    Grandad2b said:
    MLeeman said:
    A good 4.45 O's today. Might reach March target after all!

    On sunny days in the mid to late afternoon my generation curve seems to lessen quicker than it should (not lots but .5  ish) and then later afternoon it jumps back up again. No clouds or shading seems to be causing this.

    Up until lunch time is working perfect.

    Anyone have a thought on this?

    Here's my output for today 
    No idea why there's a big hole every day, I just put it down to cloud. Funny how it's always just as the sun gets to its highest.
    I had a similar problem last summer with output dropping unexpectedly on very sunny days. After a bit of investigation it turned out the inverter was tripping out when the grid voltage was in the high 250s. I live in a rural area and my house along with about a dozen others is fed from a transformer on a pole. Another one of the houses also has solar. Grid voltage here varies with load/solar generation (from 212v to 259v) and the pV generation on those sunny days were taking the voltage beyond the limits the inverter could handle causing it to trip out then a few minutes later restart as the voltage dropped. 
    Northern Lincolnshire. 7.8 kWp system, (4.2 kw west facing panels , 3.6 kw east facing), Solis inverters, Solar IBoost water heater, Mitsubishi SRK35ZS-S and SRK20ZS-S Wall Mounted Inverter Heat Pumps, ex Nissan Leaf owner)
  • legoman62
    legoman62 Posts: 4,987 Forumite
    Part of the Furniture 1,000 Posts Name Dropper
    Poor start to the month. 1.025 O’s here today🤷🏼‍♂️
    16 Sanyo Hit 250s.4kWp SMA 3.8kWp inverter. SW roof. 28° pitch. Minimal shade. Nov 2011 install. Hybrid car. Ripple Kirk Hill. N.E Lincs Coast.
  • Magnitio
    Magnitio Posts: 1,210 Forumite
    1,000 Posts Third Anniversary Name Dropper
    Another poor day at 1.37 O's
    We need more of this:

    6.4kWp (16 * 400Wp REC Alpha) facing ESE + 5kW Huawei inverter + 10kWh Huawei battery. Buckinghamshire.
  • Merlin139
    Merlin139 Posts: 7,259 Forumite
    Part of the Furniture 1,000 Posts Name Dropper Photogenic
    Poor start to April. Saw one glimpse of the sun but I think it ran away because of the rain.

    1.29 O's
    3.795 kWp Solar PV System. Capital of the Wolds

  • EcoScruples
    EcoScruples Posts: 422 Forumite
    Third Anniversary 100 Posts Name Dropper Photogenic
    A very disaponting March indeed, only managed 253kw (expected 380kw) so quite a bit short.
    My first year comes round mid June so let's keep those clouds away.
    4.3kwp JA panels, Huawei 3.68kw Hybrid inverter, Huawei 10kw Lunar 2000 battery, Myenergi eddi, South facing array with a 15 degree roof pitch, winter shade.
  • Bill73
    Bill73 Posts: 10 Forumite
    First Anniversary Name Dropper First Post

    Grandad2b said:
    Is a 20kW wind turbine very large? Not that I've any realistic prospect of having one myself but I have a mental picture of something quite big.

    It's all relative of course, the tower is 20 metres high and the blades are 6 metres, so 26 metres base to tip. The generator weighs just over a tonne. Average rpm is about 70 depending on the wind. Today 2nd April it is just ticking over as there isn't much wind. Production on an average day here (North East Scotland) is between 200 and 300 kWh. That's 24 hours of course - it works fine at night  :D
  • Grandad2b
    Grandad2b Posts: 352 Forumite
    Part of the Furniture 100 Posts Photogenic Name Dropper
    JKenH said:
    Grandad2b said:
    MLeeman said:
    A good 4.45 O's today. Might reach March target after all!

    On sunny days in the mid to late afternoon my generation curve seems to lessen quicker than it should (not lots but .5  ish) and then later afternoon it jumps back up again. No clouds or shading seems to be causing this.

    Up until lunch time is working perfect.

    Anyone have a thought on this?

    Here's my output for today 
    No idea why there's a big hole every day, I just put it down to cloud. Funny how it's always just as the sun gets to its highest.
    I had a similar problem last summer with output dropping unexpectedly on very sunny days. After a bit of investigation it turned out the inverter was tripping out when the grid voltage was in the high 250s. I live in a rural area and my house along with about a dozen others is fed from a transformer on a pole. Another one of the houses also has solar. Grid voltage here varies with load/solar generation (from 212v to 259v) and the pV generation on those sunny days were taking the voltage beyond the limits the inverter could handle causing it to trip out then a few minutes later restart as the voltage dropped. 
    I had a look at the log. Grid voltage was well within normal tolerances but the string voltage was 441V at the point the output dropped to zero. I need to do more analysis of the other figures since it seems there are all kinds of discrepancies which may or may not matter. Probably going to talk to the installers once I'm a bit clearer about what appears to be happening so I can at least give the impression of asking intelligent questions.
  • Grandad2b
    Grandad2b Posts: 352 Forumite
    Part of the Furniture 100 Posts Photogenic Name Dropper
    Oh, I forgot to post yesterday's figures. Not really sure it's worth bothering: 
    4.4kWh, 0.99 O's but today is at least half decent.
  • Grandad2b
    Grandad2b Posts: 352 Forumite
    Part of the Furniture 100 Posts Photogenic Name Dropper
    Grandad2b said: today is at least half decent.
    4.5 O's. That's more like it!
  • 94JDH
    94JDH Posts: 146 Forumite
    Fourth Anniversary 100 Posts Name Dropper
    22.25kWh for me - 3.45 O's from an East West flat roof system 
    PV total 19.8 kW system:
    23 x 420W East/West split over two flat roof areas at 10 degrees inclination.
    13 x 390W South spit over two flat roof areas at 5 to 20 degrees inclination.
    6 x 390W south wall mounted at 90 degrees inclination.
    7 x 390W West wall mounted at 90 degrees inclination.
    2 x 5 kW hybrid inverters
    4 x 9.5 kWh batteries (38 kWh total)
Meet your Ambassadors

🚀 Getting Started

Hi new member!

Our Getting Started Guide will help you get the most out of the Forum

Categories

  • All Categories
  • 351.1K Banking & Borrowing
  • 253.2K Reduce Debt & Boost Income
  • 453.6K Spending & Discounts
  • 244.1K Work, Benefits & Business
  • 599.1K Mortgages, Homes & Bills
  • 177K Life & Family
  • 257.5K Travel & Transport
  • 1.5M Hobbies & Leisure
  • 16.1K Discuss & Feedback
  • 37.6K Read-Only Boards

Is this how you want to be seen?

We see you are using a default avatar. It takes only a few seconds to pick a picture.