New Combi Boiler with 15mm gas supply

I'm a little concerned, I have always been advised that for a combi you need a 22mm gas supply. I've just had a worcester combi installed and the gas registered fitter located the 22mm in the ground but from the wall up it is 15mm. Therefore there is approx 1.5 meters where the gas supply is connected with a 15mm pipe. He assured me this is ok and proved it with his handheld meter readed showing co2 output of 8.9 which is as advised by the boiler manual. Is this ok? Thanks.
«13

Comments

  • muckybutt
    muckybutt Forumite Posts: 3,760 Forumite
    edited 22 October 2012 at 6:17PM
    What make and model ?

    All the Greenstar range specify 22mm
    You may click thanks if you found my advice useful
  • ariba10
    ariba10 Forumite Posts: 5,432
    Part of the Furniture 1,000 Posts Combo Breaker
    Forumite
    Our's is the same and have had no problems in the six years it has been in.
    I used to be indecisive but now I am not sure.
  • daveyjp
    daveyjp Forumite Posts: 12,191
    Part of the Furniture 10,000 Posts Name Dropper
    Forumite
    The installation manuals will give the size of gas pipe required.
  • southcoastrgi
    southcoastrgi Forumite Posts: 6,298
    Part of the Furniture 1,000 Posts Name Dropper Photogenic
    Forumite
    it depends on the working gas pressure at the meter & boiler (which he should have tested) as more than 1mb difference means it's AR & gets shut off, plus this is tested with all the other gas appliances running, but yes it is normally 22mm
    I'm only here while I wait for Corrie to start.

    You get no BS from me & if I think you are wrong I WILL tell you.
  • southcoastrgi
    southcoastrgi Forumite Posts: 6,298
    Part of the Furniture 1,000 Posts Name Dropper Photogenic
    Forumite
    ariba10 wrote: »
    Our's is the same and have had no problems in the six years it has been in.

    as the OP hasn't said the model & output of their boiler your point isn't relevent, plus unless your boiler has been tested in accordence with my post above there is no guarentee that yours is correct.
    I'm only here while I wait for Corrie to start.

    You get no BS from me & if I think you are wrong I WILL tell you.
  • katy123
    katy123 Forumite Posts: 362
    Part of the Furniture 100 Posts Combo Breaker
    Forumite
    wow, thanks for all the prompt replies...the model is worcester greenstar 28i combination boiler
  • C_Mababejive
    C_Mababejive Forumite Posts: 11,628
    Part of the Furniture 10,000 Posts Name Dropper Combo Breaker
    Forumite
    Its all about flow rate and pressure loss. In some circumstances you might need 35mm copper ! Pretty rare I'll grant you !
    Feudal Britain needs land reform. 70% of the land is "owned" by 1 % of the population and at least 50% is unregistered (inherited by landed gentry). Thats why your slave box costs so much..
  • southcoastrgi
    southcoastrgi Forumite Posts: 6,298
    Part of the Furniture 1,000 Posts Name Dropper Photogenic
    Forumite
    if it's the 28i junior then the gas connection to the boiler is 22mm & the connected gas supply pipe is not allowed to be any smaller than this, plus the co2 readings should be 9.8 on max & 9.2 on min so your installer not only has connected the incorrect gas supply pipe size but he hasn't commisioned it correctly either
    I'm only here while I wait for Corrie to start.

    You get no BS from me & if I think you are wrong I WILL tell you.
  • katy123
    katy123 Forumite Posts: 362
    Part of the Furniture 100 Posts Combo Breaker
    Forumite
    apologies, after 30 mins of running (approx) he showed me the reading and it read 9.7 or 9.9 i remembered it was 0.1 higher or lower than the "co2 level at max. rated heat output (after 30 minutes)"
  • katy123
    katy123 Forumite Posts: 362
    Part of the Furniture 100 Posts Combo Breaker
    Forumite
    edited 22 October 2012 at 8:19PM
    if he has installed it incorrectly, what do I do? Contact gas safe? The heating and hot water seems to work fine. Poster Ariba10 also has this set up without any probs.

    i haven't paid the fitter, he fitter it on friday

    there is 5 years warranty on the boiler...I guess my main concern is the safety or would it just shut itself off
This discussion has been closed.
Meet your Ambassadors

Categories

  • All Categories
  • 340.2K Banking & Borrowing
  • 249.1K Reduce Debt & Boost Income
  • 448.3K Spending & Discounts
  • 232K Work, Benefits & Business
  • 603.2K Mortgages, Homes & Bills
  • 171.6K Life & Family
  • 245.2K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 15.8K Discuss & Feedback
  • 15.1K Coronavirus Support Boards