Boiler Pressure Questions... too low then too high!

ma9gm
ma9gm Posts: 88 Forumite
Fourth Anniversary 10 Posts Combo Breaker
Hi,
I was hoping someone would be able to help me understand what might be going on with my boiler. I have a baxi combi boiler duo tec 40 he. It's about 10 years old. When the boiler is off, the pressure sits at just below 1 bar, however, when the boiler is on the pressure goes up to just under 4. If I lower the pressure anymore the boiler won't start because it tells me the pressure is too low. But 4 seems way too high. I'm just a bit confused by it. Anyone got any idea what might be going on? Thanks in advance.
«1

Comments

  • Usually the pressure should be about 1 bar cold, and will increase to about 1.5 or 2 bar when it's hot.  If it's getting to high when it's hot, this might point to a problem with the expansion vessel or the pressure relief valve.  Probably worth getting it looked at by a heating engineer.
  • ma9gm
    ma9gm Posts: 88 Forumite
    Fourth Anniversary 10 Posts Combo Breaker
    That's really helpful. So looks like there could be an issue with the expansion vessel. I'll get someone to have a look at. Thank you
  • JohnB47
    JohnB47 Posts: 2,660 Forumite
    Part of the Furniture 1,000 Posts Name Dropper
    edited 27 November 2020 at 12:04PM
    Yes, it does sound like the expansion vessel needs repressurised. I did mine myself, on my old boiler, using a pressure guage and a bicycle pump. If your pressure has gone up to about 4 bar, it's possible that the pressure release valve (PRV) has also activated. This allows the system to vent some of the pressure and as a result, some water, usually through a copper pipe fed through the wall at the back of the boiler. If you can find that pipe and you see a drip, or signs that it has dripped, then the PRV will need to be changed too. Even though it reseats when the pressure drops, the stuff it vents is usually dirty and stops the seal closing properly, so it can drip constantly from then on. A plumber will know to check this.
  • ma9gm
    ma9gm Posts: 88 Forumite
    Fourth Anniversary 10 Posts Combo Breaker
    Oh, that's interesting. I didn't know I could re-pressurise. Is that something I can simply google? The cooper pipe looks dry and doesn't look like it's dripping, but I can keep an eye on it.
  • ma9gm
    ma9gm Posts: 88 Forumite
    Fourth Anniversary 10 Posts Combo Breaker
    Actually, I found a video that shows what needs to be done. It doesn't look too complicated.
  • ma9gm
    ma9gm Posts: 88 Forumite
    Fourth Anniversary 10 Posts Combo Breaker
    Would the big swing in pressure suggest the pressure has been lost in the vessel, or that the pressure is too much in there?
  • JohnB47
    JohnB47 Posts: 2,660 Forumite
    Part of the Furniture 1,000 Posts Name Dropper
    edited 27 November 2020 at 4:01PM
    I am not a plumber but I'm pretty certain that the symptoms you describe are due to the loss of (air) pressure in the vessel. Alternatively, the rubber diaphragm separating central heating water and the pressurised air could be punctured. Either way, the vessel is likely full or almost full of central heating water and hence there's no air there to absorb the extra pressure when the system is running.
    You've been lucky if your PRV hasn't activated.
  • ma9gm
    ma9gm Posts: 88 Forumite
    Fourth Anniversary 10 Posts Combo Breaker
    Did it and that seemed to have fixed the issue. When the boilers off it sits half way between 1&2 bars. Then now when it's on, it sits just above 2 bars. Thank you so much for your help.
  • Rodders53
    Rodders53 Posts: 2,583 Forumite
    Part of the Furniture 1,000 Posts Name Dropper Photogenic
    ma9gm said:
    Did it and that seemed to have fixed the issue. When the boilers off it sits half way between 1&2 bars. Then now when it's on, it sits just above 2 bars. Thank you so much for your help.
    That's possibly a tad high?  Consider reducing to 1 bar cold rather than 1.5 bar to keep the hot under 2 bars? 
    https://www.baxi.co.uk/our-boilers/combi-boilers/baxi-duo-tec-combi from the Installation manual:
    Central Heating Primary Circuit Pressures
     
    Safety Discharge 3 bar 
    Max Operating 2.5 bar 
    Min Operating 0.5 bar 
    Recommended Operating Range 1-2 bar 

    The pressure vessel should be pre-charged to a minimum of 0.5 bar as that is the pressure Baxi provide them set to when new.  Although up to 1 bar is not an uncommon pre-charge figure.
  • ma9gm
    ma9gm Posts: 88 Forumite
    Fourth Anniversary 10 Posts Combo Breaker
    Rodders53 said:
    ma9gm said:
    Did it and that seemed to have fixed the issue. When the boilers off it sits half way between 1&2 bars. Then now when it's on, it sits just above 2 bars. Thank you so much for your help.
    That's possibly a tad high?  Consider reducing to 1 bar cold rather than 1.5 bar to keep the hot under 2 bars? 
    https://www.baxi.co.uk/our-boilers/combi-boilers/baxi-duo-tec-combi from the Installation manual:
    Central Heating Primary Circuit Pressures
     
    Safety Discharge 3 bar 
    Max Operating 2.5 bar 
    Min Operating 0.5 bar 
    Recommended Operating Range 1-2 bar 

    The pressure vessel should be pre-charged to a minimum of 0.5 bar as that is the pressure Baxi provide them set to when new.  Although up to 1 bar is not an uncommon pre-charge figure.
    Oh ok. I'll drop the water pressure a bit then. Get it down closer to 1.
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 349.7K Banking & Borrowing
  • 252.6K Reduce Debt & Boost Income
  • 452.9K Spending & Discounts
  • 242.6K Work, Benefits & Business
  • 619.4K Mortgages, Homes & Bills
  • 176.3K Life & Family
  • 255.5K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16.1K Discuss & Feedback
  • 15.1K Coronavirus Support Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.