That seems very sensible @Meatballs . Can it be generalised?
8.5/2.5 = 3.4
So whatever CoP is achieved running "hard" for 2.5 hours; the CoP needs to be over 3.4 times better (when maintaining a constant temperature for 8.5 hours) in order to save money. I think that must be correct.Reed0 -
Meatballs said:Reed_Richards said:I use a nighttime set-back on my heating controller. For the sake of simplicity we'll say it is 21 C from 07:00 to 22:30 then 18 C overnight. If the outside temperature is near 0 C it takes about 6 hours for the temperature to cool from 21 to 18 so the heat pump is off all that time. That leaves 2.5 hour for my controller to get the temperature back up to 21 C in time for 07:00. It will do this automatically if I set "Comfort Mode". But to do this it has to make the water in my radiators hotter than is necessary to maintain a constant 21 C which means it will be running less efficiently.
Which is better for fuel economy, @shinytop's strategy of maintaining a constant internal temperature or mine? With a conventional boiler I should win but with a heat pump it's not so obvious. I'll have to try to read my heat pump meter after 22:30 and then (if I wake up in time) at 07:00 the following day to find out how much electricity that 2.5 hours of hard work uses.
vs
2.5 hours at your inefficient COP kWh
Almost certainly the 2.5 hours?
If it's a 10kWh heater running at COP1 for 2.5 hours = 25kWh
If it's running at COP 3 for 8.5 Hours - 3.333*8.5 = 28.33kWh
Unlikely you will be down to COP1?1 -
Reed_Richards said:The truth is what I actually do is more complicated than my simple explanation. I set back the room temperature by 3 C at 22:30 then up by 1 C in time for 07:00 and gradually up during the day until it arrives back at the base temperature (21 C) at 17:00. I've been doing something like that for the past 24 years, ever since I had a programmable room thermostat and with whatever boiler. It's what feels comfortable; I think because as the day progresses we get more sedentary and need it a bit warmer. So in terms of heat demand that's probably very similar to @shinytop 's red dot data.
That's a very interesting chart, @shinytop ; I'm still getting my head around the trend line. I suppose with a conventional boiler the power requirement would double from 11 C to 1 C ambient (because 2*(21-11) = 21-1 ) whereas with your heat pump arrangement it's nearer treble rather than double.
EDIT - exponential?
3 -
shinytop said:
I think the fact that it looks like a straight line and I've plotted one is misleading.Reed1 -
Reed_Richards said:shinytop said:
I think the fact that it looks like a straight line and I've plotted one is misleading.
0 -
That's very interesting, @shinytop. Is the model something you constructed yourself?
Your flow temperatures are much lower than mine, by about 10 C. My MCS certified figure is 50 C and my weather compensation only kicks-in above 4 C.Reed0 -
Reed_Richards said:That's very interesting, @shinytop. Is the model something you constructed yourself?
Your flow temperatures are much lower than mine, by about 10 C. My MCS certified figure is 50 C and my weather compensation only kicks-in above 4 C.
you had the data.
https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/dereks-heat-pump-modeling-tool#post-3793
In a way I'm lucky because my whole system/rads is designed to work at lower temps. In another way I'm not because I had to pay for it all.
But even it I changed from 40C to 50C flow, COP changes from 2.8 to about 2.4 at 0C so not that bad. The other point not covered is that these numbers are steady state. The COP will drop a lot when the ASHP is working very hard, which happens when you let external thermostats switch it on and off and it has to heat the water up from cold repeatedly.0 -
shinytop said:
The COP will drop a lot when the ASHP is working very hard, which happens when you let external thermostats switch it on and off and it has to heat the water up from cold repeatedly.
Edit: Well given that the compressor is off for a minute or two every 15 minutes it must be working a bit harder. But is the any more to it than that?Reed0 -
I think there is. I don't think it's going to be as efficient with a very high hysteresis. It depends how your ASHP works but I think it's the case with mine. Both graphs are midnight to 12 noon. The first graph is when it's <6C
The ASHP is off at night so the flow temp drops to about room temp. It kicks in at 5am and goes at high power to reach desired flow temp. It then settles down to a steady pace and keeps the flow temp very constant. On the LH scale, 20 = c. 1.2kW. I'm happy enough to pay for 1.2kW but wouldn't want to be paying for 4-5kW very much; once in the morning is offset by the zero consumption all night.
The second graph is from when it was warmer. Same time period, different day.
The initial blip is lower and shorter as expected. You can see it then trying to run steadily but it can't modulate down enough so cycles on and off. The flow temp only varies 2-3C. The average consumption during the cycling is about 0.7kW.
I don't really know the answer to your question but it would seem that raising the flow temp a lot uses a lot of power.
Are you sure your flow temp is dropping so much because the return temp is too high or is it because a thermostat stops calling for heat? It's the latter situation that I'm now avoiding.0 -
For me, and perhaps for anyone else considering an ASHP, the moral of this technical discussion with @shinytop is that ASHP heating controls are not very sophisticated. In particular they tend to lack a feature called 'Load Compensation' so they don't know how hard they should work to maintain a constant room temperature. Because of this they don't modulate to achieve the output flow temperature necessary to maintain the room temperature. I live with this, whilst @shinytop works around it by just using Weather Compensation to maintain a constant room temperature (24/7) without using a room thermostat.
By contrast, gas boilers generally can do Load Compensation (with the right controller) in fact I bought one in 1998 that had this feature.Reed2
Confirm your email address to Create Threads and Reply

Categories
- All Categories
- 351.1K Banking & Borrowing
- 253.2K Reduce Debt & Boost Income
- 453.7K Spending & Discounts
- 244.1K Work, Benefits & Business
- 599.2K Mortgages, Homes & Bills
- 177K Life & Family
- 257.5K Travel & Transport
- 1.5M Hobbies & Leisure
- 16.1K Discuss & Feedback
- 37.6K Read-Only Boards