Hi,
My mother has just moved into a small bungalow which has Baxi Solo condensing boiler which is only 2 years old fitted by British gas.
This heats the hot water which goes into an Vented insulated Immersion cylinder and heats the radiators.
She has had a combi boiler for the last 15 years and would like a combi boiler fitting as she says it only heats the hot water when she needs it, which is correct but IMO is really not worth spending £2k to get new combi boiler.
Is there much difference between heating the water into Immersion cylinder versus a combi boiler heating the water ?
Any websites I can show her or costs to heat a tank of water ?
Are Condensing conventional boiler more efficient than a Condensing combi bolier ? Are they cheaper to repair ?
thanks.
My mother has just moved into a small bungalow which has Baxi Solo condensing boiler which is only 2 years old fitted by British gas.
This heats the hot water which goes into an Vented insulated Immersion cylinder and heats the radiators.
She has had a combi boiler for the last 15 years and would like a combi boiler fitting as she says it only heats the hot water when she needs it, which is correct but IMO is really not worth spending £2k to get new combi boiler.
Is there much difference between heating the water into Immersion cylinder versus a combi boiler heating the water ?
Any websites I can show her or costs to heat a tank of water ?
Are Condensing conventional boiler more efficient than a Condensing combi bolier ? Are they cheaper to repair ?
thanks.
0
Comments
-
It would be absurd to rip out a 2 year old boiler just to fit a combi. It would take years to recoup the cost, even assuming a marginal economy from the combi, but a properly insulated hot water tank will lose very little heat anyway.No free lunch, and no free laptop0
-
I agree with macman.
The main difference she will notice is that the pressure from the hot taps will be less than what she is used to with a combi.0 -
I agree.
Personally, I'm not a fan of combi boilers but equally, others are so its pretty much an individual choice.
My current boiler is a small wall mounted one which is 25 yrs old. Water hasn't been switched off for over 20 yrs...even on hols!
Last two bills were £63 and £66.
In 25 yrs its broken down twice but I had the parts here for it
You might find someone else come on here that will say the complete opposite but at least you'd be making a more informed decision.
There are many engineers with the same experience and qualifications as me who have the opposite view.
I don't think its a case of I'm right and they're wrong, just a different opinion.
Also, there are some well meaning but mis informed posters on here that you'll need to identify and ignore. :beer:You have been reading.....another magnificent post by garethgas :beer:0 -
I agree with macman.
The main difference she will notice is that the pressure from the hot taps will be less than what she is used to with a combi.
OP - The heat losses from a cylinder are about 2kWh per day but at this time of year the heat contributes to the house heat and is not wasted.:footie:Regular savers earn 6% interest (HSBC, First Direct, M&S)
Loans cost 2.9% per year (Nationwide) = FREE money.
0 -
With a 2kWh per day heat loss, that's 7p per day or about £25pa.
So that £2,000 investment will take about 80 years to recoup, assuming all the other running costs are the same-which is a big presumption anyway.
Can anyone recommend a combi that will last 80 years?No free lunch, and no free laptop0 -
I think you mean more than what she is used to. I have a hot water cylinder and the pressure is very high. I can fill a bath in under a minute. Other homes near me with combi's it takes more than 5 minutes to fill a bath.
OP - The heat losses from a cylinder are about 2kWh per day but at this time of year the heat contributes to the house heat and is not wasted.
No I mean what I said.
She is in a bungalow, so a standard hw cylinder fed from a loft tank will not have more than the minimum 1m head, therefore less pressure.
If it is an un-vented cylinder, or she lived in a house the the answer could/would be different.
Note I'm talking about pressure and not flow rate.0 -
No I mean what I said.
She is in a bungalow, so a standard hw cylinder fed from a loft tank will not have more than the minimum 1m head, therefore less pressure.
If it is an un-vented cylinder, or she lived in a house the the answer could/would be different.
Note I'm talking about pressure and not flow rate.
Surely a bungalow is a house, a single-storey house? :rotfl:Solar install June 2022, Bath
4.8 kW array, Growatt SPH5000 inverter, 1x Seplos Mason 280L V3 battery 15.2 kWh.
SSW roof. ~22° pitch, BISF house. 12 x 400W Hyundai panels0 -
keep the old system0
-
thanks everyone.
Will discus with her (gulp) and will ask a plumber to install a shower pump to feed a new mixer shower.0
This discussion has been closed.
Confirm your email address to Create Threads and Reply

Categories
- All Categories
- 351.3K Banking & Borrowing
- 253.2K Reduce Debt & Boost Income
- 453.7K Spending & Discounts
- 244.2K Work, Benefits & Business
- 599.4K Mortgages, Homes & Bills
- 177.1K Life & Family
- 257.7K Travel & Transport
- 1.5M Hobbies & Leisure
- 16.2K Discuss & Feedback
- 37.6K Read-Only Boards