Electric shower sizing

neilmcl
Posts: 19,460 Forumite


I need to replace my electric shower which is currently on a dedicated 40A circuit. What's the max size shower can I safely install?
0
Comments
-
By 'size' do you mean electric power?40A*240V=9.6kW (at 240V). So, 9kW, possibly 9.5kW.ETA: if 9.5kW is measured at 230V (see specifications), then the current will be 41A at 230V and even higher at 240-250V. In this it's 9kW max. for you.0
-
You should be ok to install a 9.5KW shower on a 40A circuit. (The breaker shouldn't trip until the current is 13% above its rated value).
Try to find one that is made in the UK and rated for 240v. It is likely that the installation instructions will be online for any shower you are considering, so yo can also check to see if the manufacturer confirms that nothing higher than a 40A breaker is required.The comments I post are my personal opinion. While I try to check everything is correct before posting, I can and do make mistakes, so always try to check official information sources before relying on my posts.1 -
I currently have a 9.5kw Triton which gave up the ghost this morning I was surprised it was 9.5kw as most places I've seen only recommend 8.5kw for a 40A fused circuit but it's worked fine for me up until now.
Update: I've checked the installation guide for a replacement Triton T80Z and they do state that a 40A MCB will be ok for a 9.5kw, so I'm good to go.0 -
Its not quite so simple as kW / voltage = amps. This does give the correct answer provided the wire are short and not confined, but this is rarely realistic in a property, The cable may be long, because of the distance involved or because of routeing. It may be run through conduit which will reduce the rate at which it can lose heat.
The real answer needs to be calculated by an experienced electrician who can see the route and the size of cable in place, which also has a significant bearing.
Personally I'd see 9.5 kW as just a bit too much for a 40A MCB and stick to 8.5.0 -
nofoollikeold said:Its not quite so simple as kW / voltage = amps. This does give the correct answer provided the wire are short and not confined, but this is rarely realistic in a property, The cable may be long, because of the distance involved or because of routeing.
0 -
@neilmcl worth a quick look through this thread where we drilled down to the nitty-gritty. The table shows the scenarios where the cable needs to be downrated
https://forums.moneysavingexpert.com/discussion/6270614
(Crikey it's even harder to find anything on this site now)0
Confirm your email address to Create Threads and Reply

Categories
- All Categories
- 350.5K Banking & Borrowing
- 252.9K Reduce Debt & Boost Income
- 453.3K Spending & Discounts
- 243.5K Work, Benefits & Business
- 598.2K Mortgages, Homes & Bills
- 176.7K Life & Family
- 256.7K Travel & Transport
- 1.5M Hobbies & Leisure
- 16.1K Discuss & Feedback
- 37.6K Read-Only Boards