We’d like to remind Forumites to please avoid political debate on the Forum.
This is to keep it a safe and useful space for MoneySaving discussions. Threads that are – or become – political in nature may be removed in line with the Forum’s rules. Thank you for your understanding.
📨 Have you signed up to the Forum's new Email Digest yet? Get a selection of trending threads sent straight to your inbox daily, weekly or monthly!
Outdoor fuse/trip switch for car charger

benish
Posts: 51 Forumite


Morning folks,
Can any qualified sparkys tell me if this is safe!?

Can any qualified sparkys tell me if this is safe!?
I had a pod point car charger installed a week ago, I wasn’t in at the time so never had the chance to query the workman, but ever since I’ve wondered if the fuse switch/mcb shouldn’t be outside. I opened the cover up after a rain shower and water leaked in through the sides. I certainly wouldn’t want to open it during a shower!

0
Comments
-
Interesting! I'm not an electrician, so not qualified to comment, but a quick google suggests that the box is a Europa ECW series insulated distribution enclosure, which conforms to IP65. And that IP65 means: Water resistant. “Protected against water jets from any angle”0
-
Googling europa do an ip65 rated consumer box and it looks like the one in your picture but if in doubt call the installer for confirmation0
-
Ok. I guess if it’s IP rated it’s fine. Thanks for the comments.0
-
Although it may be the correct box surely it shouldn't be letting water in. It may simply be a case that the seal hasn't been seated properly but I would get the person back who did the installation to check it out.
0 -
Was it the act of opening the cover that let the rain in?0
-
External equipment needs to be adequately IP rated. That said, "consumer units and similar switchgear assemblies in domestic (household) premises" must be made from non-combustible material, or housed in a cabinet made from non-combustible material. Ferrous metal, e.g. steel, is given as an example of non-combustible material. So in my opinion it doesn't comply with BS 7671:2018 (2020) aka the IEE Wiring Regulations.
0 -
Risteard said:External equipment needs to be adequately IP rated. That said, "consumer units and similar switchgear assemblies in domestic (household) premises" must be made from non-combustible material, or housed in a cabinet made from non-combustible material. Ferrous metal, e.g. steel, is given as an example of non-combustible material. So in my opinion it doesn't comply with BS 7671:2018 (2020) aka the IEE Wiring Regulations.
If it sticks, force it.
If it breaks, well it wasn't working right anyway.0 -
Ectophile said:Risteard said:External equipment needs to be adequately IP rated. That said, "consumer units and similar switchgear assemblies in domestic (household) premises" must be made from non-combustible material, or housed in a cabinet made from non-combustible material. Ferrous metal, e.g. steel, is given as an example of non-combustible material. So in my opinion it doesn't comply with BS 7671:2018 (2020) aka the IEE Wiring Regulations.
Not true. They consider the external wall of a dwelling to be part of the dwelling. They simply suggested that a detached garage might not be considered to be. That has always been their position on it, so I am assuming that this is what the article you have linked to alludes to.
0
Confirm your email address to Create Threads and Reply

Categories
- All Categories
- 351.7K Banking & Borrowing
- 253.4K Reduce Debt & Boost Income
- 454K Spending & Discounts
- 244.7K Work, Benefits & Business
- 600.1K Mortgages, Homes & Bills
- 177.3K Life & Family
- 258.3K Travel & Transport
- 1.5M Hobbies & Leisure
- 16.2K Discuss & Feedback
- 37.6K Read-Only Boards