterion for the headline power output?  And the steady-state consumption is the 9.1 amps = about 2.1 kW.   
    They state that as 'MAX' so it shouldn't go much over that, apart from switch-on inrush current


  • QrizB
    QrizB Posts: 16,496 Forumite
    10,000 Posts Fourth Anniversary Photogenic Name Dropper
     And the steady-state consumption is the 9.1 amps = about 2.1 kW.   
    They state that as 'MAX' so it shouldn't go much over that, apart from switch-on inrush current
    I think the [MAX] in square brackets relates to the [22] also in square brackets, so max. current 22A.
    N. Hampshire, he/him. Octopus Intelligent Go elec & Tracker gas / Vodafone BB / iD mobile. Ripple Kirk Hill member.
    2.72kWp PV facing SSW installed Jan 2012. 11 x 247w panels, 3.6kw inverter. 33MWh generated, long-term average 2.6 Os.
    Not exactly back from my break, but dipping in and out of the forum.
    Ofgem cap table, Ofgem cap explainer. Economy 7 cap explainer. Gas vs E7 vs peak elec heating costs, Best kettle!
  • coffeehound
    coffeehound Posts: 5,741 Forumite
    Tenth Anniversary 1,000 Posts Photogenic Name Dropper
    QrizB said:
     And the steady-state consumption is the 9.1 amps = about 2.1 kW.   
    They state that as 'MAX' so it shouldn't go much over that, apart from switch-on inrush current
    I think the [MAX] in square brackets relates to the [22] also in square brackets, so max. current 22A.
    Ah okay. so perhaps that is the switch-on current
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 349.8K Banking & Borrowing
  • 252.6K Reduce Debt & Boost Income
  • 453K Spending & Discounts
  • 242.7K Work, Benefits & Business
  • 619.5K Mortgages, Homes & Bills
  • 176.3K Life & Family
  • 255.6K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16.1K Discuss & Feedback
  • 15.1K Coronavirus Support Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.