No temperture setting for hot water

Mgreen
Mgreen Posts: 8 Forumite
Vaillant Eco tech
Heatre sadia mega flo
Honeywell timerST6400c


I tried to read the manufactures instructions but still don't understand why the temp is 60 . Why doesn't hot water dial do anything.

I wanted to know if my!!hot water was wasting!!because i set it to come on too often. There are four people living in the house . My question was relating to if I was turning the timer on too often for hot water . I want Just enough hot water for the day . to do normal things shower dishes etc.

Comments

  • HappyMJ
    HappyMJ Posts: 21,115 Forumite
    10,000 Posts Combo Breaker
    You could set it to be on 24 hours a day. It will cost a little more but it won't cost that much more than timing it and potentially running out of hot water if each of the four people in your house decided to have a bath after one another and the hot water was not set to reheat immediately.
    :footie:
    :p Regular savers earn 6% interest (HSBC, First Direct, M&S) :p Loans cost 2.9% per year (Nationwide) = FREE money. :p
  • Mgreen
    Mgreen Posts: 8 Forumite
    The temp goes above 60 when the boiler fire up

    The dial on vaillant Eco tec is on 50
  • HappyMJ
    HappyMJ Posts: 21,115 Forumite
    10,000 Posts Combo Breaker
    Mgreen wrote: »
    The temp goes above 60 when the boiler fire up

    The dial on vaillant Eco tec is on 50
    The temp where? The boiler will heat water to well over 60 degrees then pumps the very hot water around your cylinder transferring heat from the very hot water to your cooler cylinder water until the water in your cylinder reaches 50 and the thermostat stops calling for heat.
    :footie:
    :p Regular savers earn 6% interest (HSBC, First Direct, M&S) :p Loans cost 2.9% per year (Nationwide) = FREE money. :p
  • southcoastrgi
    southcoastrgi Posts: 6,298 Forumite
    Part of the Furniture 1,000 Posts Name Dropper Photogenic
    I'm lost as well MJ :D
    I'm only here while I wait for Corrie to start.

    You get no BS from me & if I think you are wrong I WILL tell you.
  • gas4you
    gas4you Posts: 2,602 Forumite
    The hot water stat on the boiler front does absolutely nothing on these boilers, unless you have a VR65 unit fitted, which with a Megaflo you wont.

    It is best to leave it set to minimum and forget about it.

    The hot water temperature is set on the thermostat on the Megaflo.
This discussion has been closed.
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 353.7K Banking & Borrowing
  • 254.2K Reduce Debt & Boost Income
  • 455.1K Spending & Discounts
  • 246.8K Work, Benefits & Business
  • 603.2K Mortgages, Homes & Bills
  • 178.2K Life & Family
  • 260.8K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16K Discuss & Feedback
  • 37.7K Read-Only Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.