Can I run an oven and induction hob off a 32A supply

Options
I’ve got my 3.5kw oven connected to a 32A mcb and want to add a 7,5kw induction hob onto this. Would it be safe.
«13

Comments

  • pinkshoes
    pinkshoes Posts: 20,557 Forumite
    Part of the Furniture 10,000 Posts Name Dropper Photogenic
    proterra wrote: »
    I’ve got my 3.5kw oven connected to a 32A mcb and want to add a 7,5kw induction hob onto this. Would it be safe.

    No.

    If you run them at the same time you would draw more than 32A, so the induction hob would need its own ring-main.

    We did this last summer and had to have our entire (ancient) consumer unit changed to have another “loop” added in!!
    Should've = Should HAVE (not 'of')
    Would've = Would HAVE (not 'of')

    No, I am not perfect, but yes I do judge people on their use of basic English language. If you didn't know the above, then learn it! (If English is your second language, then you are forgiven!)
  • pinkshoes wrote: »
    No.

    If you run them at the same time you would draw more than 32A, so the induction hob would need its own ring-main.

    We did this last summer and had to have our entire (ancient) consumer unit changed to have another “loop” added in!!

    The hob may draw more than that on its own.
  • FreeBear
    FreeBear Posts: 18,245 Forumite
    Tenth Anniversary 10,000 Posts Name Dropper Photogenic
    proterra wrote: »
    I’ve got my 3.5kw oven connected to a 32A mcb and want to add a 7,5kw induction hob onto this. Would it be safe.

    Depends.
    What size is the cable from consumer unit to isolator switch ?
    How long is this cable ?
    Is the cable buried in an insulated wall or clipped in free air ?

    Best to get a qualified electrician to have a look, do the calculations, and advise accordingly.
    Her courage will change the world.

    Treasure the moments that you have. Savour them for as long as you can for they will never come back again.
  • Risteard
    Risteard Posts: 2,000 Forumite
    Part of the Furniture 1,000 Posts Name Dropper
    pinkshoes wrote: »
    No.

    If you run them at the same time you would draw more than 32A, so the induction hob would need its own ring-main.

    We did this last summer and had to have our entire (ancient) consumer unit changed to have another “loop” added in!!

    Nonsense...
  • ianto11
    ianto11 Posts: 251 Forumite
    100 Posts Second Anniversary Name Dropper
    edited 19 January 2020 at 2:45PM
    Risteard wrote: »
    Nonsense...

    Why....?
    With the potential for max 11Kw's, that's over 45A ? Admittedly the MCB will be undersized rather than oversized, but could cause nuisance tripping of the MCB from overloading ?
  • Probably safe in a domestic setting.

    (a) there is the principle of diversity which assumes that not all rings on the hob will be on max at the same time. They will cycle on/off according to head required, as will the oven.
    (b) a lot of induction hobs have an installer setting to limit the maximum demand
    A kind word lasts a minute, a skelped erse is sair for a day.
  • FreeBear
    FreeBear Posts: 18,245 Forumite
    Tenth Anniversary 10,000 Posts Name Dropper Photogenic
    ianto11 wrote: »
    Why....?
    With the potential for max 11Kw's, that's over 45A ? Admittedly the MCB will be undersized rather than oversized, but could cause nuisance tripping of the MCB from overloading ?

    A type B mcb (most common in domestic consumer units) will not trip immediately until an overload of 3-5 times the rated current is detected. Below this, you can quite easily draw quite a bit of current for an extended period of time.

    With a 32A mcb, you could quite easily draw 48A for a minute or more before it trips.
    Her courage will change the world.

    Treasure the moments that you have. Savour them for as long as you can for they will never come back again.
  • Risteard wrote: »
    Nonsense...

    As you have previously deemed yourself to be:
    probably the most helpful user on this forum.
    https://forums.moneysavingexpert.com/showpost.php?p=75418167&postcount=11

    then rather than posting a single word response, why not actually take the time to explain why you consider it to be nonsense? because what you have posted above isn't exactly helpful to anyone.
  • neilmcl
    neilmcl Posts: 19,460 Forumite
    Part of the Furniture 10,000 Posts Name Dropper
    Risteard wrote: »
    Nonsense...
    If you going to make posts like this then at the very least back it up with the reasons why, otherwise it's just plain rude!
  • knightstyle
    knightstyle Posts: 7,227 Forumite
    Part of the Furniture 1,000 Posts Name Dropper
    I was amazed by FreeBear's comment and looking at the graphs for type B MCBs I see that it can sustain 1.5 times the rated current for 10 minutes before tripping! So 48amps for 10 minutes!
This discussion has been closed.
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 351K Banking & Borrowing
  • 253.1K Reduce Debt & Boost Income
  • 453.6K Spending & Discounts
  • 244K Work, Benefits & Business
  • 599K Mortgages, Homes & Bills
  • 176.9K Life & Family
  • 257.4K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16.1K Discuss & Feedback
  • 37.6K Read-Only Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.