ASHP: lagging pipes in loft

1356710

Comments

  • lovesgshp
    lovesgshp Posts: 1,413 Forumite
    Ninth Anniversary 1,000 Posts
    Thanks Gterr. Alarms are old, so no problem. Pump size looks okay for the house size, so does look more like a setup issue. There will be more questions tomorrow!!!
    As Manuel says in Fawlty Towers: " I Know Nothing"
  • albyota
    albyota Posts: 1,106 Forumite
    I'll try not to interfere with Geotherms kind offer, but i will keep an eye on this thread, Below is a link to the technical details of the system, I cannot find any info on the performance curves at higher water temps (45 / 50) it only shows outputs at 35 degrees at +7, +2 and minus 7

    i.e. 7.1kW at plus 2 degrees and 5.6kW at minus 7 degrees

    http://www.worcester-bosch.co.uk/homeowner/heat-pumps/air-to-water-heat-pumps/greensource-air-to-water-heat-pump-95kw/technical-data-table
    There are three types of people in this world...those that can count ...and those that can't! ;)

    * The Bitterness of Low Quality is Long Remembered after the Sweetness of Low Price is Forgotten!
  • gterr
    gterr Posts: 555 Forumite
    Geotherm wrote: »
    Thanks Gterr. Alarms are old, so no problem. Pump size looks okay for the house size, so does look more like a setup issue. There will be more questions tomorrow!!!

    Many thanks. Out today but will respond this evening.
  • lovesgshp
    lovesgshp Posts: 1,413 Forumite
    Ninth Anniversary 1,000 Posts
    albyota wrote: »
    I'll try not to interfere with Geotherms kind offer, but i will keep an eye on this thread, Below is a link to the technical details of the system, I cannot find any info on the performance curves at higher water temps (45 / 50) it only shows outputs at 35 degrees at +7, +2 and minus 7

    i.e. 7.1kW at plus 2 degrees and 5.6kW at minus 7 degrees

    http://www.worcester-bosch.co.uk/homeowner/heat-pumps/air-to-water-heat-pumps/greensource-air-to-water-heat-pump-95kw/technical-data-table

    If you would like the heat curve settings down to -20C, I can send you them if you pm your email, as it is a pdf file.
    As Manuel says in Fawlty Towers: " I Know Nothing"
  • lovesgshp
    lovesgshp Posts: 1,413 Forumite
    Ninth Anniversary 1,000 Posts
    Gterr.
    Can you let me know the electrical heater connection, which should be 4.5Kw. (menu 12.2.3). If you do not know how to access that, let me know, as factory setting is 13.5Kw
    As Manuel says in Fawlty Towers: " I Know Nothing"
  • gterr
    gterr Posts: 555 Forumite
    Geotherm wrote: »
    Gterr.
    Can you let me know the electrical heater connection, which should be 4.5Kw. (menu 12.2.3). If you do not know how to access that, let me know, as factory setting is 13.5Kw

    State total output, Compressor mode, Additional Heat only, all set to 4.5KW
  • lovesgshp
    lovesgshp Posts: 1,413 Forumite
    Ninth Anniversary 1,000 Posts
    Ok, that is the correct setting.
    I am thinking that this is something to do with the flow rates through the thermostatic rad valves. Are there bypass valves fitted?
    As Manuel says in Fawlty Towers: " I Know Nothing"
  • gterr
    gterr Posts: 555 Forumite
    Geotherm wrote: »
    Ok, that is the correct setting.
    I am thinking that this is something to do with the flow rates through the thermostatic rad valves. Are there bypass valves fitted?

    How would I tell? (preferably without taking up carpet and floorboards).

    Are you thinking that the flow goes first through the rads then on to the U/F coils? The rads are on a time clock, so only on 2 hours morning and 5 hours evening. What happens when they are timed off? I could see if the pipe leading down to the U/F manifold still gets hot when the rads are off, but of course that says nothing about the flow rate.
  • lovesgshp
    lovesgshp Posts: 1,413 Forumite
    Ninth Anniversary 1,000 Posts
    This is the type of valve I mean. As soon as the TRV shuts down, the flow is carried on.
    http://www.myson.co.uk/products/automatic_bypass_valves.asp
    As Manuel says in Fawlty Towers: " I Know Nothing"
  • gterr
    gterr Posts: 555 Forumite
    Geotherm,

    Here are pics of two rads: landing one and bathroom one. Landing one is a Danfoss, I think.

    Two other points: original plumber told us not to turn off all the rads at once otherwise a pump would burn out, so we keep the bathroom one turned on at the rad valve.
    Also, if you look at the previous pics I posted, the one showing the manifold has a motorised valve on the pipe flowing down to the manifold. Not sure what that's for, or what controls it, but presumably if it's off then nothing could get to the U/F coils??

    ASHP9


    ASHP10
This discussion has been closed.
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 351.6K Banking & Borrowing
  • 253.3K Reduce Debt & Boost Income
  • 453.9K Spending & Discounts
  • 244.5K Work, Benefits & Business
  • 599.8K Mortgages, Homes & Bills
  • 177.2K Life & Family
  • 258.1K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16.2K Discuss & Feedback
  • 37.6K Read-Only Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.