humming noise when lights are on

Options
Had some downlights fitted recently but when there switched on there is a humming noise coming from the light switch & also the consumer (spelling) box, is it anything to worry about if it is what to do about it. Cannot contact electrician who fitted them he on holiday at mo.
if i had known then what i know now
«1

Comments

  • real1314
    real1314 Posts: 4,432 Forumite
    is it a dimmer switch? how many downlights and what rating are they?

    could be an overloaded switch, but downlights do tend to cause some humming.
  • oysterman
    oysterman Posts: 749 Forumite
    Part of the Furniture 100 Posts
    real1314 wrote: »
    is it a dimmer switch? how many downlights and what rating are they?

    could be an overloaded switch, but downlights do tend to cause some humming.

    Yes it is a dimmer switch(double) 12 total, 4 off one & 8 off the other not sure of the rating thou
    if i had known then what i know now
  • fazer_2
    fazer_2 Posts: 20 Forumite
    Relax, got a dimmer switch in the kid's bedroom which hums, can only hear it if it's super quiet in house or got my ear next to switch.
  • rsvtoddy
    rsvtoddy Posts: 244 Forumite
    Part of the Furniture 100 Posts
    Suspect you've got too many on the dimmer - I was looking for one to do 7 50watt GU10 bulbs (350 watts total) and couldn't find one with enough wattage taking into account de-rating.

    If you've got 12 bulbs (50W?) they'll fry the dimmer fairly soon! I hope your sparkie was suitably qualified/competent and gave you certification?!
  • It's your dimmer switch, you'll maybe notice that the humming noise goes away when you turn the dimmer to the max setting ie: lights fully on.
    Perfectly normal for these components, it's how it reduces the power to the light basically chopping up the voltage input.
  • maypole
    maypole Posts: 1,816 Forumite
    Part of the Furniture 1,000 Posts Combo Breaker
    I get a humming/buzzing noise from a lamp with a low energy light bulb from Ikea, really gets on my nerves :mad:
  • Dormouse
    Dormouse Posts: 5,617 Forumite
    Part of the Furniture 1,000 Posts Combo Breaker
    maypole wrote: »
    I get a humming/buzzing noise from a lamp with a low energy light bulb from Ikea, really gets on my nerves :mad:
    Yeah, I've got a lamp with a low energy bulb from Tesco and it buzzes too, pretty annoying. :rolleyes:
  • real1314
    real1314 Posts: 4,432 Forumite
    I've got 6 x 50 watt downlights in one room - had to use a double dimmer to get within the load for each of the switches, and also to allow reduced consumption.


    I think most dimmers stipulate that you should treat halogen downlights as being double their value for loading purposes, some might say 50% extra allowance.

    8 x 50 watts = 400watts, x 1.5 to 2 = 600 to 800 watts on a single dimmer = v expensive switch? or overloaded switch?

    and just another point - lighting circuits are normally 6 amp, which gives a maximum load of about 1500 watts. Your lights in that room alone amount to 600 watts; might be worth checking if you've got separate circuits for upstairs/downstairs, and checking the load on the circuit.
  • jaxxy00
    jaxxy00 Posts: 1,010 Forumite
    model500 wrote: »
    It's your dimmer switch, you'll maybe notice that the humming noise goes away when you turn the dimmer to the max setting ie: lights fully on.
    Perfectly normal for these components, it's how it reduces the power to the light basically chopping up the voltage input.

    This happens to ours and when turned up to full you cant hear it. Saying that though i cant hear it that much anyway as a bit luggy :D
  • There is a noise supressor in the dimmer (it is there to help prevent TV and radio interference- the kind you used to get when you turned a flourescant light on and yor AM radio crackled)


    Dimmers should be suitably rated.
    Some dimmers require de-rating (400w dimmer = 200w halogen)
    Some don't require derating example below:
    http://www.aurora-lighting.com/srspe.aspx?txtSearchTerm=dimmer&cmbSearchScope=Dimmers%20and%20Switches

    Shop about (not B&Q / Homebase) ; use local electrical wholesalers.
    baldly going on...
This discussion has been closed.
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 350.8K Banking & Borrowing
  • 253.1K Reduce Debt & Boost Income
  • 453.5K Spending & Discounts
  • 243.8K Work, Benefits & Business
  • 598.7K Mortgages, Homes & Bills
  • 176.8K Life & Family
  • 257.1K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16.1K Discuss & Feedback
  • 37.6K Read-Only Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.