We've just discovered our new home (small converted former school, 5 bedrooms, no high consumption habits) has managed to use 2,000L of LPG in 8 weeks.
Calor confirm it won't be a leak as it's tested on delivery, that leaves either the boilers (2x Viessemann Vitodens 100, one for hot water and one for heating) or the stove top (modern LPG conversion 5 ring).
There was nothing on the PIF when we purchased (completed Dec 2020) to suggest this level of consumption, and Calor are stumped.
We have a heating engineer booked, but my only suspicion at the moment is the temperature of the hot water is incredibly high, near 80-90c. This also runs 24/7..
Any other suggestions to get this nailed?
Calor confirm it won't be a leak as it's tested on delivery, that leaves either the boilers (2x Viessemann Vitodens 100, one for hot water and one for heating) or the stove top (modern LPG conversion 5 ring).
There was nothing on the PIF when we purchased (completed Dec 2020) to suggest this level of consumption, and Calor are stumped.
We have a heating engineer booked, but my only suspicion at the moment is the temperature of the hot water is incredibly high, near 80-90c. This also runs 24/7..
Any other suggestions to get this nailed?
0
Comments
-
20,000LAssuming that the 'standard' domestic tank is 2100L (?) that's a refill every week - really?0
-
2000 litre = 14,000 kWh of energy in 8 weeks. What does the EPC estimate for annual heating/hot water use?
Two boilers is pretty unusual in one dwelling. What exact ratings are the two - they come with 5 outputs 13, 16, 19, 26 & 35 kW from a quick looks see of the makers website. They are also 'heat only' aka 'system boilers' so not combi for the water, I think?
Therefore turn the HW boiler's stat down. 60C max is needed if hot water stored in a tank for Legionella reasons. The tank thermostat may have stuck in 'on demand' position? Stored water heat loss is proportional to the temperature difference so that is a concern. It's also a scalding risk, even if thermostatic mixer valves are on the bath and showers, other taps probably don't have them?
The HW will only need to be on once or twice a day for a few hours to reheat water used, depending on your water use. That'll save a bit immediately
Heating boiler. What does it supply? Radiators, underfloor heating manifolds? What temp is the CH boiler circulating water set to?0
Confirm your email address to Create Threads and Reply

Categories
- All Categories
- 351K Banking & Borrowing
- 253.1K Reduce Debt & Boost Income
- 453.6K Spending & Discounts
- 244K Work, Benefits & Business
- 599K Mortgages, Homes & Bills
- 177K Life & Family
- 257.4K Travel & Transport
- 1.5M Hobbies & Leisure
- 16.1K Discuss & Feedback
- 37.6K Read-Only Boards